  1. Back To Top    #1

    Join Date
    Apr 2012
    Location
    Southeast Louisiana
    Posts
    174

    New building code for low voltage lights around pool?

    I've been reading with great interest the various posts here and elsewhere regarding low voltage lights, and how they are not allowed to be closer than 10ft. from the water's edge. Some people say that it's dangerous, others say that with a pool-specific transformer it's perfectly safe (though still a code violation).

    Regardless, I came across this recent article that seems to indicate a change in the code is in the works.

    http://www.ecmag.com/section/codes-stan ... k%E2%80%A9

    In the 2011 and previous editions of the National Electrical Code (NEC), installing low-voltage lighting in close proximity to the edge of a swimming pool was a Code violation, yet almost every backyard swimming pool with a landscaped yard has low-voltage lighting too close to the pool’s edge. Low-voltage lighting systems are not permitted to be installed within 10 feet of the nearest edge of the water for a pool, spa or fountain, unless otherwise permitted by Article 680. With the acceptance of new text in 680.22(B)(6) of the 2014 NEC, many of these installations will now be compliant.
    -snip-

    The proposed new 680.22(B)(6) states: “Low-Voltage Luminaires. Listed low-voltage luminaires not requiring grounding, not exceeding the low-*voltage contact limit, and supplied by listed transformers or power supplies that comply with 680.23(A)(2) are permitted to be located less than 1.5 m (5 ft) from the inside walls of the pool.” Section 680.23(A)(2) states that transformers used for low-voltage lighting around pools shall incorporate isolated windings with an ungrounded secondary and a grounded metal barrier between the primary or secondary or double insulation between the primary and secondary windings. This change should provide safety for low-voltage lighting systems close to pool or spa edges.
    --Michael
    Slidell, Louisiana (near New Orleans) • 11,000gal kidney shaped Trilogy fiberglass pool • Intelliflo VS • Triton TR100 filter • Easytouch 4 w/IC20 SWCG • Polaris 280

  2. Back To Top    #2
    JasonLion's Avatar
    Join Date
    May 2007
    Location
    Silver Spring, MD
    Posts
    37,879

    Re: New building code for low voltage lights around pool?

    Progress moves slowly. The 2014 edition is not yet published, and will not be enacted in any given area for quite some time after that, but eventually they will get there.
    19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
    Creator of PoolMath and Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School

  3. Back To Top    #3
    Melt In The Sun's Avatar
    Join Date
    Oct 2009
    Location
    Tucson, AZ
    Posts
    3,899

    Re: New building code for low voltage lights around pool?

    Looking forward to it I can wait a while to put mine in...got plenty of other stuff to do still!
    11,200 gal, Pebble-Tec; Tristar 2-speed 1hp - Swimclear 325 ft2 cart - SWG - A & A in-floor cleaner - Heat pump. For the poolside cooking, a Yoder Wichita and a Big Steel Keg!
    TF Test Kits -- PoolMath -- Pool School
    Make each day your masterpiece. - John Wooden

  4. Back To Top    #4

    Re: New building code for low voltage lights around pool?

    These systems use an isolating power supply that must not exceed 30V (42.4Vpk) under any load condition, even while open circuited.

  5. Back To Top    #5
    JasonLion's Avatar
    Join Date
    May 2007
    Location
    Silver Spring, MD
    Posts
    37,879

    Re: New building code for low voltage lights around pool?

    The way the voltage limits are going to be specified is more complex than the old limits, though the effect is essentially the same. The number to remember is still a max of 15 volts AC. The numbers JosephSpark just gave are RMS peak to peak and absolute peak to peak, which are not commonly used units. There is also a lower limit for certain kinds of square wave power supplies, which is getting way to technical to explain here.
    19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
    Creator of PoolMath and Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School

  6. Back To Top    #6
    JasonLion's Avatar
    Join Date
    May 2007
    Location
    Silver Spring, MD
    Posts
    37,879

    Re: New building code for low voltage lights around pool?

    The 2014 NEC is out and specific kinds of lights are now allowed within 5 feet of the water. There are both voltage limits and current limits on the new kind of lighting, and all components of the lighting system must be listed for this kind of use. Because of the current limits, it looks like only LED lighting will be efficient enough to provide useful amounts of light and still meet the requirements.

