    Wiring 220V Toggle Switch for new Pump

    I replaced my old 2HP pump today and when opening the old toggle switch box, there was a fair amount of corrosion on the toggle switch. I picked up a two pole (30A) switch which showed the two hots connect to the bottom two screws (one on each side) and then the switch activates the two legs from the two top screws (one on each side).

    The old switch I pulled out was wired like a common 115V with two hots on one side, and then the legs on the other.

    Am I missing something? I wired it up as the manufacturer diagram. I can always check to see if both legs are dead when switched off, and both live when on, but I figured I'd ask here before throwing the breaker in case the pump could get upset if it sees only 115V of one leg, if I'm missing something.

    Here's the wiring diagram, and how I wired it. The Load here would be the pump.

    [attachment=0:19f0yn2o]2pole switch.JPG[/attachment:19f0yn2o]
    Attached Images Attached Images
    IG, 13,000 gal, concrete, DE, VS Intelliflo Pump, Intellichlor SWG

    San Diego, Ca.

  2. Back To Top    #2
    Ohm_Boy's Avatar
    Join Date
    May 2007
    Location
    Orlando, FL
    Posts
    1,344

    Re: Wiring 220V Toggle Switch for new Pump

    That should do it.
    [center:1kpalu48]Helpful Links: Pool School | CYA/Chlorine Chart | Pool Calculator[/center:1kpalu48]

  3. Back To Top    #3
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    22,347

    Re: Wiring 220V Toggle Switch for new Pump

    X2.
    Just to interject, a lot of 220 volt pump installations only switch one leg. I don't like that, but it's done a lot.
    Dave J. TFP Moderator
    24' x 52" Round AGP. 2hp/¼hp SPL Power-Flo 2-speed pump. 200sqft Waterway Cartridge Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit

  4. Back To Top    #4

    Join Date
    May 2009
    Location
    Youngsville NC
    Posts
    395

    Re: Wiring 220V Toggle Switch for new Pump

    Using the DPDT switch (as in OP's original post - switch is out by pump) is exactly how I have my pump hooked up after the timer in my shed. IMO, not doing it this way is setting yourself up for a potential shock or worse.
    16x32 IG 19,000 gallons, Pentair 1.5 hp Energy Efficient Superflo pump (348024),vinyl liner, Chlorine dispenser, Hayward S-244T sand filter

  5. Back To Top    #5

    Join Date
    Jun 2011
    Location
    San Diego California
    Posts
    88

    Re: Wiring 220V Toggle Switch for new Pump

    Quote Originally Posted by Bama Rambler
    X2.
    Just to interject, a lot of 220 volt pump installations only switch one leg. I don't like that, but it's done a lot.
    In the manual for the intelliflo, it stated both legs should switch at the same time. So as long as the switch manufacturer's drawing is correct, that is what should happen.

    Quote Originally Posted by scooperhsd
    Using the DPDT switch (as in OP's original post - switch is out by pump) is exactly how I have my pump hooked up after the timer in my shed. IMO, not doing it this way is setting yourself up for a potential shock or worse.
    Yep. The way it was wired previously seemed to leave one side of the load always hot, which woudl surprise someone if they thought the switch truely meant "off" when switched to "off".
    IG, 13,000 gal, concrete, DE, VS Intelliflo Pump, Intellichlor SWG

    San Diego, Ca.

  6. Back To Top    #6
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    22,347

    Re: Wiring 220V Toggle Switch for new Pump

    That's the reason I don't like just switching one leg. Even though you should make sure the breaker is off before touching it.
    Dave J. TFP Moderator
    24' x 52" Round AGP. 2hp/¼hp SPL Power-Flo 2-speed pump. 200sqft Waterway Cartridge Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit

  7. Back To Top    #7
    Ohm_Boy's Avatar
    Join Date
    May 2007
    Location
    Orlando, FL
    Posts
    1,344

    Re: Wiring 220V Toggle Switch for new Pump

    Naturally, switching one leg is common for 120V, where only one leg is hot.

    I hate to be this blunt, but wiring 220V that way is, in my opinion, irresponsible and dangerous, and done by people who don't want to put forth the time, money, or effort to do it right.
    [center:1kpalu48]Helpful Links: Pool School | CYA/Chlorine Chart | Pool Calculator[/center:1kpalu48]

  8. Back To Top    #8
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    22,347

    Re: Wiring 220V Toggle Switch for new Pump

    Quote Originally Posted by Ohm_Boy
    I hate to be this blunt, but wiring 220V that way is, in my opinion, irresponsible and dangerous, and done by people who don't want to put forth the time, money, or effort to do it right.
    Completely agree! My note was more of a warning so someone doesn't get caught off guard.
    Dave J. TFP Moderator
    24' x 52" Round AGP. 2hp/¼hp SPL Power-Flo 2-speed pump. 200sqft Waterway Cartridge Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit

  9. Back To Top    #9
    Ohm_Boy's Avatar
    Join Date
    May 2007
    Location
    Orlando, FL
    Posts
    1,344

    Re: Wiring 220V Toggle Switch for new Pump

    I should add to that:

    ...done by people who don't want to put forth the time, money, or effort to do it right.
    or have no business doing it at all.
    [center:1kpalu48]Helpful Links: Pool School | CYA/Chlorine Chart | Pool Calculator[/center:1kpalu48]

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •