    Heater blower on when pump is off or on low RPM

    We just had an EasyTouch, Intelliflo, IntellipH, SCG, and new filter installed. The pump is an upgrade from a single speed. If I run the pump below 1350 RPMs, the blower on the heater kicks on, and I get the "lo" error message that usually means low water flow. This happens at less than 1350 RPM and when the pump is off. The heater is an old Hayward H400IDL2 installed around 2005/2006.

    Any ideas? I guess my next step on my end is to disconnect the remote wire just to see if it's an interface issue.

    Thanks for any replies and suggestions.
    14.5K gal Plaster IGP, Intelliflo VS, EasyTouch 8, SWG, IntellipH, Clear and Clean 420 Cartridge Filter, Attached Spa, H400IDL2 NG Heater

  2. Back To Top    #2

    In the Industry

    ps0303's Avatar
    Join Date
    Jul 2011
    Location
    FL
    Posts
    3,437

    Re: Heater blower on when pump is off or on low RPM

    The heater shouldn't be coming on unless you have selected to activate it. Sounds to me like you have some crossed wires or wires connected where they shouldn't be.
    Paul
    http://www.gastekservices.com A word of caution: When working with gas and electrical you might want to consider a licensed contractor. Consider the value of your life and others around you. If you would like to provide a review of the help I provided, please use the following link to leave a review. gastek - Google Search,

  3. Back To Top    #3
    phipsi1237's Avatar
    Join Date
    Jan 2011
    Location
    North Las Vegas, NV
    Posts
    228

    Re: Heater blower on when pump is off or on low RPM

    I've disconnected the remote switch. Blower is running right now with same service code "Lo." I did notice the heater is connected directly through to the circuit breaker with the pump. Seems as if the heater is powered all the time. So, if water flow is sufficient, blower doesn't come on.

    Should I connect the heater power to the filter/pump relay? At least this way, power is off to the heater until the pump is powered. I can't find anything in the heater or EasyTouch manual discussing this.
    14.5K gal Plaster IGP, Intelliflo VS, EasyTouch 8, SWG, IntellipH, Clear and Clean 420 Cartridge Filter, Attached Spa, H400IDL2 NG Heater

  4. Back To Top    #4
    phipsi1237's Avatar
    Join Date
    Jan 2011
    Location
    North Las Vegas, NV
    Posts
    228

    Re: Heater blower on when pump is off or on low RPM

    Not that this has anything to do with the issue at hand, but the heater is connected to the same circuit breaker as the pump. The Intelliflo manual says the pump should be on it's own circuit. Moving the heater to the load side of the pump relay will fix this. The SCG is connected to the load side of the pump relay as well. Would this be a problem?
    14.5K gal Plaster IGP, Intelliflo VS, EasyTouch 8, SWG, IntellipH, Clear and Clean 420 Cartridge Filter, Attached Spa, H400IDL2 NG Heater

  5. Back To Top    #5
    phipsi1237's Avatar
    Join Date
    Jan 2011
    Location
    North Las Vegas, NV
    Posts
    228

    Re: Heater blower on when pump is off or on low RPM

    Just got off the phone with Pentair. He said by hooking the heater through the pump relay I may be hiding a different issue. For now, 2 options:

    Wire to the relay, that way the heater fan won't run when the pump is off.
    Or
    Run the pump for 24 hours. I'm already running 23, so what's another hour.

    I've got an email into Hayward support since I couldn't find a number for them.

    Even though the heater is always powered, the remote switch should be doing it's job. I'm at a loss until Hayward gets back to me.
    14.5K gal Plaster IGP, Intelliflo VS, EasyTouch 8, SWG, IntellipH, Clear and Clean 420 Cartridge Filter, Attached Spa, H400IDL2 NG Heater

  6. Back To Top    #6
    mas985's Avatar
    Join Date
    May 2007
    Location
    Pleasanton, CA
    Posts
    11,490

    Re: Heater blower on when pump is off or on low RPM

    A lot of heaters operate this way as a safety feature so the best solution is to wire it with the pump relay. This is the way mine is wired.
    Mark
    Hydraulics 101; Pump Ed 101; Pump/Pool Spreadsheets; Pump Run Time Study; DIY Acid Dosing; DIY Cover Roller
    18'x36' 20k plaster, MaxFlo SP2303VSP, Aqualogic PS8 SWCG, 420 sq-ft Cartridge, Solar, 6 jet spa, 1 HP jet pump, 400k BTU NG Heater

  7. Back To Top    #7
    phipsi1237's Avatar
    Join Date
    Jan 2011
    Location
    North Las Vegas, NV
    Posts
    228

    Re: Heater blower on when pump is off or on low RPM

    That will definitely solve the issue of the heater fan turning on when the pump goes off.