    It will still be years before local adoption of the 2014 NEC, but at least progress along these lines continues.
    19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
    Creator of PoolMath and Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School

  7. Back To Top    #7

    Re: New building code for low voltage lights around pool?

    Where can this be found? I'm curious how close I got on my install.

    Led seems to be the only way to go.


    14,000 gallon IG plaster pool, Cartridge Filter

  8. Back To Top    #8
    JasonLion's Avatar
    Join Date
    May 2007
    Location
    Silver Spring, MD
    Posts
    37,879

    Re: New building code for low voltage lights around pool?

    Amazon has the full NEC code here, or you can search around the Internet looking for things like "nec low voltage contact lighting 2014" you can find various partial discussions of the new code requirements.
    19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
    Creator of PoolMath and Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School

  9. Back To Top    #9
    Melt In The Sun's Avatar
    Join Date
    Oct 2009
    Location
    Tucson, AZ
    Posts
    3,899

    Re: New building code for low voltage lights around pool?

    Hm, LED is the future anyway I guess. Thanks for the heads up Jason!

    jlentz, if you google "nec 2014" you can find some sites (like NFPA) that will give you free access...not sure if there's a better way.
    11,200 gal, Pebble-Tec; Tristar 2-speed 1hp - Swimclear 325 ft2 cart - SWG - A & A in-floor cleaner - Heat pump. For the poolside cooking, a Yoder Wichita and a Big Steel Keg!
    TF Test Kits -- PoolMath -- Pool School
    Make each day your masterpiece. - John Wooden

  10. Back To Top    #10

    Join Date
    May 2014
    Location
    Port Richey, Florida
    Posts
    4

    Re: New building code for low voltage lights around pool?

    Don't get too excited about this "great change" just yet. I have put in a proposal to delete it or at least get change or clarification.

    The problem, as I see it, is that the human is at the same potential as the pool bonding grid. This is a good thing, though. The purpose of a pool bonding grid is to abate step and touch voltages (keep everything at the same potential). One must remember that the pool water is bonded therefore the person in the pool will theoretically be at the same potential as the bonding grid.

    Now the change allows lights (theoretically) to be right next to the pool, where someone will reach out and touch.

    Providing GFCI protection on the primary side of an isolation transformer will not provide GFCI protection on the secondary side. Low-voltage luminaires are commonly listed and wired using prong-type quick connects that are designed to pierce the insulation of the wiring. If someone in the pool (skin will be wet) was to touch (on purpose or accidentally) these connections to the low-voltage luminaire, there could be an external voltage introduced onto the bonding grid and that person in the pool would receive some type of shock, whether mild or otherwise.

    It gets worse -

    An active implantable medical device (AIMD) is any medical device which is intended to be totally or partially introduced, surgically or medically, into the human body, and which is intended to remain after the procedure. The most common of these devices are pacemakers and defibrillators. The heart produces electrical signals (or action potentials) which need to be reliably detected by the AIMD's sensing leads. External voltage can induce signals on these sensing leads that prevent the device working properly.

    Any external (interference) voltage with an implanted heart device can have the potential to be serious. If this happens to a pacemaker, it usually reverts to constant pacing mode. A defibrillator could in theory send a shock when one was not needed, or possibly be inhibited from providing a shock when one is needed.

    So don't be fooled that any low-voltage right next to the pool can be safe. It isn't. Now we need to find out if there is some sort of special listing on these "fixtures" and/or if they are to be wired with some type of conduit connection, like a niche, or whatever. So far UL has been pretty silent on the "how" this change is to be accomplished. I have not been able to get any answers yet, or to find examples of working systems that are properly listed to meet this new code.

    Please chime in if you can shoot any holes in my opinion.
    Thanks,
    guru

  11. Back To Top    #11

    Join Date
    May 2014
    Location
    Port Richey, Florida
    Posts
    4

    Re: New building code for low voltage lights around pool?

