Thread: running an electrical line for my SWG.

  1. Back To Top    #1

    Join Date
    Jan 2011
    Location
    south louisiana
    Posts
    43

    running an electrical line for my SWG.

    Im about to run an electrical line 100 feet from my electrical panel to my SWG for power. Its going to be 220 volts and its going to be underground, the cable not the pump. I might also want to run my 110 that goes to my pump on that same line cable. Any suggestions on what kind of line/cable I need? Where should I get it from? Thanks. Any and all help is greatly appreciated and needed.
    dont know how many gallons i got but if i remember correctly the pool is about 20'wide and 32' long and goes from 4 to 8 foot. I think i remember someone telling me about 35k in gallons but i could be off.

    filter type-Sand

    its an in-ground plaster

    dont know the size of the pump or size of the filter.

    http://m1099.photobucket.com/albums/vodkacop/

  2. Back To Top    #2
    dremin2flyhi's Avatar
    Join Date
    Jun 2010
    Location
    Darlington, SC
    Posts
    121

    Re: running an electrical line for my SWG.

    will you be using conduit or direct burial wire--If you do it has to be UF rated wire .. Also I would make the pump or SWG the same voltage -- it is not a good practice to make a Branch circuit from a 220 to a 110 off the same circuit ... I would not use less than a 10/2 at the long range --not knowing the amp rating of the pump. If you can fill in some of the blanks there -- I can try and help out some more.
    24' x52" Sharkline Venture (May 2016) ABG (13,500)
    Hayward S180T15932S --Sand filter/ Flo-Matrix pump pack
    Aquatrol-RJ SWG-- Nitelighter NLMC
    Dolphin E10
    Duraspa G2- Premium hot tub --Rotomold style

  3. Back To Top    #3

    Join Date
    Dec 2009
    Location
    Central Massachusetts
    Posts
    2,690

    Re: running an electrical line for my SWG.

    You can't use direct burial wire for a pool pump. The ground has to be insulated and direct burial has a bare copper ground.
    Does the SWCG have to be 220? If not, just run the SWCG off the same line as the pump. Tie the pump and the SWCG into the load side of a timer.
    You dont want a 120 branch circuit off of the 220.
    14,000 gallon IG, Vinyl. Hayward 3/4 hp superpump, Penatair IC40 SWCG, Pentair automation, Hayward sand filter, Aqua Comfort heat pump, Hayward 400k Lo-Nox LP heater.

  4. Back To Top    #4

    Join Date
    Jan 2011
    Location
    south louisiana
    Posts
    43

    Re: running an electrical line for my SWG.

    Well the pentair we have now is 1.5hp, 115 volts and 12 amps and the wire running to it is underground. So in guessing it is AC, armored cable, and its using 110. I would have no idea how to change a 110 to a 220 or a 220 to a 110. As for making the SWG a 110 I just didn't think you could run something that needed 220 on a 110.
    dont know how many gallons i got but if i remember correctly the pool is about 20'wide and 32' long and goes from 4 to 8 foot. I think i remember someone telling me about 35k in gallons but i could be off.

    filter type-Sand

    its an in-ground plaster

    dont know the size of the pump or size of the filter.

    http://m1099.photobucket.com/albums/vodkacop/

  5. Back To Top    #5
    JasonLion's Avatar
    Join Date
    May 2007
    Location
    Silver Spring, MD
    Posts
    37,879

    Re: running an electrical line for my SWG.

    Almost all of the common SWGs can be reconfigured for either 115 or 230.
    19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
    Creator of PoolMath and Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School

  6. Back To Top    #6
    Ohm_Boy's Avatar
    Join Date
    May 2007
    Location
    Orlando, FL
    Posts
    1,344

    Re: running an electrical line for my SWG.

    You may wish to consult with an electrician who can take a look at your particular configuration of equipment, terrain, and resources and recommend a plan for your install which fits your situation and local codes. The physical aspects of digging a trench, laying in the conduit, and pulling the wire isn't overly complicated, but there are considerations which depend upon the details. Wire size will depend on the voltage, the load of the equipment, and the length of the whole run. Conduit size will depend on wire size and fill percentage. The trench will need to be at least 18", and if there is more than four 90 degree elbows there will have to be a pull box somewhere, etc. You can certainly do the work yourself, but a professional opinion by someone knowledgeable who can actually see your setup would be the best starting point.
    [center:1kpalu48]Helpful Links: Pool School | CYA/Chlorine Chart | Pool Calculator[/center:1kpalu48]

  7. Back To Top    #7

    Join Date
    Jan 2011
    Location
    south louisiana
    Posts
    43

    Re: running an electrical line for my SWG.

