problem with AquaPro 500 heat pump

I purchased a new heat pump and cannot seem to get it working. It continues to error out with an HP (high pressure) code after about 5-10 min of operation.

Anyone have any experience with these units? Calling for service, but really worried that we are off to such a bad start.

?
 
The HP error should be on the freon side and that shouldn't happen as long as there is water flowing through the system. Have you checked to make sure you have water flowing through the heat pump to the pool? Make sure the bypass valve is closed if there is one.
 