    AGP electrical question. Stranded vs solid THHN #12

    I have a electrical question, does anyone know if one is better to use than the other? I have a 50 foot run and getting ready to pull it through the conduit, but have not bought the wire yet. Can I use either one? I know stranded is easier to pull, but that is not an issue. Any do's or dont's? I will be pulling 12 g THHN/THWN

    Thanks,

    George
    21 10500 gal AGP 52' sides, haward 3/4 hp xl pump and earth filter ec50
    Using the bbb method. Tf-100 kit. My first pool so learning in progress!

  2. Back To Top    #2
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    22,331

    Re: AGP electrical question. Stranded vs solid THHN #12

    I would personally use stranded, but it really doesn't make a difference. Either will work fine.
    Dave J. TFP Moderator
    24' x 52" Round AGP. 2hp/¼hp SPL Power-Flo 2-speed pump. 200sqft Waterway Cartridge Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit

  3. Back To Top    #3
    Isaac-1's Avatar
    Join Date
    May 2010
    Location
    SW Louisiana
    Posts
    6,711

    Re: AGP electrical question. Stranded vs solid THHN #12

    You should always use stranded when connecting to vibration sources like motors, generators, etc.
    Indoor 20x40 35,000 gallon vinyl pool with 1.5 HP 2 speed Jandy FloPro pump, Hayward EC75 Perflex DE filter, 11 4x12 Techno-Solis solar panels w/ Aquasolar controller, Aquabot Turbo T Robot Cleaner. Also LMI metering chlorine dispenser pump and HotSpring Jetsetter
    I use and endorse TFtestKits TF-100 from http://tftestkits.net
    ~Remember TFP counts on your donations to keep this site ad free~

  4. Back To Top    #4

    Join Date
    May 2012
    Location
    Endicott NY
    Posts
    87

    Re: AGP electrical question. Stranded vs solid THHN #12

    Thanks,

    There should be no vibration, It does not get connected directly to the motor.

    Thanks,

    Geo
    21 10500 gal AGP 52' sides, haward 3/4 hp xl pump and earth filter ec50
    Using the bbb method. Tf-100 kit. My first pool so learning in progress!

  5. Back To Top    #5
    Samantha Sabrina's Avatar
    Join Date
    Apr 2012
    Location
    Bloomsdale, Mo
    Posts
    346

    Re: AGP electrical question. Stranded vs solid THHN #12

    If you are running a supply line to a service panel, then you should use solid, and I would recommend going with #10 instead.

    You get a voltage drop over distance, and 50' is not a short span, and if you are going underground with your conduit then there will be even more loss.

    #12 will work, but if you ever decide to add other loads, or increase motor size, ect. ect, then pulling heavier wire now will save you down the road.

    Stranded wire from the breaker/service panel to the equipment will be fine, just make sure you size your wire properly.
    Samantha