    Under sized wiring

    Well I purchased my house over the summer and assumed the pump was wired to a 240v circuit. Well after inspecting my wiring for another project I realized that it is on a 120v circuit and the ga is way to small considering the run and amps. Basically I am left with 2 options, either change it over to 240v which will put the ga into proper operating range or run 100 feet or so of thick wire through old metal underground conduits. My personal feeling is change it over to 240v would be the much smarter option, but I'd like to ask for some outside opinions on the subject. Thanks
    26K Gallon, IG vinyl
    1.5 HP Hayward Super Pump, DE Filter 36 SqFt
    Older than time TELEDYNE LAARS HEATER (removed from system for now)

  2. Back To Top    #2
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    22,331

    Re: Under sized wiring

    What size is the existing wire? Did you actually use a wire gauge or micrometer to measure it?
    How far is the run from the breaker box to the pump?
    Is this a pool pump or well pump?
    How many wires are running from the breaker panel to the pump?
    Dave J. TFP Moderator
    24' x 52" Round AGP. 2hp/¼hp SPL Power-Flo 2-speed pump. 200sqft Waterway Cartridge Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit

  3. Back To Top    #3
    Mod Squad jblizzle's Avatar
    Join Date
    May 2010
    Location
    Tucson, AZ
    Posts
    37,389

    Re: Under sized wiring

    How long has this setup been running as it is?
    I think I would agree that sticking with a 230V pump would be the best option. Reason being, if you were to upgrade to a 2-speed or VS pump (for the electrical savings), they are almost all 230V.

    FYI, I have a 100 foot 12awg 230V circuit that supplies ALL my equipment power with smaller subpanel (pump, SWG, automation, pool light) When I was looking for a new pump, I quickly realized that going to a 115V pump was never going to be a good idea given the small wire size feeding the subpanel.

    I hope to eventually run new wire to the subpanel and have enough for a future hot tub.
    Jason, TFP Moderator
    18k IG pebblesheen pool, Hayward ProLogic P4 w/ T-15 SWG, Pentair 1HP 2-speed Superflo, Hayward 6020 DE filter
    500 sqft Heliocol solar panels, ThePoolCleaner, TF-100 test kit w/ SpeedStir
    Pool School + Test Kit + PoolMath = A TROUBLE FREE POOL
    If you found TFP helpful and we saved you money ... Become a TFP Supporter!

  4. Back To Top    #4

    Join Date
    Jul 2013
    Location
    Central New Jersey
    Posts
    55

    Re: Under sized wiring

    It is 12 ga I have access to the wire inside the house and it is 12/2 with ground (3 total wires).

    The run to the pump from the box is roughly 100 feet 20-25 feet inside the rest underground. The line is wired to the timer, which is inside next to the breaker box and then directly to locking style 3 prong outlet that powers the pump.

    Yes, this is a pool pump, sorry forget to mention that. Wasn't sure if I should put this in the pump section or here.

    The 12/2 only supplies the the pump and is on its own 20amp breaker. Which is actually too small for a Hayward Super Pump 1.5hp as it pulls roughly 18.6 amps @ 120v already over the 80% which a 20amp breaker truly is rated for.
    26K Gallon, IG vinyl
    1.5 HP Hayward Super Pump, DE Filter 36 SqFt
    Older than time TELEDYNE LAARS HEATER (removed from system for now)

  5. Back To Top    #5

    Join Date
    Jul 2013
    Location
    Central New Jersey
    Posts
    55

    Re: Under sized wiring

    Luckily a super pump can be rewired to 230v.

    Surprisingly jblizzle this setup has been running for the previous owner anywhere from 42 to 16 years. I say this since I'm not sure if any rewiring was done when he had the pool revamped in 96, but the pool was originally built in 72-73. Though I'm sure he was gone through a few pumps in all those years. If memory serves me correct he has been using this pump for 9 years or so.
    26K Gallon, IG vinyl
    1.5 HP Hayward Super Pump, DE Filter 36 SqFt
    Older than time TELEDYNE LAARS HEATER (removed from system for now)

  6. Back To Top    #6
    Mod Squad jblizzle's Avatar
    Join Date
    May 2010
    Location
    Tucson, AZ
    Posts
    37,389

    Re: Under sized wiring

    Since it is a dedicated circuit for the pump, you should be able to just re-purpose the common wire and wire the pump for 230V ... Disclaimer: check your local codes if that is approved
    Jason, TFP Moderator
    18k IG pebblesheen pool, Hayward ProLogic P4 w/ T-15 SWG, Pentair 1HP 2-speed Superflo, Hayward 6020 DE filter
    500 sqft Heliocol solar panels, ThePoolCleaner, TF-100 test kit w/ SpeedStir
    Pool School + Test Kit + PoolMath = A TROUBLE FREE POOL
    If you found TFP helpful and we saved you money ... Become a TFP Supporter!

  7. Back To Top    #7
    Isaac-1's Avatar
    Join Date
    May 2010
    Location
    SW Louisiana
    Posts
    6,711

    Re: Under sized wiring

    So there is no other 120V equipment at your pad? Is the timer a 120V only timer?
    Indoor 20x40 35,000 gallon vinyl pool with 1.5 HP 2 speed Jandy FloPro pump, Hayward EC75 Perflex DE filter, 11 4x12 Techno-Solis solar panels w/ Aquasolar controller, Aquabot Turbo T Robot Cleaner. Also LMI metering chlorine dispenser pump and HotSpring Jetsetter
    I use and endorse TFtestKits TF-100 from http://tftestkits.net
    ~Remember TFP counts on your donations to keep this site ad free~

  8. Back To Top    #8

    Join Date
    Jul 2013
    Location
    Central New Jersey
    Posts
    55

    Re: Under sized wiring

    There is other 120v equipment at the pad and around the pool, but it is all on another separate circuit/breaker. I think the timer can be wired for both 240 or 120, it just needs 120 to run the timer itself (could be wrong on this).
    26K Gallon, IG vinyl
    1.5 HP Hayward Super Pump, DE Filter 36 SqFt
    Older than time TELEDYNE LAARS HEATER (removed from system for now)

  9. Back To Top    #9

    TFP Guide

    Join Date
    Jun 2012
    Location
    western NY
    Posts
    1,557

    Re: Under sized wiring

    If the timer needs 120 to run then the wiring will need to be replaced. Once you remark and use the white as a power feed you will no longer have a neutral for the 120. BTW, a 20 amp breaker is rated for 20 amps, not 80% of 20 amps. The 80% comes in when you are determining if the load is considered a continuous load or not. Any load that is on for more than 3 hours at a time is considered a continuous load. This may apply here as most pumps run longer than that.