    DIY Help Needed ... Rebar Sticking Out of Bond Beam

    What do you recommend I do with the rebar that extends above the bond beam? Do I just clip it flush, or should I bend it down and clip it at a lower point so it doesn't interfere with the coping or decking?


  2. Back To Top    #2

    Join Date
    Apr 2013
    Location
    Sacramento, CA
    Posts
    2,769

    Re: DIY Help Needed ... Rebar Sticking Out of Bond Beam

    Ok, I'll bite.

    Who poured (shot) that? Was it inspected by a building inspector before it was poured (shot)?

    In very rough terms you have to have at least 2 inches of cover over rebar. Sometimes 3, sometimes less.

    I might bring in a gunite crew and figure out a way to get some real coverage here. You still end up with a seam with exposed rebar in it in a high moisture environment. Just cutting it off and grouting over doesn't satisfy the building code. I's be very concerned that over time your rebar system will rust internally.

    In short I have no answer. You might call a swimming pool engineer, they may be able to give you some advice.
    22k gallon IG pebblefina, Jandy 1.5 HP VS, Jandy CV Cartridge filter, Fafco solar panels, Polaris 360 supply side cleaner, waterfall

  3. Back To Top    #3

    Join Date
    Jan 2014
    Location
    SE Louisiana
    Posts
    147

    Re: DIY Help Needed ... Rebar Sticking Out of Bond Beam

    Thanks for the response ... although I could've done without the "who poured/shot that?" comment. A quick scan of current build threads shows this approach being used on about 90% of the jobs. It's an interesting point though. Having many contractors build out this way does not necessarily mean it's best practice. Regardless, I'll have to work with what I have.

    Anyone happen to notice what the coping or decking subs did when rebar was installed this way? Another possibility I was thinking of is that they might be bending these pieces horizontally to tie in concrete decking. Not sure if that would partially defeat the purpose of the expansion joints.

    Thoughts?

    thanks
    Scot

  4. Back To Top    #4
    Patrick_B's Avatar
    Join Date
    Jun 2011
    Location
    Midland TX
    Posts
    15,001

    Re: DIY Help Needed ... Rebar Sticking Out of Bond Beam

    Quote Originally Posted by imperator View Post
    Thanks for the response ... although I could've done without the "who poured/shot that?" comment. A quick scan of current build threads shows this approach being used on about 90% of the jobs. It's an interesting point though. Having many contractors build out this way does not necessarily mean it's best practice. Regardless, I'll have to work with what I have.

    Anyone happen to notice what the coping or decking subs did when rebar was installed this way? Another possibility I was thinking of is that they might be bending these pieces horizontally to tie in concrete decking. Not sure if that would partially defeat the purpose of the expansion joints.

    Thoughts?

    thanks
    Scot
    I agree on the comment. This is very common and that is exactly what they did on my build. They bent and tied it right into the decking rebar. I don't see anything wrong, sloppy, or bad at all. Of course, I'm no PB expert, but I don't see anything to worry about.
    TFP Moderator
    Essential Links:
    ABC's Of Pool Chemistry, Test Kits, SLAM Your Pool
    28K Gal IG FreeForm, CLI Quartz, Pentair 36"SF & VS Pump, Dolphin M5, Rheem

  5. Back To Top    #5

    In the Industry

    duraleigh's Avatar
    Join Date
    Apr 2007
    Location
    Sebring, Florida
    Posts
    30,078

    Re: DIY Help Needed ... Rebar Sticking Out of Bond Beam

    1. Thread title contains "DIY" so I assume OP may have done his own rebar. Regardless, rebar should be embedded deeply into the gunite with nothing sticking up.

    If you bend it over to tie into the decking, you will have tied the pool walls to the decking which is a no-no.