    Well, since my last post - I haven't been able to locate any of these new mysterious lights that are listed to be used above ground at the pool's edge. A collegue of mine told me that they were the "exact same light" as an underwater pool light. But that can't be since the sealed beam light comes with a factory cord that contains a ground wire. One of the conditions for the "next to the pool light" is that it doesn't require grounding.

    So far - I have found LED that 1) Don't require a niche, and 2) don't require grounding - but the problem is that they are listed for underwater use. I can't find one that is listed for above ground. If you can find one, please post a link to it here. Thanks.

  12. Back To Top    #12

    Re: New building code for low voltage lights around pool?

    Quote Originally Posted by necguru View Post
    ...but the problem is that they are listed for underwater use. I can't find one that is listed for above ground. If you can find one, please post a link to it here. Thanks.
    Maybe I'm not reading enough into it, but if it's listed for underwater use, then wouldn't it be fine for above ground? I know that if something is not listed for use underwater then you shouldn't use it underwater but wouldn't it be ok the other way around??
    11,500 gallon mountain pond shaped vinyl line / Hayward 2spd pump / Hayward S244T sand filter (filled with zeobrite) / Hayward PL-P4 Automation panel / Hayward SWG (T-3 Cell) / Polaris 280 with booster / Hayward AquaConnect / Hayward CrystalLogic color changing LEDS

  13. Back To Top    #13

    Join Date
    Jan 2014
    Location
    Buckeye AZ
    Posts
    807

    Re: New building code for low voltage lights around pool?

    what about solar leds with a wire running to a solar panel? Not connected to the pool/house grid...
    10,500 gal IG, Topaz Pebble, auto-level
    Hayward DE filter, 2HP Ecostar VSP, ProLogic PS-4, GVA actuators
    Cal Pools Wave Force Plus (wall return jets plus 2 floor pop-ups), Venturi Skimmer
    Water sheer, 2 wok pots, bubbler stem on the baja step
    ColorLogic Mutlicolor LED lamp. Taylor 2006+speed stir

  14. Back To Top    #14

    Join Date
    May 2014
    Location
    Port Richey, Florida
    Posts
    4

    Re: New building code for low voltage lights around pool?

    To answer some of the comments - If something is listed for underwater use then it isn't listed for above ground use...

    Solar - no. It would be bad to introduce voltage (especially from another system) around the pool.

    Here is a recent article on this very same subject:

    http://www.ecmag.com/section/introdu...ound-pool-area

  15. Back To Top    #15

    Join Date
    Aug 2014
    Location
    NJ
    Posts
    426

    Re: New building code for low voltage lights around pool?

    Necguru,

    My town told me it was acceptable to put outside speakers five feet from the waters edge. The outside speakers are connected by speaker wires to a Sonos device on my house. Does that make sense to you? Or would the same concept apply that they shouldn't be 5 feet from the pool? Also, based on what you said I am assuming (perhaps incorrectly) that landscape lights within 5 feet of the water's edge would be ok if no one inside the pool could ever touch them. I don't have any landscape lights near the pool, but was thinking about it. I have a rock wall and a grotto that would prevent anyone from inside the pool from ever touching the light. Would that alleviate the problem?

    Thanks
    1200 Sq Ft 41,000 Gal. Gunite, JANDY SVRS VS pump, JANDY JXI 400,000 BTU, Polaris 280 w/ 3/4 BP, Rockwall and Grotto (w/6 jets and blower), 2 JANDY Lam Jets, 2 LED Bubblers, 5 Ledlights, AQUALINK P16 RS, 90% Quartz, SWF 185 GMP BP, SWF 125 BP, Levelor K1100 Autofill, AP Digital SWG, 2 skim and 5 returns, and mostly 3 inch piping

  16. Back To Top    #16

    Join Date
    May 2014
    Location
    Port Richey, Florida
    Posts
    4

    Re: New building code for low voltage lights around pool?

    Sorry - I haven't been around for a while.

    I don't know what a Sonos device is.

    The question I would have is not where the speakers or landscape lights are but where the WIRING is located.
    If it is properly listed for what you are using it for, and the wiring is at least 5-feet away, then the speakers being 5-feet away is probably a non-issue. Landscape lighting isn't listed for 5-feet, it must be at least 10-feet away from the pool.