    morning startup trips heat pump circuit breaker

    Hello
    My pool is 3 years old and I just had to replace my Hayward pump 1.5 hp. Several times a week when the timer starts the pool in the morning the heater will not come on, the circuit breaker trips. Could this be somehow related as to why the pump went bad? I was hoping the new pump would correct this but it didn't
    The pump is on a separate 220 amp circuit and the heater on it's own 440 circuit. I had the heat pump company come out 2 years ago and it was working as it should.
    I'm thinking a delay of some type is that possible?

    Thanks
    Tom

  2. Back To Top    #2
    Mod Squad JohnT's Avatar
    Join Date
    Apr 2007
    Location
    SW Indiana
    Posts
    9,089

    Re: morning startup trips heat pump circuit breaker

    Is it the heater or pump circuit breaker that trips? Does the timer try to turn them both on at the same time or is there a delay to allow the flow to start before the heater powers on?
    TFP Moderator
    20K Gallon 20X36 Vinyl Inground
    Hayward S244T Sand Filter with 1HP Whisperflo Pump. Liquidator C-201 and Solar Heat

  3. Back To Top    #3

    Re: morning startup trips heat pump circuit breaker

    It is the heater that trips and yes they come on together by the timer
    Tom

  4. Back To Top    #4

    Re: morning startup trips heat pump circuit breaker

    Is the heat pump 440 volts? What is the amp rating of the circuit breaker for the heat pump?

  5. Back To Top    #5

    Re: morning startup trips heat pump circuit breaker

    I will get that info and get back to you. Not positive on the 440 but I think so
    Tom

  6. Back To Top    #6

    Re: morning startup trips heat pump circuit breaker

    This is what I have
    Looks like 80 amps for heater and 40 for pump??



    Tom

  7. Back To Top    #7
    linen's Avatar
    Join Date
    Jul 2010
    Location
    Twin Cities, MN
    Posts
    8,649

    Re: morning startup trips heat pump circuit breaker

    To me it looks like you pump is 20 amp, 240 V and you heater is 40 amp, 240 V. What amperage service do you have running to the pool subpanel? You may want to switch out your 40 amp breaker, with a new one to see if it is a breaker problem.
    TFP Expert who uses Pool School and my TF100 test kit along with PoolMath for my: Round 11K gallon AGP with deep end, 20" sand filter, Matrix 1hp 2spd, 6 2ftX20ft solar panels (and solar cover!), Intex SWCG (copper bars disconnected) and a Rubadub hot tub (chlorine). The SLAM process is not finished until: 1. CC < 0.5 ppm, 2. An OCLT < 1.0 ppm and, 3. The water is crystal clear.

  8. Back To Top    #8

    Re: morning startup trips heat pump circuit breaker

    I have 80 amps going to panel. I'll switch out the breaker
    thanks