Thread: Installing Natural Gas Heater on AG

  1. Back To Top    #1

    Installing Natural Gas Heater on AG

    I have a Pentair MasterTemp 400,000 btu heater to be hooked up to an Intex. In reading through the heater manual, it talks about the "pressure switch" needing to be adjusted if the heater will be "below water level." I don't see that the manual explains this. I don't understand how to compare the placement of the heater to the water level - what part of the water should I consider relative to what part of the heater? That is; the bottom of the pool, the top of the water, or an inlet or outlet port?

    My pool will sit on a concrete pad. The pool equipment will be on pavers that will be close to level with the concrete the pool sits on, but I'm sure the grade is not exactly level between the concrete and where the pavers will be. Can someone tell me how to know if my heater installer (a freelance guy who supposedly knows pools) is supposed to adjust for below or at water level?

    Here is an excerpt from the manual:
    The water pressure switch is set in the factory at 3.00 PSI (± 0.75 PSI). This setting is for a heater installed at pool level. If the heater is to be installed more than 1’ above or below, the water pressure switch must be adjusted by a qualified service technician. See page 34, Figure 29.
    If the heater is installed more than 5’ above the pool or more than 4’ below the pool level, you will be beyond the limits of the pressure switch and a flow switch must be installed. Locate and install the flow switch externally on the outlet piping from the heater, as close as possible to the heater. Connect the flow switch wires in place of the water
    pressure switch wires.

    POOL: Intex ultra new in 2014 (32 x 16 x 52) (seasonal; on concrete pad covered with 1.5" extruded or whatever foam insulation sheets - ugly, but comfy); added a through-wall skimmer; I add salt for feel. EQUIPMENT: Pentair SuperFlo pump (1HP, 2SPD); Pentair cartridge filter (200 sq. ft); Pentair MasterTemp natural gas heater (400,000 btu) Climate/Location: Eastern Nebraska

  2. Back To Top    #2
    JasonLion's Avatar
    Join Date
    May 2007
    Silver Spring, MD

    Re: Installing Natural Gas Heater on AG

    The height is measured from the surface of the water to the top of the heater manifold. The manifold roughly corresponds to the location of the inlet and outlet pipe connection on the heater. You can see a diagram showing this on page 18 of this manual. A few pages before that it explains how to adjust the pressure switch. That manual might not exactly correspond to your heater, but yours should be quite similar.
    19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
    Creator of PoolMath and Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School