    Hayward H400

    I have an H400 that I'm having issues with and could use any help. The panel is not lighting up at all. I checked power to the transformer (240) is there. The other side had no power so I put a new one on it. Still the same result. What are the odds my new transformer is bad also? The panel was flickering and seemed to have water in it (long story, we'll say from the rain). I'm lost now anyone know if I can check the board? I'm sure they are expensive so don't want to dump money on one if I don't need it. Any help would be great, thanks!

  2. Back To Top    #2

    TFP Guide

    Join Date
    Jun 2012
    Location
    western NY
    Posts
    1,557

    Re: Hayward H400

    How did you check the power in and out of the transformer? It is unlikely that a new one is bad but not impossible. A volt/ohm meter set to the proper scale should read 24 volts at the terminals on the board. I would not be too suspicious of the board until you verify the voltage is there

  3. Back To Top    #3

    Re: Hayward H400

    I checked it with 2 different multimeters. It had under 1 vac. So I did get another one and it has one 1 vac. I'm sure it's not 2 bad xformers so now I'm stuck. The ground seems to be strong but I'm going to try and run a wire straight from the 240 side over to the 24 side. Thoughts?

  4. Back To Top    #4

    Re: Hayward H400

    Ok so just checked the 24 side of the transformer and without the leads that go to the board on it, I'm getting 2 VAC on it....I'm lost. The 240 side is good I have 2 120 wires and the ground. I can only think the ground has to be weak. The ground is attached to the same metal the ground from the pump is on.

  5. Back To Top    #5

    In the Industry

    ps0303's Avatar
    Join Date
    Jul 2011
    Location
    FL
    Posts
    3,436

    Re: Hayward H400

    Is this a newer Hayward unit? An FD series unit?
    Paul
    http://www.gastekservices.com A word of caution: When working with gas and electrical you might want to consider a licensed contractor. Consider the value of your life and others around you. If you would like to provide a review of the help I provided, please use the following link to leave a review. gastek - Google Search,

  6. Back To Top    #6

    Re: Hayward H400

    It's about 9 years old. So I checked the 240 side again, only had 120 this time. Checked continuity if the wires under ground in the conduit and it was intermittent. So long story short, one wire had broke underground. Ran 2 new wires and the heater works again. Thanks for the help guys.

  7. Back To Top    #7

    In the Industry

    ps0303's Avatar
    Join Date
    Jul 2011
    Location
    FL
    Posts
    3,436

    Re: Hayward H400

    Are the wires in a liquid tight conduit? If not, they should be.
    Paul
    http://www.gastekservices.com A word of caution: When working with gas and electrical you might want to consider a licensed contractor. Consider the value of your life and others around you. If you would like to provide a review of the help I provided, please use the following link to leave a review. gastek - Google Search,

  8. Back To Top    #8

    Re: Hayward H400

    Yes they are. Well they were dry.