    I have a Jandy Aquapure EI(plug in version) arriving today. I have no outlet at my pump pad. Where should I wire in an outlet? Can I tie into the Intermatic timer box, or should I somehow tap into the breaker box? Thanks for any help.
    17,500 gallon 18x36 gunite pool
    Hayward super II 1.5 hp pump, Hayward cartridge filter
    Jandy AquaPure Ei SWG 35K, Raypak R6350TI-E HeatPump
    Solar cover, Loop Lok winter Cover
    Artisian Antigua hot tub, Polk Atrium 4's

  2. Back To Top    #2
    Mod Squad jblizzle's Avatar
    Join Date
    May 2010
    Location
    Tucson, AZ
    Posts
    37,389

    Re: Where should I wire in an outlet for my SWG?

    The power for the SWG should come off the LOAD side of the timer so that it can not be on when the pump is off.
    Jason, TFP Moderator
    18k IG pebblesheen pool, Hayward ProLogic P4 w/ T-15 SWG, Pentair 1HP 2-speed Superflo, Hayward 6020 DE filter
    500 sqft Heliocol solar panels, ThePoolCleaner, TF-100 test kit w/ SpeedStir
    Pool School + Test Kit + PoolMath = A TROUBLE FREE POOL
    If you found TFP helpful and we saved you money ... Become a TFP Supporter!

  3. Back To Top    #3
    gullzway's Avatar
    Join Date
    Nov 2009
    Location
    Tulsa,OK
    Posts
    103

    Re: Where should I wire in an outlet for my SWG?

    Quote Originally Posted by jblizzle
    The power for the SWG should come off the LOAD side of the timer so that it can not be on when the pump is off.

    Thank you!

    So the Positive for the outlet goes to the #4 and the negative to the #2 on the timer right?
    Attached Images Attached Images
    17,500 gallon 18x36 gunite pool
    Hayward super II 1.5 hp pump, Hayward cartridge filter
    Jandy AquaPure Ei SWG 35K, Raypak R6350TI-E HeatPump
    Solar cover, Loop Lok winter Cover
    Artisian Antigua hot tub, Polk Atrium 4's

  4. Back To Top    #4
    Mod Squad jblizzle's Avatar
    Join Date
    May 2010
    Location
    Tucson, AZ
    Posts
    37,389

    Re: Where should I wire in an outlet for my SWG?

    Based on those wire colors ... your pump appears to be 230V ... so neither of those are "negative" {I think you mean "neutral" when talking about 115V}

    So if you SWG is only 115V, you may have to run a neutral from the panel (if there is not one already) and then power the SWG off EITHER the 2 or 4 terminal. EDIT: But honestly I am not sure if that is a good idea as it would result is mismatched current through the 2 LINES coming from the pump breaker.
    Jason, TFP Moderator
    18k IG pebblesheen pool, Hayward ProLogic P4 w/ T-15 SWG, Pentair 1HP 2-speed Superflo, Hayward 6020 DE filter
    500 sqft Heliocol solar panels, ThePoolCleaner, TF-100 test kit w/ SpeedStir
    Pool School + Test Kit + PoolMath = A TROUBLE FREE POOL
    If you found TFP helpful and we saved you money ... Become a TFP Supporter!

  5. Back To Top    #5
    gullzway's Avatar
    Join Date
    Nov 2009
    Location
    Tulsa,OK
    Posts
    103

    Re: Where should I wire in an outlet for my SWG?

    Quote Originally Posted by jblizzle
    Based on those wire colors ... your pump appears to be 230V ... so neither of those are "negative" {I think you mean "neutral" when talking about 115V}

    So if you SWG is only 115V, you may have to run a neutral from the panel (if there is not one already) and then power the SWG off EITHER the 2 or 4 terminal. EDIT: But honestly I am not sure if that is a good idea as it would result is mismatched current through the 2 LINES coming from the pump breaker.

    The pump sticker says 115/230, but with it running, all 4 terminals read 120 volts. So it looks like I'll have to run it from the breaker box. Thanks for the help!
    Attached Images Attached Images
    17,500 gallon 18x36 gunite pool
    Hayward super II 1.5 hp pump, Hayward cartridge filter
    Jandy AquaPure Ei SWG 35K, Raypak R6350TI-E HeatPump
    Solar cover, Loop Lok winter Cover
    Artisian Antigua hot tub, Polk Atrium 4's

  6. Back To Top    #6
    gullzway's Avatar
    Join Date
    Nov 2009
    Location
    Tulsa,OK
    Posts
    103

    Re: Where should I wire in an outlet for my SWG?

