Heater tripping GFCI breaker

Jul 17, 2012
31
So...New electrical work has been finished for a week now. About once a day the GFCI breaker was tripping for the heater circuit. The heater is a Hayward heat pump on a dedicated 240 volt 20 amp circuit. I called pool builder to ask them about it and they said to call the electrician. Called electrician and he came out and replaced the GFCI circuit with a non-GFCI breaker. It's been running a few days now and hasn't tripped the breaker. Is it safe to run heater on a non-GFCI protected circuit?
 
What does the electrician say about it? I would think you should have a GFCI circuit for it but you need to consult with the codes and the electrician. Did he say why he swapped it out for a non GFCI?
 
He said sometimes the GFCI breakers are too sensitive for something that has a larger startup load.

I thought I read somewhere that a GFCI is not required if the heater is hard wired. True??


Sent from my iPhone using Tapatalk
 
There is likely a ground fault that should be addressed. Whether it's required is determined by your local code/electrical inspector, not something you may have read somewhere :smile: In general I would think a GFCI is needed on equipment that touches pool water, but then again, I'm not an electrician so can't tell you for sure.
 
walt7474 said:
He said sometimes the GFCI breakers are too sensitive for something that has a larger startup load.
You need a better electrician. GFCI's do not fault on over current. As was mentioned there is a current leak somewhere

walt7474 said:
I thought I read somewhere that a GFCI is not required if the heater is hard wired. True??
Ask your inspector who approved the instalation. I do not have my code book here at home to check.
 
Not familiar with the Hayward heat pumps but on Pentair units they require a 50 amp breaker the load at startup is around 42 to 45 amps then drops off to 35 amps for the compressor. Verify that a 20 amp breaker is large enough to handle the startup load.
 