    PB did not install bonding

    Noticed today no bonding installed to the pool. Pool is filled with water, is it possible to remove support post to access wall seam bolting to install bonding lug with the pool filled with water? Concerned removing post to access bolting culd cause pool to collapse.
    21' x 54" Round AGP, Sand Filter, 1.5 Hp, Approx 10500 gallons, TF-100

  2. Back To Top    #2
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    22,347

    Re: PB did not install bonding

    I would try and route the wire up the post and lug it at the top without removeing the post if I could. Theoretically you should be able to remove and replace a post, tying it at the top eliminates the chance of something happening and it still accomplishes the bonding.
    Dave J. TFP Moderator
    24' x 52" Round AGP. 2hp/¼hp SPL Power-Flo 2-speed pump. 200sqft Waterway Cartridge Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit

  3. Back To Top    #3

    Re: PB did not install bonding

    Bama, tell me about the bonding wire. We have not connected one yet.

    Diagram is fuzzy...could you offer a link with the right config.

    Copper #8 wire that should be installed from the lug on our Aqua Trol SWG to the pump and then to a grounded metal source right???
    Hill Country of Texas~above ground Sharkline Matrix 18' round, with Gorilla pad (installed 7/25/2013)
    Hayward Power flo LX and Pro sand filter, Hayward salt cell Generator
    Sheer descent water fall

  4. Back To Top    #4
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    22,347

    Re: PB did not install bonding

    To do it correctly you need to bury a bare #8 wire around the pool 24" from the wall 4 to 6" deep and then connect it to the pool in 4 places equally around it. Then you extend it to any other pieces of metallic equipment larger than 9 sqin.
    Dave J. TFP Moderator
    24' x 52" Round AGP. 2hp/¼hp SPL Power-Flo 2-speed pump. 200sqft Waterway Cartridge Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit

  5. Back To Top    #5

    TFP Guide

    Join Date
    Jun 2012
    Location
    western NY
    Posts
    1,557

    Re: PB did not install bonding

    Quote Originally Posted by Bama Rambler
    To do it correctly you need to bury a bare #8 wire around the pool 24" from the wall 4 to 6" deep and then connect it to the pool in 4 places equally around it. Then you extend it to any other pieces of metallic equipment larger than 9 sqin.
    Your pump motor (and heater) should have a separate bonding lug on them as well. You will also need to supply a water bond of at least 9 sq in. If you have a heater, that may be acceptable for a water bond. All of these are to be connected together with the perimiter bond.
    Unknown make 18' above ground (bought used in 1999) Sparco sand filter. Hayward 100,000 BTu heater. 2 speed pump

  6. Back To Top    #6

    Re: PB did not install bonding

    Do not have a heater, we swim year round here almost!

    But this pool has vinyl rails at the bottom and vinyl caps, coping and struts, in fact the only metal parts are the walls themselves and some screws...it mostly snaps together. So where will I attach the wire to the pool. I could attach to the screws on the metal joint on the wall with the skimmer and jet....right?
    Hill Country of Texas~above ground Sharkline Matrix 18' round, with Gorilla pad (installed 7/25/2013)
    Hayward Power flo LX and Pro sand filter, Hayward salt cell Generator
    Sheer descent water fall

  7. Back To Top    #7
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    22,347

    Re: PB did not install bonding

    That's what most people do. Just attach a lug to a seam bolt. If the uprights have metal top and/or bottom brackets you can attach to that as well.
    Dave J. TFP Moderator
    24' x 52" Round AGP. 2hp/¼hp SPL Power-Flo 2-speed pump. 200sqft Waterway Cartridge Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit