Thread: AquaLink not communicating with valve?

  1. Back To Top    #1

    AquaLink not communicating with valve?

    Noticed that my Jandy AquaLink no longer communicates with the Jandy valve that moves the solar on/off valve. The valve moves just fine if you use the switch on the valve, but doesn't respond with the controller inside the house or per the programed on/off times. Made sure wires are connected at the circuit board, suggestions on how to trouble shoot? Also use to get a solar temp display on the inhouse controller which is no longer there.

    Know there is a sensor up on the roof that reads temp and allows for some overides like freeze protect and max limits, any chance that's where the problem resides or is this a board problem?

    Thanks for any thoughts and suggestions.

  2. Back To Top    #2
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    22,331

    Re: AquaLink not communicating with valve?

    If the actuator moves with the manual reversing switch, it has power from the board. Can you switch it with the Aqualink?
    Have you checked the programming?
    Dave J. TFP Moderator
    24' x 52" Round AGP. 2hp/¼hp SPL Power-Flo 2-speed pump. 200sqft Waterway Cartridge Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit

  3. Back To Top    #3

    Re: AquaLink not communicating with valve?

    Thanks for the input! Just double checked programming, all good. Can't make the valve move with the AquaLink - so my problem is either between AquaLink and the board or perhaps something to do with the sensor that also feeds into the system? Thanks again.

  4. Back To Top    #4
    JasonLion's Avatar
    Join Date
    May 2007
    Location
    Silver Spring, MD
    Posts
    37,879

    Re: AquaLink not communicating with valve?

    Check the small switch on the actuator. In it's middle position the actuator is turned off and will not work remotely, and if you switch between the other two positions, the actuator should move.
    19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
    Creator of PoolMath and Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School

  5. Back To Top    #5
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    22,331

    Re: AquaLink not communicating with valve?

    Can you check voltage at the actuator?
    Dave J. TFP Moderator
    24' x 52" Round AGP. 2hp/¼hp SPL Power-Flo 2-speed pump. 200sqft Waterway Cartridge Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit

  6. Back To Top    #6

    Re: AquaLink not communicating with valve?

    Should be able to check the voltage, have a meter and basic knowledge. I'll see what I can figure out tonight - anything specific I should be looking for?

    (small switch on the actuator is working, toggles the valve open or closed, doesnt respond however to the Aqualink controller in the house when left in either up or down position)

    Thanks

  7. Back To Top    #7
    JasonLion's Avatar
    Join Date
    May 2007
    Location
    Silver Spring, MD
    Posts
    37,879

    Re: AquaLink not communicating with valve?

    That means the wiring and power supply are good and it is something to do with the software setup in the controller or the relay.
    19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
    Creator of PoolMath and Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School

  8. Back To Top    #8

    Re: AquaLink not communicating with valve?

    ok, thanks for your help! I'll dig a bit further into the system.

  9. Back To Top    #9

    Re: AquaLink not communicating with valve?

    It's working! Problem was in the SW setup as suggested. In system setup no JVA was assigned, how that changed after 8 years of working just fine?

    Thanks so much for the help in narrowing down the problem, really appreciated!