    The picture is quite dark.....a better pic might give some insight.
    Dave S.
    42k vinyl and concrete pool, 1.5hp pump, 140gpm filter
    TFTestkits , PoolMath , Pool School

  6. Back To Top    #6

    Join Date
    Jan 2014
    Location
    SE Louisiana
    Posts
    147

    Re: DIY Help Needed ... Rebar Sticking Out of Bond Beam

    Quote Originally Posted by duraleigh View Post
    If you bend it over to tie into the decking, you will have tied the pool walls to the decking which is a no-no.

    The picture is quite dark.....a better pic might give some insight.
    Interesting. It appears to be more common on builds in the south. Maybe it's more acceptable down here because of the high water table we deal with along the coast. Could it reduce the chance of pool pop out.

    I guess semi-DIY would be a better way for me to title my future build thread. I will do several steps myself, but I opted to go with a single sub to handle excavation, rebar, gunite. I figured all of those steps to be way out of my league and after watching them work, I realized I was absolutely right about that. At this point, it's basically all DIY. I "intend" to handle the coping and decking, so I'll need to figure this out.

    Sorry about the bad pic. Owner builder paranoia crept up on me yesterday evening, so I rushed a pic out there. Here's a better shot of what they did earlier in the process. In pic 1, you can see the rebar grid before it was raised. After being raised, the top portion of the grid is centered in the upper portion of the bond beam and enclosed by plenty of gunite in all directions with the exception of the S shaped rebar which continues to extend upwards out the back of the bond beam.




  7. Back To Top    #7
    Patrick_B's Avatar
    Join Date
    Jun 2011
    Location
    Midland TX
    Posts
    15,001

    Re: DIY Help Needed ... Rebar Sticking Out of Bond Beam

    We'll, mine was centered in the shell, but they did bend some over to the decking rebar. I assumed it was for a reason and they knew what they were doing with that. A lot too late now, but I'll be asking why. My apologies for the hijack.
    TFP Moderator
    Essential Links:
    ABC's Of Pool Chemistry, Test Kits, SLAM Your Pool
    28K Gal IG FreeForm, CLI Quartz, Pentair 36"SF & VS Pump, Dolphin M5, Rheem

  8. Back To Top    #8

    Join Date
    Jan 2014
    Location
    SE Louisiana
    Posts
    147

    Re: DIY Help Needed ... Rebar Sticking Out of Bond Beam

    Please let me know what you find out.

  9. Back To Top    #9
    Patrick_B's Avatar
    Join Date
    Jun 2011
    Location
    Midland TX
    Posts
    15,001

    Re: DIY Help Needed ... Rebar Sticking Out of Bond Beam

    I will indeed. I'm anxious to hear an anwer now. My apologies for assuming it was right because my PB did it this way. Sheesh!
    TFP Moderator
    Essential Links:
    ABC's Of Pool Chemistry, Test Kits, SLAM Your Pool
    28K Gal IG FreeForm, CLI Quartz, Pentair 36"SF & VS Pump, Dolphin M5, Rheem

  10. Back To Top    #10
    JasonLion's Avatar
    Join Date
    May 2007
    Location
    Silver Spring, MD
    Posts
    37,879

    Re: DIY Help Needed ... Rebar Sticking Out of Bond Beam

    Rebar sticking up out of the bond beam is just fine. You cut off some and bend the rest of it over so it gets embedded in the coping mortar, which helps lock the coping to the wall. In some rare situations you bend it over so it gets embedded in the deck, but that is only for special situations where you need to lock the deck to the shell (which usually causes more problems than it solves).

    The problem I see in your picture is that the rebar should be centered horizontally in the wall thickness. Instead, it is coming out of the very edge of the wall. If I am reading the picture correctly it is on the outside of the wall, away from the water, so rust shouldn't be a dramatic problem in the short run. However, rebar that close to the edge won't serve the structural purpose it is supposed to serve; which could dangerously weaken the wall. In places it also isn't really even sealed into the wall, which could lead to long term rusting out and eventual complete loss of the rebar.

