    Looking for the proper surge protector to install at the pad

    I have 240v out to the equipment pad and I'm upgrading from an Intermatic timer to a new Easy Touch 4 system.
    1- I have read here that it's appropriate to add some type of surge protection for the control panel, could you point out a model I should look at?
    2- I am also going to install new GFCI breakers for the new (Intelliflo VF) pump, existing heater, and for the single pool and single spa lights. Should I also install one for the control panel transformer as well?
    Thanks in advance.

  2. Back To Top    #2
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    22,347

    Re: Looking for the proper surge protector to install at the

    1) There are a lot of whole house protectors that will work for you. Leviton makes a decent whole house protector that I'm familiar with. The 51120 series would be a good choice.
    2) I would install one on everything in that panel.
    Dave J. TFP Moderator
    24' x 52" Round AGP. 2hp/¼hp SPL Power-Flo 2-speed pump. 200sqft Waterway Cartridge Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit

  3. Back To Top    #3

    Join Date
    Aug 2011
    Location
    Southern California
    Posts
    188

    Re: Looking for the proper surge protector to install at the

    2) I would install one on everything in that panel.
    Will do.


    Bama, as for the surge protector, the power running to my pad has two 30 amp breakers feeding it. Couldn't I install the surge on the main lugs inside the Easy Touch panel? That would cover all/any breakers installed?

    Was thinking of this

  4. Back To Top    #4
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    22,347

    Re: Looking for the proper surge protector to install at the

    That Intermatic is a good unit. Installing it on the main lugs will work fine.
    Dave J. TFP Moderator
    24' x 52" Round AGP. 2hp/¼hp SPL Power-Flo 2-speed pump. 200sqft Waterway Cartridge Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit

  5. Back To Top    #5

    Re: Looking for the proper surge protector to install at the

    I'm a big fan of GFCIs (and surge supressors). But, for those of us on a budget, there is relief.

    A GFCI cannot "see" past a transformer. So the GFCI is either protecting 10 inches of wire inside the automation box or 10 feet of wire to the light transformer, if you have one. The wires past the transformer are safe becouse of the transformer. The GFCI, in this case, has no effect on bather safety.

    Modern GFCI breakers and receptacles are subject to the same strict standards, and the same flaws in the system. A good name brand of either is just as safe. There is no reason to put a modern GFCI receptacle on a GFCI breaker. Older GFCI receptacles should be replaced with modern GFCI receptacles.

    A 15 amp GFCI circuit can easily protect four 300 watt pool lights. The only advantage to having lights on different circuits is knowing which light is at fault when the GFCI trips. If you're calling a pool tech to fix the lights anyway, diagnosing which light is at fault should be simple for him to do.

    Although very common, putting surge protector wires under the main lugs is a code violation. Putting two wires in a lug not listed for it is a violation. That includes almost all lugs on breakers. The surge protector should have its own, not GFCI, breaker.

  6. Back To Top    #6

    Join Date
    Aug 2011
    Location
    Southern California
    Posts
    188

    Re: Looking for the proper surge protector to install at the

    Quote Originally Posted by Glennsparky
    I'm a big fan of GFCIs (and surge supressors). But, for those of us on a budget, there is relief.

    A GFCI cannot "see" past a transformer. So the GFCI is either protecting 10 inches of wire inside the automation box or 10 feet of wire to the light transformer, if you have one. The wires past the transformer are safe becouse of the transformer. The GFCI, in this case, has no effect on bather safety.

    Modern GFCI breakers and receptacles are subject to the same strict standards, and the same flaws in the system. A good name brand of either is just as safe. There is no reason to put a modern GFCI receptacle on a GFCI breaker. Older GFCI receptacles should be replaced with modern GFCI receptacles.

    A 15 amp GFCI circuit can easily protect four 300 watt pool lights. The only advantage to having lights on different circuits is knowing which light is at fault when the GFCI trips. If you're calling a pool tech to fix the lights anyway, diagnosing which light is at fault should be simple for him to do.

    Although very common, putting surge protector wires under the main lugs is a code violation. Putting two wires in a lug not listed for it is a violation. That includes almost all lugs on breakers. The surge protector should have its own, not GFCI, breaker.
    All great info Glenn, thanks for passing it on. Also, Welcome to the board!
    I'll put the surge protector on it's own breaker, will a 15 amp single pole be sufficient? By isolating the surge protector to it's own breaker, will it still protect all circuits in that load center?

  7. Back To Top    #7

    Re: Looking for the proper surge protector to install at the

    Yes. As long as that breaker is on... You will need a 2-pole breaker since the surge protector protects both legs.
    32K gal, gunite, French Gray DB, IntelliFlo VF, IntelliFlo, WhisperFlo, Quad DE 100 filter, IntelliTouch, IC-60 SWG, IntelliChem, Dolphin M5

  8. Back To Top    #8

    Join Date
    Aug 2011
    Location
    Southern California
    Posts
    188

    Re: Looking for the proper surge protector to install at the

    Quote Originally Posted by jtech1
    Yes. As long as that breaker is on... You will need a 2-pole breaker since the surge protector protects both legs.

    Makes perfect sense.