    Help - Wiring for H400 IDL2 into Aqualink Panel

    Hello, my pool heater fried - burnt resistors on the control boards. After finding out that there are differences between a H400, and the H400 IDL2 control boards, I have my heater working (mostly). I've replaced the display, the display board, and the control board in the unit.

    The heater now works by manually starting/adjusting it physically outside at the unit.

    However, my Aqualink is not controlling the unit. I'm going to change the wire to the panel as one last thing to do.

    Questions
    On the aqualink outdoor panel (which I haven't touched, so this is the original and at one point working wiring)
    - blue/white wire is wired into terminal '1'
    - orange/white is wired into terminal '2'

    On the heater control board, what should the wiring be??? I don't know if I mixed up the wiring when I put in the new card.
    - Pool (blue/white??)(orange/white??)
    - 24 VAC (empty)
    - Spa (blue/white??)(orange/white??)

    I've tried the 'bo' where you hold down mode/low and that doesn't allow me to control the heater with the aqualink inside. It used to work 2 yrs ago, then last winter was on the fritz. This winter it fried.
    Houston Texas - 18 k gals pool, Hayward 2 HP main pump, 0.75 hp boost pump, 2 HP waterfall pump, Hayward H400 idl Heater, DE filter
    Polaris 280 pool bot - Taylor 2006 Test Kit - BB (no Borax yet)

  2. Back To Top    #2

    In the Industry

    ps0303's Avatar
    Join Date
    Jul 2011
    Location
    FL
    Posts
    3,435

    Re: Help - Wiring for H400 IDL2 into Aqualink Panel

    You need one set of wires to be connected to either pool or spa, not both. The other set goes to the 24v AC. Then put the unit in bo, Bypass Operation and the Aqualink should control it.

    So try blue/white to pool and orange/white to the 24vAC. Don't forget that you have to set the Pool temp set point on the heater to as high as it will go, usually 104.
    Paul
    http://www.gastekservices.com A word of caution: When working with gas and electrical you might want to consider a licensed contractor. Consider the value of your life and others around you. If you would like to provide a review of the help I provided, please use the following link to leave a review. gastek - Google Search,

  3. Back To Top    #3

    Re: Help - Wiring for H400 IDL2 into Aqualink Panel

    Ok, that worked, thank you PS0303.

    I'm posting the sequence I performed for anyone else doing a similar project

    - Replaced 3 of the control boards in Hayward H400 (IDL2) heater
    - Wired
    - blue/white in top spot (labeled pool) on card
    - orange/white in the 24 V middle spot on card
    - set pool and spa to max temp (104 F)
    - put the unit on 'standby'
    - held 'mode' and 'decrease temp' for 3 seconds to put in 'bo' mode which showed on the display
    - hit mode twice to put the heater in 'pool' mode (red LED lit), 'bo' still on heater

    Works perfect now
    Houston Texas - 18 k gals pool, Hayward 2 HP main pump, 0.75 hp boost pump, 2 HP waterfall pump, Hayward H400 idl Heater, DE filter
    Polaris 280 pool bot - Taylor 2006 Test Kit - BB (no Borax yet)