    The structural issues could be a major problem, depending on how much of the rebar is that close to the outside edge of the wall.
    19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
    Creator of PoolMath and Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School

  11. Back To Top    #11

    Join Date
    Apr 2013
    Location
    Sacramento, CA
    Posts
    2,769

    Re: DIY Help Needed ... Rebar Sticking Out of Bond Beam

    Sorry if my response was considered snarky -- I saw the DIY I just didn't think anyone shot their own gunite.

    I agree with all Jason has said but want to make a couple of points clear.

    The issue is not the rebar sticking up out of the bond beam. That can be cut epoxied or grouted and would probably be fine.

    The problem is the rebar close to and exposed on the outside of the wall. The code call for generally 2 inches and sometimes more gunite or concrete between the rebar and the ground. We don't know what it looks like inside so we can't really comment on the structural soundness of the wall but Jason's points are well taken.

    Second, regarding the top of the bond beam. You should almost never connect your bond beam to the deck with rebar. They are very different structures that will respond very differently to weather. Pool Engineering in Anaheim, CA which I bet engineers more pools than anyone in the US has as its standard a coping and deck floating over the bond beam. No rebar, no dowels, no pegs. Just floating. This allows the two structures to move completely independently of each other. I think I could find you a sketch. But that doesn't solve your real problem.
    22k gallon IG pebblefina, Jandy 1.5 HP VS, Jandy CV Cartridge filter, Fafco solar panels, Polaris 360 supply side cleaner, waterfall

  12. Back To Top    #12

    Join Date
    Jul 2012
    Location
    Oklahoma City
    Posts
    72

    Re: DIY Help Needed ... Rebar Sticking Out of Bond Beam

    I have found this article very helpful on the subject. Now getting the subs and/or PB to follow this information is another thing!!!

    http://www.pooleng.com/Reinforcing-S...ion/av-64.aspx
    IG gunite Edmond, OK(OKC), 18x36 freeform ~20K, 4-8' deep, Pentair equip, (2) 3hp VS+ pump, 520 cart filter, 3 LED, Easytouch8, ItellichlorIC40 SWG, Polaris 3900 cleaner, Spa 8'x18"raised, 20' raised bond beam 2 sheers, Stonescape Tahoe Blue quartz plaster, TF-100 kit.
    Feb. 25, 2014 dig started, May 24, 2014 filled.

  13. Back To Top    #13

    Join Date
    Jan 2014
    Location
    SE Louisiana
    Posts
    147

    Re: DIY Help Needed ... Rebar Sticking Out of Bond Beam

    Quote Originally Posted by gwegan View Post
    Sorry if my response was considered snarky -- I saw the DIY I just didn't think anyone shot their own gunite.
    No worries ... I can see how my title would have created reason for concern.

    Regarding structural issues for my situation ... I think I'm OK here. After looking at several builds in different locations, it appears that the Louisiana and Texas builds have the same quantity and layout of structural rebar as that used in other areas. Therefore, we have sufficient rebar encased in 3 or more inches of gunite. The difference for several of us is that there is an additional piece of rebar (generally every 2-4 feet) that is extended horizontally out of the back of the gunite wall (about 3 inches below zero bond beam) and then bent upwards. I called my sub and he confirmed that these pieces are intended for connections to a poured concrete deck. I'm not going to get into the topic of attached deck vs non-attached mainly because it's not a consideration for me. I've planned to go the paver route from the start. All I'll say about that is different areas may call for different methods.

    I went ahead and clipped these rebar pieces yesterday after hearing from my sub. Based on comments above, my only other issue might be the potential rusting of the rebar because the tips are exposed under soil. I'm not sure this is a major concern because I'm pretty sure my rebar will be wet 75+ percent of the year. If I dig a hole in my backyard today, it would be filled with water within 15 minutes. I'm sure all of my rebar is exposed to moisture because the concrete is porous. However, I guess it's better to be safe than sorry. I could easily put some of the membrane/sealer and mortar over it when I do the coping.

    Thanks so much for the advice.
    Scot