    Or can I tie the outlet into the green wire, which is coming from the neutral bar in the breaker box?

    EDIT: Just saw your edit about mismatched current tying into one of the 120 lines. I'll tie into the breaker box, Thanks!!!
    17,500 gallon 18x36 gunite pool
    Hayward super II 1.5 hp pump, Hayward cartridge filter
    Jandy AquaPure Ei SWG 35K, Raypak R6350TI-E HeatPump
    Solar cover, Loop Lok winter Cover
    Artisian Antigua hot tub, Polk Atrium 4's

  7. Back To Top    #7
    Mod Squad jblizzle's Avatar
    Join Date
    May 2010
    Location
    Tucson, AZ
    Posts
    37,389

    Re: Where should I wire in an outlet for my SWG?

    I am just not knowledgeable enough to know if running the SWG off one leg of the 230V pump circuit is OK or not.

    Most SWG usually are hardwired and designed to be wired for both 115V or 230V. You should check and if yours could be rewired for 230V, I would recommend tieing it into the timer for the safest installation.
    Jason, TFP Moderator
    18k IG pebblesheen pool, Hayward ProLogic P4 w/ T-15 SWG, Pentair 1HP 2-speed Superflo, Hayward 6020 DE filter
    500 sqft Heliocol solar panels, ThePoolCleaner, TF-100 test kit w/ SpeedStir
    Pool School + Test Kit + PoolMath = A TROUBLE FREE POOL
    If you found TFP helpful and we saved you money ... Become a TFP Supporter!

  8. Back To Top    #8
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    22,347

    Re: Where should I wire in an outlet for my SWG?

    The first thing I notice is that I don't see any gfci breakers in that panel. They should be.

    You shouldn't tie the neutral wire of the swg into the ground wires in the timer. You could run a neutral from the panel to the timer box and run it that way.

    There are a couple of ways to run the pump and swg from that timer.
    1. Run a neutral wire from the panel to the swg through the timer and hook the hot of the swg to terminal 2 or 4.

    2. Run a neutral wire and a hot wire from the panel to the timer and then remove the wires from terminal 3 & 4 (even the white one) and wirenut them together. Then run the neutral to the swg and hook the hot to terminal 3 and the swg hot wire to terminal 4.

    3. Leave the pump hooked up like it is now and run the swg to the panel and hope the flow switch shuts it down every time.

    I don't recommend #3!
    Dave J. TFP Moderator
    24' x 52" Round AGP. 2hp/¼hp SPL Power-Flo 2-speed pump. 200sqft Waterway Cartridge Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit

  9. Back To Top    #9
    Mod Squad jblizzle's Avatar
    Join Date
    May 2010
    Location
    Tucson, AZ
    Posts
    37,389

    Re: Where should I wire in an outlet for my SWG?

    2 is a pretty good idea basically making the timer have 2 SPST switches instead of 1 DPST switch (you would need to add a new SWG breaker) ... although some would argue that you should turn both legs of the 230V to the pump off with the timer to be "safer". Although I would not be messing with the wires without throwing the breaker off anyway

    Still not sure #1 is recommended ... in fact if you change the pump breaker to a GFCI, I am pretty sure #1 would cause the GFCI to trip since it monitors the current through the 2 legs for a difference.
    Jason, TFP Moderator
    18k IG pebblesheen pool, Hayward ProLogic P4 w/ T-15 SWG, Pentair 1HP 2-speed Superflo, Hayward 6020 DE filter
    500 sqft Heliocol solar panels, ThePoolCleaner, TF-100 test kit w/ SpeedStir
    Pool School + Test Kit + PoolMath = A TROUBLE FREE POOL
    If you found TFP helpful and we saved you money ... Become a TFP Supporter!

  10. Back To Top    #10
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    22,347

    Re: Where should I wire in an outlet for my SWG?

    I forgot to say that #2 is the preferred choice.

