Results 1 to 13 of 13
Thread: Heater problem
    Heater problem
    I have a Teledyne Laars EPM 175,000 BTU heater and it started up just fine. I shut it off to save on fuel cost and went to turn it back on it wouldn't ignite. So went through the steps again and re lit the gas pilot and came on just fine but it will not innit unless I jumper it on the coil and the th side of the gas valve. I change out the therostat a couple of years ago with a compuerized thermostat with a blinking light. The light is no longer blinking. The Heater use a pilot generator to produce the the current that is neccessary to ignite the burners. I replaced the pressure swith. I put a jumper from the coil to the black lead of the pressure switch and a jumper to the th on the valve to the white wire of the pressure switch and it fires every time. Any sugeestions what could cause it to not to fire.
    Articfox918's Avatar
    May 2012
    Western, Wisconsin
    99
    Re: Heater problem
    I haven't worked on a whole lot of pool heaters but have worked on a few and I used to work on all kinds of furnaces (so basically the same concept w/o water) when you say pressure switch are we talking the water pressure switch or the combustion blower pressure switch? I looked up your heater and found a diagram uyou said you put a jumper on the white wire of the switch which according to the diagram I saw that's on the water pressure switch is this correct?
    **EDIT** I think the diagram I found is a newer version of the one you got I will look for a different diagram the one I found did not have a pilot generator for flame proof**
    POOL SIZE: 27 FT round 52" Deep on edges 66" Deep in center
    FILTER TYPE: Hayward Sand Filter
    PUMP SIZE: Hayward 1 HP Pump 60GPM
    FILTER SIZE/FLOW RATE: Unknown
    HEATER: None at the moment but in process of making my solar panels should be operational by next season!
    Jun 2012
    western NY
    1,560
    Re: Heater problem
    You are obviously pretty good at knowing your way around inside your heater. With that, it should be simple enough to trace out which switch is bad. With everything hooked up as normal, one at a time unhook the switches and jumper the wires. When the heater fires up, you found the culprit. The entire proving system in these is nothing more than a daisy chain of switches similar to an old string of christmas lights (If one goes out they all go out)
    Unknown make 18' above ground (bought used in 1999) Sparco sand filter. Hayward 100,000 BTu heater. 2 speed pump
    Re: Heater problem
    Water Pressure switch. Ya I have actullay taken out the burner valve and burner and cleaned it. What bugs me is it was working fine. Some time I have to jiggle the wires to get it going and this time I tried restarting it and wouldnt ignite. I have checked all of the wires and cleaned all of the terminals and done a bunch of tests. In my own opinion it is either the pilot generator or the themastat. But with out taking the generator out or taking the half of the top off to get to the thermasta I wanted a second opinion.
    May 2012
    Western, Wisconsin
    99
    Re: Heater problem
    Do you have a meter that reads milliamps? You then could check the pilot generator
    May 2012
    Western, Wisconsin
    99
    Re: Heater problem
    Do you have the manual? I just found this and from what you have said thus far sounds like you can figure it out. it has a good troubleshooting section in it for determining cause of failure
    https://www.parts4heating.com/v/vspfile ... eries1.pdf
    Jun 2012
    western NY
    1,560
    Re: Heater problem
    If jumping the terminals on the gas valve makes it work them It will not be the power generator. Just to verify, it should be puting out 750 Millivolts (unless it is one of the rare lower mv generators). Easy way to verify the thermostat would be to jump across the wires to the thermostat and see if it fires
    Re: Heater problem
    I tested the thermostat with the voltmeter and it didn't move the meter at all it just maintained the same readings. A new thermostat is $221.00 you just can't go in buy just the thermostat you have to buy the whole unit. And to answer previous questions yes I have volt meter and a manual. Not real good with volt meter but get buy. I'm going to first remove the burner tray and clean the pilot generator and then I will look towards a new thermostat if cleaning the generator doesn't take care of it. Thanks
    Qwaxalot's Avatar
    Jun 2012
    439
    Re: Heater problem
    Before you do that replace all of the wire end spade connectors (you can buy 16 guage connectors at a home depot or radio shack) Corrosion at the connectors is by far and away the most common problem on millivolt heaters.
    In the industry, CSP (Certified Service Professional) by the NSPI and it's successor the APSP. My company services over 600 pools every year. I think the practices regularly espoused on this forum (especially the BBB method) are outstanding; however my comments will be often oriented towards the goal of getting it done, and getting it done right now!
    Re: Heater problem
    Ok here is the skinny. Changed the generator and cleaned the pilot light with a brass brush put in a brand new pilot generator in, still wouldn't start butwhen I jumpered the coil and a black wire on the Pressure Switch it started and then I could use the toggle switch to turn it off and I could turn down the thermostat, which indicated that it was a high temp electrical diode, I changed out the bad diode and put a new one in and every thing is workig great. The one thing I'm having trouble with is putting the hood on cant see to remember were some of the sheetmetal goes. I have put this lid on a couple times befor and I can't remember wher things go. Happy aout getting heater running again
    Re: Heater problem
    I put my pressure switch back on and that was not part of the problem so it boils down to a new pilot generator and a high limit diode.
    Jun 2012
    western NY
    1,560
    Re: Heater problem
    My guess is it was the high temp diode all along. When you jumped the terminals on the gas valve and it fired up you took all of the controls out of the loop. If it did not fire up then I would suspect the powerpile.
    Oh, and don't feel bad about putting the puzzle back together. In both of my past careers (auto mech and heating tech) that was the hardest part of the job sometimes. I could diagnose the problem fairly easily but getting all of the parts back on afterwards was the tough part.
    Re: Heater problem
    I guess I need to take a picture of it when I take it apart. I'm pushing 60 and sometimes I second guess my self some times. Thanks