Thread: Hayward Super Pump 1hp. 230v vs 115v

  1. #1
    Senior Member
    Join Date
    May 2010
    Location
    Central Connecticut
    Posts
    110

    Hayward Super Pump 1hp. 230v vs 115v

    I am replacing my existing Hayward pump with another Hayward Superpump. My old pump was 115v. However, extra wire was run in the conduit to setup 230v circuit. I am trying to decide if I should stay with 115v or get the system wired for 230v. What is the benefit of running the pump at 230v vs 115v. Electric bill?

    Thanks,
    Rich
    18x36 IG 26,000 gal, 24" Sand filter Hayward 220, Jandy AE3000 heatpump and 1 HP pump. Circupool RJ45 SWG

  2. #2
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    20,909

    Re: Hayward Super Pump 1hp. 230v vs 115v

    If it's the same size pump it'll use the same amount of power whether it's 115 or 230 volts. The reason for running 230 volts is to cut down on wire size. A 1 sfhp 230 volt pump uses half the current that a 1 sfhp 115 volt pump does, so you can have smaller wires. Also since the voltage is higher the voltage drop will be less for the same distance.
    Dave J. TFP Moderator
    24' x 52" Round AGP. 1.5hp Dynamo pump. 24" Pentair Sand Dollar Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit
    You can stop SLAMing your pool when you pass the OCLT (You lose 1ppm or less FC overnight, & You have .5ppm CC's or less) & your water is clear.

  3. #3
    Senior Member Ohm_Boy's Avatar
    Join Date
    May 2007
    Location
    Orlando, FL
    Posts
    1,362

    Re: Hayward Super Pump 1hp. 230v vs 115v

    +1 for no difference in power consumption or cost. Since you already have everything (including the circuit breaker) set up for 120V, why not just stick with it? There's no practical benefit to changing at this point.
    [center:1kpalu48]Helpful Links: Pool School | CYA/Chlorine Chart | Pool Calculator[/center:1kpalu48]

  4. #4
    Administrator JasonLion's Avatar
    Join Date
    May 2007
    Location
    Silver Spring, MD
    Posts
    34,658

    Re: Hayward Super Pump 1hp. 230v vs 115v

    Given that the wire already exists and isn't changing size, there will be less voltage drop across the wire, and thus improved overall efficiency, if the pump is setup for 240 volts instead of 120 volts. The difference won't be very large, but it will be just a little more efficient at the higher voltage.
    19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
    TFP Admin. Creator of PoolMath and Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School

  5. #5
    Mod Squad jblizzle's Avatar
    Join Date
    May 2010
    Location
    Tucson, AZ
    Posts
    21,663

    Re: Hayward Super Pump 1hp. 230v vs 115v

    One other thing to consider is the timer you currently use. While a 115V timer switch probably could be used to switch one leg of the 230V circuit, the other would remain "live". This would function, but could pose a surprise to someone that did not turn off the breaker when working on the motor.

    Then again, maybe you are not supposed to use the 115V timer in this manner ... I am unsure.
    Jason, TFP Moderator
    18k IG pebblesheen pool, Hayward ProLogic P4 w/ T-15 SWG, Pentair 1HP 2-speed Superflo, Hayward 6020 DE filter
    500 sqft Heliocol solar panels, Dolphin Diagnostic Robotic Cleaner, TF-100 test kit w/ SpeedStir
    Gone: Hayward RS1500 pump, undersized DIY solar heater, Dolphin Dynamic Robotic Cleaner
    Pool School + Test Kit + PoolMath = A TROUBLE FREE POOL
    If you found TFP helpful and we saved you money ... Become a TFP Supporter!

  6. #6
    Senior Member
    Join Date
    May 2010
    Location
    Central Connecticut
    Posts
    110

    Re: Hayward Super Pump 1hp. 230v vs 115v

    Thank you all for the help. With no substantial benefit for the 230V, I will switch the motor wiring to 115V and stay with the 115v system. The Hayward 1HP Superpump comes wired for either 115v or 230V. (the default setting is 230v).

    However, I believe you just have to change a jumper in the back of the motor.
    18x36 IG 26,000 gal, 24" Sand filter Hayward 220, Jandy AE3000 heatpump and 1 HP pump. Circupool RJ45 SWG

  7. #7
    Senior Member
    Join Date
    May 2010
    Location
    Central Connecticut
    Posts
    110

    Re: Hayward Super Pump 1hp. 230v vs 115v

    Does anyone have experience or instructions on how to change the 1HP Hayward Super Pump from 230v to 115v. ? Is it a jumper change in the back of the motor? The manual with the pump didn't explain this.

    Thanks
    18x36 IG 26,000 gal, 24" Sand filter Hayward 220, Jandy AE3000 heatpump and 1 HP pump. Circupool RJ45 SWG

  8. #8
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    20,909

    Re: Hayward Super Pump 1hp. 230v vs 115v

    There's a diagram on the motor that shows how it's done. Mfg's use different motors on the pumps and different motors are switched differently.

    If you'll take a pic of the dataplate we'll walk you through it.
    Dave J. TFP Moderator
    24' x 52" Round AGP. 1.5hp Dynamo pump. 24" Pentair Sand Dollar Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit
    You can stop SLAMing your pool when you pass the OCLT (You lose 1ppm or less FC overnight, & You have .5ppm CC's or less) & your water is clear.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •