    Hello everyone,

    I want to start off by saying this board has been a great reference since my wife and I bought our first house a couple years ago. The house came with a large, 45' x 20' inground pool and spill over spa and we knew very little about pool care prior to taking ownereship. It's been a fair amount of work, but, worth it.

    I'm hoping someone can point me in the right direction to troubleshoot our Pentair Minimax 400 Millivolt heater. When i run the heater, it will run for about 5 minutes or so, the heater turns off, the service LED becomes lit, then, goes out, and the heater comes on again. It will keep doing this until the water reaches the correct temperature.

    It did this when we first moved in. I called the home warranty company who sent out a Pentair service tech who said the issue was likely due to an undersized gas meter. I had the gas company come out and replace the meter with a larger unit which didn't fix the issue. The Pentair tech came back and replaced the flow valve because it was badly corroded; this fixed problem up until recently.

    I checked the flow valve and it looked fine; almost new. I also removed the service panels and made sure everything was cleaned out and all electrical connections were good. Does anyone have any suggestions i could try? I'm comfortable with safely working on this heater and replacing components, I just need to know what to check.

    Thanks,

    Joe
    45' x 20' (apprx 37,500 gallons) IG plaster pool. WhisperFlo 2HP, 2-speed pump
    Pentair MiniMax 400 MilliVolt heater, PentAir cartridge filter.

  2. Back To Top    #2
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    22,347

    Re: Pentair Minimax 400 questions

    That sure sounds like the flow switch. Did you remove it and make sure it was clean and working correctly?
    Dave J. TFP Moderator
    24' x 52" Round AGP. 2hp/¼hp SPL Power-Flo 2-speed pump. 200sqft Waterway Cartridge Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit

  3. Back To Top    #3

    Re: Pentair Minimax 400 questions

    Thank you for the reply. I did take the "flow valve" out, which looks somewhat like a copper or bronze thermostat on a car and is installed in the water in/out headers on the heater and it looked fine - I didn't see much that could require cleaning. The other one was replaced because the pool chemistry had been bad at some point before we took ownership (home was foreclosure) and literally disintegrated.

    Is the flow switch something different? I could try replacing the flow valve, but, I would need to purchase one at $100.00 or so.

    Joe
    45' x 20' (apprx 37,500 gallons) IG plaster pool. WhisperFlo 2HP, 2-speed pump
    Pentair MiniMax 400 MilliVolt heater, PentAir cartridge filter.

  4. Back To Top    #4
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    22,347

    Re: Pentair Minimax 400 questions

    Hopefully one of the heater guys will see this and respond.
    Dave J. TFP Moderator
    24' x 52" Round AGP. 2hp/¼hp SPL Power-Flo 2-speed pump. 200sqft Waterway Cartridge Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit

  5. Back To Top    #5

    Join Date
    May 2011
    Location
    Orange County, CA
    Posts
    696

    Re: Pentair Minimax 400 questions

    We have a Minimax 400 as well, and I can tell you that these heaters need a properly sized gas line to work. When we purchased our house and got the pool running, the heater would not start. I called out a pool guy who first thought it was spider webs clogging the burners. But, after much trial and error, he tested the pressure on the gas line and found it to be quite low. It was keeping the heater from lighting up. So, we had to replace the gas line which was corroding. It was also undersized at 1". We ended up having it replaced with a 1 1/2" PE line, which was expensive. But, now the heater works without a hitch.

    As others have said, it would be worth checking the pressure valve on the heater. But, also do a pressure test to make sure there is enough NG coming through the line.
    38K in ground pool with attached spa. Current equipment: Easytouch 8 (521150) with IC-60 SWCG with web control by Autelis, 1x Pentair IntelliFlo 011018 pump (for filter), 1x Pentair 2HP WhisperFlo pump (for waterfall), 2X Pentair IntelliBrite 5G 12V lights, Pentair MiniMax400 NG Heater, Pentair SMBW2060 DE filter. Zodiac Barracuda MX8 cleaner on dedicated cleaner line. Lighting/home automation controlled by Insteon/ISY-99i.

  6. Back To Top    #6

    Re: Pentair Minimax 400 questions

    Thanks for the suggestions. I will check the pressure valve sometime this weekend and hopefully be able to resolve the issue. Fortunately for us, we already had 1.5" gas piping going to the pool heater and the gas pressure has been fine since switching out the gas meter.
    45' x 20' (apprx 37,500 gallons) IG plaster pool. WhisperFlo 2HP, 2-speed pump
    Pentair MiniMax 400 MilliVolt heater, PentAir cartridge filter.

  7. Back To Top    #7

    Re: Pentair Minimax 400 questions

    I've got a Minimax 400 that's been pretty reliable over the years (8+). However, recently my spa has stopped producing bubble when the pump is running. I'm thinking that maybe the heater is plugged, or the flow valve is malfunctioning. Can anyone describe what that flow valve (spring, copper "thermostat" looking thing) actually does? Is there any way to test it?

  8. Back To Top    #8
    Richard320's Avatar
    Join Date
    Jan 2010
    Location
    San Dimas, CA (LA County)
    Posts
    18,768

    Re: Pentair Minimax 400 questions

    Quote Originally Posted by contraption
    I've got a Minimax 400 that's been pretty reliable over the years (8+). However, recently my spa has stopped producing bubble when the pump is running. I'm thinking that maybe the heater is plugged, or the flow valve is malfunctioning. Can anyone describe what that flow valve (spring, copper "thermostat" looking thing) actually does? Is there any way to test it?
    I doubt the heater has anything to do with it. All it does is warm the water.

    Somewhere there's an air intake that's connected to a type of venturi, that adds air and hence bubbles to the spa. Mine looks like an uncapped pipe with an elbow on it. There's probably some leaves or spider webs, something, blocking it. No air gets in, no bubbles.

    Find the air intake, and run a plumber's snake down it. Or a drain king.
    16K freeform gunite with spa; Pentair 4000 DE filter; Century Whisperflow 1 HP; Pentair Minimax heater.
    Troublefree does not mean Maintenancefree. It's like brushing your teeth: You can spend a couple minutes a day and pennies a week or go to the dentist once a year and spend several thousand dollars.
    A pool is like a pet - you have to feed it every day, even the days you don't want to play with it!

  9. Back To Top    #9

    In the Industry
    Pool Clown's Avatar
    Join Date
    Sep 2008
    Location
    Silicon Valley, CA
    Posts
    1,637

    Re: Pentair Minimax 400 questions

    Quote Originally Posted by Richard320
    Quote Originally Posted by contraption
    I've got a Minimax 400 that's been pretty reliable over the years (8+). However, recently my spa has stopped producing bubble when the pump is running. I'm thinking that maybe the heater is plugged, or the flow valve is malfunctioning. Can anyone describe what that flow valve (spring, copper "thermostat" looking thing) actually does? Is there any way to test it?
    I doubt the heater has anything to do with it. All it does is warm the water.

    Somewhere there's an air intake that's connected to a type of venturi, that adds air and hence bubbles to the spa. Mine looks like an uncapped pipe with an elbow on it. There's probably some leaves or spider webs, something, blocking it. No air gets in, no bubbles.

    Find the air intake, and run a plumber's snake down it. Or a drain king.
    To add to that, those venturi require a certain amount of (water)flow to properly pull the air in as well. check and make sure all your pump baskets are clear of debris and no excessive pressure on the filter gauge!
    Factory Warranty Station for:
    Jandy/Zodiac, Pentair, Sta-Rite, Raypak, Polaris,
    and Paramount pool cleaning systems.

  10. Back To Top    #10

    Re: Pentair Minimax 400 questions

    thanks guys. the top of my venturi (with blower on top) is clear but maybe there's something down inside, so i'll check again. As Richard320 suggested, I'm thinking that the low bubble problem is a symptom of low flow, but i can't seem to find any restriction. I've check the JVAs, T-cell, pump, and run the filter without cartridges. I've also replaced the (thankfully serviceable) check valve innards over on the spa makeup circuit. The only things left are 1 inline (glued in) check valve that i can't inspect, the heater, a weak pump, or some line restriction. The funny thing is that the pressure is running about normal, maybe a couple of psi higher than when it was built 8 years ago, but nothing major.

    I just replaced the impeller and diffuser on the pump, but that didn't change anything. Has anyone ever seen a motor (3HP whisperflo) go "soft" where it can't pump like it used to? Would a failed or failing run capacitor affect the motor power?

    The pump did pop the breaker for the very first time a few days ago and would struggle to start afterward. For a week or so before that, the bubbles were decreasing day by day. when I took the pump apart I did find that the impeller seemed a little bit stuck with some small, tough, leaves stuck in the small gap between the impeller nose and the diffuser ring. I replaced both parts (i had the parts on hand as i've been thinking this problem might be "blow by" inside the pump), but as I said, no luck there. It is at least running again, but still no bubbles.

    I'm usually really good at detective work like this, but this one has me flummoxed.

    Do check valves get stuck (this one is after the filter)? Motors go soft? Heaters get clogged?

  11. Back To Top    #11

    In the Industry

    Join Date
    Mar 2011
    Posts
    441

    Re: Pentair Minimax 400 questions

    Yes, check valves can and do get stuck. The flow control "flap" type tend to tear the rubber mount off causing the disk to block the outlet port.

    On a 3hp pump, If the pressure is over 30, there difference between it flowing, and not could only be 8 psi,
    20X40 30,000 gallon gunite pool

  12. Back To Top    #12

    Re: Pentair Minimax 400 questions

    @racket: regarding the check valve - is there any way to figure out if the flapper is busted? it appears to be a sealed "capsule". The other one I have (spa makeup) has a screw-on lid and replaceable spring loaded assembly inside (that i've replaced). It seems like i might need a snake style inspection camera to get inside the capsule one. In your experience, is failure likely after 8 years of service?

    My pressure with only the main pump on (no solar) runs about 22-24psi with clean cartridges. It's always been higher with the spa on, maybe 30 or 32 psi. It might be a bit higher than that now, but not as high as I imagine it would go if the pump were deadheaded.

  13. Back To Top    #13

    In the Industry

    Join Date
    Mar 2011
    Posts
    441

    Re: Pentair Minimax 400 questions

    A 3hp pump deadheaded might be only 40-45psi Some older pumps might only hit ~38
    20X40 30,000 gallon gunite pool

  14. Back To Top    #14

    In the Industry

    Join Date
    Mar 2011
    Posts
    441

    Re: Pentair Minimax 400 questions

    Quote Originally Posted by contraption
    It seems like i might need a snake style inspection camera to get inside the capsule one. In your experience, is failure likely after 8 years of service?.
    The only way I know would be to tap in a pressure gauge on the effluent (outlet) side of the check valve. Instead of worrying about renting a camera to inspect it, I would replace it with a Pentair or Jandy check valve with replaceable internals.
    20X40 30,000 gallon gunite pool

  15. Back To Top    #15

    In the Industry
    Pool Clown's Avatar
    Join Date
    Sep 2008
    Location
    Silicon Valley, CA
    Posts
    1,637

    Re: Pentair Minimax 400 questions

    Quote Originally Posted by contraption
    The only things left are 1 inline (glued in) check valve that i can't inspect
    Thats my vote. Replace it. Even if it's not it, Now you got a serviceable check valve.