    #1 will not work as JB points out, if you change the breakers to gfci (which I highly recommend).
    Dave J. TFP Moderator
    24' x 52" Round AGP. 2hp/¼hp SPL Power-Flo 2-speed pump. 200sqft Waterway Cartridge Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit

  11. Back To Top    #11
    gullzway's Avatar
    Join Date
    Nov 2009
    Location
    Tulsa,OK
    Posts
    103

    Re: Where should I wire in an outlet for my SWG?

    Quote Originally Posted by Bama Rambler
    The first thing I notice is that I don't see any gfci breakers in that panel.

    You shouldn't tie the neutral wire of the swg into the ground wires in the timer. You could run a neutral from the panel to the timer box and run it that way.
    One is labeled GFCI, it runs over to my Koi pond.

    Why would tying into the ground of the timer(which comes straight from the neutral bar in the breaker box,) be any different from running another wire to the neutral bar?
    17,500 gallon 18x36 gunite pool
    Hayward super II 1.5 hp pump, Hayward cartridge filter
    Jandy AquaPure Ei SWG 35K, Raypak R6350TI-E HeatPump
    Solar cover, Loop Lok winter Cover
    Artisian Antigua hot tub, Polk Atrium 4's

  12. Back To Top    #12
    Mod Squad jblizzle's Avatar
    Join Date
    May 2010
    Location
    Tucson, AZ
    Posts
    37,389

    Re: Where should I wire in an outlet for my SWG?

    Quote Originally Posted by gullzway
    One is labeled GFCI, it runs over to my Koi pond.
    That is probably just saying it has a GFCI outlet on that circuit. None of your breakers are GFCI

    Quote Originally Posted by gullzway
    Why would tying into the ground of the timer(which comes straight from the neutral bar in the breaker box,) be any different from running another wire to the neutral bar?
    It just is Granted it would work, but that would not be correct or to code. It could result in engerizing all the ground wires.
    Jason, TFP Moderator
    18k IG pebblesheen pool, Hayward ProLogic P4 w/ T-15 SWG, Pentair 1HP 2-speed Superflo, Hayward 6020 DE filter
    500 sqft Heliocol solar panels, ThePoolCleaner, TF-100 test kit w/ SpeedStir
    Pool School + Test Kit + PoolMath = A TROUBLE FREE POOL
    If you found TFP helpful and we saved you money ... Become a TFP Supporter!

  13. Back To Top    #13
    gullzway's Avatar
    Join Date
    Nov 2009
    Location
    Tulsa,OK
    Posts
    103

    Re: Where should I wire in an outlet for my SWG?

    OK, thanks to you both for the help!!
    17,500 gallon 18x36 gunite pool
    Hayward super II 1.5 hp pump, Hayward cartridge filter
    Jandy AquaPure Ei SWG 35K, Raypak R6350TI-E HeatPump
    Solar cover, Loop Lok winter Cover
    Artisian Antigua hot tub, Polk Atrium 4's

  14. Back To Top    #14
    gullzway's Avatar
    Join Date
    Nov 2009
    Location
    Tulsa,OK
    Posts
    103

    Re: Where should I wire in an outlet for my SWG?

    Just got The Jandy in, and realized I don't have enough room to install the unit and flow meter after the filter. Can I install the flow meter before the filter and the swg after?

    Attached Images Attached Images
    17,500 gallon 18x36 gunite pool
    Hayward super II 1.5 hp pump, Hayward cartridge filter
    Jandy AquaPure Ei SWG 35K, Raypak R6350TI-E HeatPump
    Solar cover, Loop Lok winter Cover
    Artisian Antigua hot tub, Polk Atrium 4's

  15. Back To Top    #15
    Mod Squad jblizzle's Avatar
    Join Date
    May 2010
    Location
    Tucson, AZ
    Posts
    37,389

    Re: Where should I wire in an outlet for my SWG?

    SWG must be last. What type of flow meter? It might be ok to put before the filter and not get clogged.
    Jason, TFP Moderator
    18k IG pebblesheen pool, Hayward ProLogic P4 w/ T-15 SWG, Pentair 1HP 2-speed Superflo, Hayward 6020 DE filter
    500 sqft Heliocol solar panels, ThePoolCleaner, TF-100 test kit w/ SpeedStir
    Pool School + Test Kit + PoolMath = A TROUBLE FREE POOL
    If you found TFP helpful and we saved you money ... Become a TFP Supporter!

