    Pentair VS3050 Wiring

    Ok, dumb question...again... Wiring the Pump (220vac) to the ET panel GFCI. 1 hot to LN1, 1 hot LN2, where does the neutral go? Do I need a seperate Green (ground) wire from the panel to the pump?
    N Virginia
    -Leisure Moroccan 38' Fiberglass
    -19,800 Gallons
    -Pentair EasyTouch 4 w/IC40 Chlorinator,VS3050 Pump, Clean&Clear Plus 320 Cartridge Filter,Prowler 720 Robot Cleaner
    -1 Skimmer/ 3 Returns/2 Drains/2" Piping
    -3 Fiberstar Pal Treo LED lights/Wirtran
    -TF100 TestKit

  2. Back To Top    #2
    JasonLion's Avatar
    Join Date
    May 2007
    Location
    Silver Spring, MD
    Posts
    37,879

    Re: Pentair VS3050 Wiring

    You don't use a neutral with 240 volt power unless you are wiring a sub-panel.

    Yes, you need a ground to the pump. I'm not sure what you mean by "seperate".
    19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
    Creator of PoolMath and Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School

  3. Back To Top    #3

    Re: Pentair VS3050 Wiring

    The 220 GFCI breaker has connection for Load/Neutral/Load?
    N Virginia
    -Leisure Moroccan 38' Fiberglass
    -19,800 Gallons
    -Pentair EasyTouch 4 w/IC40 Chlorinator,VS3050 Pump, Clean&Clear Plus 320 Cartridge Filter,Prowler 720 Robot Cleaner
    -1 Skimmer/ 3 Returns/2 Drains/2" Piping
    -3 Fiberstar Pal Treo LED lights/Wirtran
    -TF100 TestKit

  4. Back To Top    #4
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    22,333

    Re: Pentair VS3050 Wiring

    The neutral wire on the breaker goes to the neutral bar in the panel.
    Dave J. TFP Moderator
    24' x 52" Round AGP. 2hp/¼hp SPL Power-Flo 2-speed pump. 200sqft Waterway Cartridge Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit

  5. Back To Top    #5
    JasonLion's Avatar
    Join Date
    May 2007
    Location
    Silver Spring, MD
    Posts
    37,879

    Re: Pentair VS3050 Wiring

    240 volt GCFI breakers come in two variants. Both kinds have two load connections and a white wire (usually coiled) coming out. The two load connections get wired to L1 and L2 on the pump, while the coiled white wire gets connected to neutral inside the panel. Some of them also have a third connection for load neutral. If yours has the load neutral connection you simply leave it unwired. In either case it is crucial that the coiled white wire coming out of the breaker get wired to the neutral bar inside the panel. In either case you also run a green ground wire from the panel ground bar to the pump. Sometimes the ground bar and neutral bar inside the panel are combined into one bar.
    19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
    Creator of PoolMath and Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School

  6. Back To Top    #6

    Join Date
    May 2011
    Location
    Orange County, CA
    Posts
    696

    Re: Pentair VS3050 Wiring

    Quote Originally Posted by JasonLion
    240 volt GCFI breakers come in two variants. Both kinds have two load connections and a white wire (usually coiled) coming out. The two load connections get wired to L1 and L2 on the pump, while the coiled white wire gets connected to neutral inside the panel. Some of them also have a third connection for load neutral. If yours has the load neutral connection you simply leave it unwired. In either case it is crucial that the coiled white wire coming out of the breaker get wired to the neutral bar inside the panel. In either case you also run a green ground wire from the panel ground bar to the pump. Sometimes the ground bar and neutral bar inside the panel are combined into one bar.
    It should be noted that on a sub-panel, the ground and neutral should NOT be tied together, as this would be in violation of the NEC code. Any sub-panel should have a separate neutral bar that is not bonded to the ground bar. In addition, if the sub-panel is attached to a separate structure (like a pool house or cabana), then a nearby ground rod must be installed and connected to the grounding terminal, along with a green wire run from the main panel. This is to minimize potential differences between the equipment ground at the main panel and the sub-panel.
    38K in ground pool with attached spa. Current equipment: Easytouch 8 (521150) with IC-60 SWCG with web control by Autelis, 1x Pentair IntelliFlo 011018 pump (for filter), 1x Pentair 2HP WhisperFlo pump (for waterfall), 2X Pentair IntelliBrite 5G 12V lights, Pentair MiniMax400 NG Heater, Pentair SMBW2060 DE filter. Zodiac Barracuda MX8 cleaner on dedicated cleaner line. Lighting/home automation controlled by Insteon/ISY-99i.