    Now I need to figure out why the fan comes (with "Lo" service light) when the flow rate drops even though I'm not asking for heat. I got it down to 1240 RPMs by closing the bypass valve they installed with everything else. I don't see a reason I shouldn't be able to run the pump at 750 RPMs, hence the point of a variable sipped pump.
    14.5K gal Plaster IGP, Intelliflo VS, EasyTouch 8, SWG, IntellipH, Clear and Clean 420 Cartridge Filter, Attached Spa, H400IDL2 NG Heater

  8. Back To Top    #8
    mas985's Avatar
    Join Date
    May 2007
    Location
    Pleasanton, CA
    Posts
    11,490

    Re: Heater blower on when pump is off or on low RPM

    Quote Originally Posted by phipsi1237
    Now I need to figure out why the fan comes (with "Lo" service light) when the flow rate drops even though I'm not asking for heat.
    As I said before, it is designed to do that as a safety feature. If the unit is powered on and the water pressure drops below a set point, the exhaust fan is designed to turn on. However, the pressure swithc set point should be adjustable. Is the heater elevated significantly above the water line? If so, there should be a procedure in the manual to adjust the pressure switch set point. Most heaters have a minimum flow rate that they are designed for. My heater and most heaters require at least 40 GPM. If you operate below that level, it could damage the heat ex-changer.
    Mark
    Hydraulics 101; Pump Ed 101; Pump/Pool Spreadsheets; Pump Run Time Study; DIY Acid Dosing; DIY Cover Roller
    18'x36' 20k plaster, MaxFlo SP2303VSP, Aqualogic PS8 SWCG, 420 sq-ft Cartridge, Solar, 6 jet spa, 1 HP jet pump, 400k BTU NG Heater

  9. Back To Top    #9
    phipsi1237's Avatar
    Join Date
    Jan 2011
    Location
    North Las Vegas, NV
    Posts
    228

    Re: Heater blower on when pump is off or on low RPM

    Thanks for all the info. I have read about an adjustable pressure switch. I understand about the minimum flow requirements as well. But, I assumed the min flow was for when I was calling for heat. I'm running the pump 23 hours a day and would really like to be able to dial it down from the current 1240RPM to whatever I can.
    14.5K gal Plaster IGP, Intelliflo VS, EasyTouch 8, SWG, IntellipH, Clear and Clean 420 Cartridge Filter, Attached Spa, H400IDL2 NG Heater

  10. Back To Top    #10
    phipsi1237's Avatar
    Join Date
    Jan 2011
    Location
    North Las Vegas, NV
    Posts
    228

    Re: Heater blower on when pump is off or on low RPM

    Oh, and as for the height above the water. I guess it might be a foot or so above.
    14.5K gal Plaster IGP, Intelliflo VS, EasyTouch 8, SWG, IntellipH, Clear and Clean 420 Cartridge Filter, Attached Spa, H400IDL2 NG Heater

  11. Back To Top    #11
    phipsi1237's Avatar
    Join Date
    Jan 2011
    Location
    North Las Vegas, NV
    Posts
    228

    Re: Heater blower on when pump is off or on low RPM

    I adjusted the water pressure switch and can run the pump as low as I want for the heater. HOWEVER!!! Now I can't go below 1050 RPMs because I get a low flow light on the IC40 cell. I'm guessing there's no way around that. Plus, any lower than that almost worries me about circulation. I think I can live with 150 watts though. Now, I do need to hook the heater to the filter/pump relay so that it turns off when the pump does.
    14.5K gal Plaster IGP, Intelliflo VS, EasyTouch 8, SWG, IntellipH, Clear and Clean 420 Cartridge Filter, Attached Spa, H400IDL2 NG Heater