  16. Back To Top    #16
    gullzway's Avatar
    Join Date
    Nov 2009
    Location
    Tulsa,OK
    Posts
    103

    Re: Where should I wire in an outlet for my SWG?

    Quote Originally Posted by jblizzle
    SWG must be last. What type of flow meter? It might be ok to put before the filter and not get clogged.
    It just has a little black paddle in it in the flow path. When I ordered the unit it wasn't pictured, so I didn't know it came with it.
    17,500 gallon 18x36 gunite pool
    Hayward super II 1.5 hp pump, Hayward cartridge filter
    Jandy AquaPure Ei SWG 35K, Raypak R6350TI-E HeatPump
    Solar cover, Loop Lok winter Cover
    Artisian Antigua hot tub, Polk Atrium 4's

  17. Back To Top    #17
    Mod Squad jblizzle's Avatar
    Join Date
    May 2010
    Location
    Tucson, AZ
    Posts
    37,389

    Re: Where should I wire in an outlet for my SWG?

    Oh! You mean the flow switch/sensor for the SWG not a separate flow meter.

    Should be fine before the filter, verify the plumbing requirements in the manual.
    Jason, TFP Moderator
    18k IG pebblesheen pool, Hayward ProLogic P4 w/ T-15 SWG, Pentair 1HP 2-speed Superflo, Hayward 6020 DE filter
    500 sqft Heliocol solar panels, ThePoolCleaner, TF-100 test kit w/ SpeedStir
    Pool School + Test Kit + PoolMath = A TROUBLE FREE POOL
    If you found TFP helpful and we saved you money ... Become a TFP Supporter!

  18. Back To Top    #18
    gullzway's Avatar
    Join Date
    Nov 2009
    Location
    Tulsa,OK
    Posts
    103

    Re: Where should I wire in an outlet for my SWG?

    Got it installed, thanks for the help. I'll have to test and see if it's making chlorine, but so far so good. I ran a neutral wire from the breaker box to the outlet, and ran the positive from terminal 4. So I guess that was option #1, option #2 confused me, working good so far!

    Attached Images Attached Images
    17,500 gallon 18x36 gunite pool
    Hayward super II 1.5 hp pump, Hayward cartridge filter
    Jandy AquaPure Ei SWG 35K, Raypak R6350TI-E HeatPump
    Solar cover, Loop Lok winter Cover
    Artisian Antigua hot tub, Polk Atrium 4's

  19. Back To Top    #19

    Join Date
    Jul 2007
    Location
    Hillsborough, NC
    Posts
    515

    Re: Where should I wire in an outlet for my SWG?

    Quote Originally Posted by gullzway
    Why would tying into the ground of the timer(which comes straight from the neutral bar in the breaker box,) be any different from running another wire to the neutral bar?
    Just FYI, you can but it is against code. Household appliances (Dryers, electric stoves, etc) generally use 220V for heating and 110V for the controls. You could wire them with 2 hots and a ground, and the 110V side would use the ground as the neutral. This works, but the problem is the bare ground is now carrying current. The NEC decided that was bad (it is) so starting around 1993 required 2 hots, a ground and a neutral. This is why electric dryers have a 3-prong or 4-prong plug. The difference is the separate neutral. When I bought my house I found that the 110V condensate pump for the air handler in the basement was using 1 leg of the 220V supply and the bare ground for the air handler as a neutral. It worked fine, it was just dangerous.
    27' Round Might Sun AG Pool 18000 Gallon Intex Krystal Clear SWG Hayward Pump/Filter on a Timer

  20. Back To Top    #20
    gullzway's Avatar
    Join Date
    Nov 2009
    Location
    Tulsa,OK
    Posts
    103

    Re: Where should I wire in an outlet for my SWG?

    Looking good, chlorine up from 1 ppm last night to 2.5 ppm today.
    17,500 gallon 18x36 gunite pool
    Hayward super II 1.5 hp pump, Hayward cartridge filter
    Jandy AquaPure Ei SWG 35K, Raypak R6350TI-E HeatPump
    Solar cover, Loop Lok winter Cover
    Artisian Antigua hot tub, Polk Atrium 4's