    Will it be just a regular electrician I need or one who specializes in pool pumps or swimming pool/outdoor wiring?
    dont know how many gallons i got but if i remember correctly the pool is about 20'wide and 32' long and goes from 4 to 8 foot. I think i remember someone telling me about 35k in gallons but i could be off.

    filter type-Sand

    its an in-ground plaster

    dont know the size of the pump or size of the filter.

    http://m1099.photobucket.com/albums/vodkacop/

  8. Back To Top    #8
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    22,347

    Re: running an electrical line for my SWG.

    Just to add fuel to the fire. At 100' 15 amps and 120 volts, you'll need #10 AWG wire. If it were me, I'd go ahead and set a small sub panel near there and use that to power the pump, swcg, lights, etc.
    Dave J. TFP Moderator
    24' x 52" Round AGP. 2hp/¼hp SPL Power-Flo 2-speed pump. 200sqft Waterway Cartridge Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit

  9. Back To Top    #9

    Join Date
    May 2011
    Location
    lebanon tn
    Posts
    370

    Re: running an electrical line for my SWG.

    What bama said- I'd run like a 50 amp 220 subpanel, then have very short runs from the subpanel to all the pool stuff-
    and the subpanel will break up the 220 into the 110 legs you need-
    There is not a problem running a 110 leg from a 220 circuit- heck, your whole house is a 220 leg off of a 440 circuit, powered through a transformer from like 7500 volts!
    It needs to be wired correctly, but is not a problem!
    24ft x 52in AGP 18000 gal
    sand filter, 200#,1.5 hp single speed pump
    Wood deck (still in progress...)

  10. Back To Top    #10

    Join Date
    Dec 2009
    Location
    Central Massachusetts
    Posts
    2,690

    Re: running an electrical line for my SWG.

    Quote Originally Posted by madwil

    There is not a problem running a 110 leg from a 220 circuit- heck, your whole house is a 220 leg off of a 440 circuit, powered through a transformer from like 7500 volts!
    It needs to be wired correctly, but is not a problem!
    We were adding the caution that its not good pratice to run a 120VAC circuit off of an existing 240VAC circuit by sharing a hot leg. Besides, a 2 wire 240VAC circuit has no neutral, and you need one for a 120VAC circuit.

    Quote Originally Posted by madwil
    your whole house is a 220 leg off of a 440 circuit
    Most residential 200 amp service panels have two, 120VAC legs on opposite phases.
    14,000 gallon IG, Vinyl. Hayward 3/4 hp superpump, Penatair IC40 SWCG, Pentair automation, Hayward sand filter, Aqua Comfort heat pump, Hayward 400k Lo-Nox LP heater.

  11. Back To Top    #11

    Join Date
    Jan 2011
    Location
    south louisiana
    Posts
    43

    Re: running an electrical line for my SWG.

    Quote Originally Posted by Bama Rambler
    Just to add fuel to the fire. At 100' 15 amps and 120 volts, you'll need #10 AWG wire. If it were me, I'd go ahead and set a small sub panel near there and use that to power the pump, swcg, lights, etc.

    It will be jump the pump and swcg on it. There's nothing else to hook up. Was told I could use one line to run my pump and swcg. I was planning on just undigging the old line that the pump runs on now and putting the new line next to it and burying them both.
    dont know how many gallons i got but if i remember correctly the pool is about 20'wide and 32' long and goes from 4 to 8 foot. I think i remember someone telling me about 35k in gallons but i could be off.

    filter type-Sand

    its an in-ground plaster

    dont know the size of the pump or size of the filter.

    http://m1099.photobucket.com/albums/vodkacop/

  12. Back To Top    #12

    Join Date
    Jan 2011
    Location
    south louisiana
    Posts
    43

    Re: running an electrical line for my SWG.

    I was also told I should add another panel by the pumps like y'all were talking about. What kind of housing would I need to protect it from the elements? I know I need something to house the swcg in so more then likely it would have both in it. So something not to big but not really small.
    dont know how many gallons i got but if i remember correctly the pool is about 20'wide and 32' long and goes from 4 to 8 foot. I think i remember someone telling me about 35k in gallons but i could be off.

    filter type-Sand

    its an in-ground plaster

    dont know the size of the pump or size of the filter.

    http://m1099.photobucket.com/albums/vodkacop/

  13. Back To Top    #13


    Join Date
    Sep 2008
    Location
    The Woodlands, Texas, USA
    Posts
    243

    Re: running an electrical line for my SWG.

    Go to loses and buy a smAll subpanel. Get an NEMA outdoor/weather rated on with room for enough breakers for your stuff.

    I would look into reconfiguring your pump for 220 while your doing all this anyway.
    IG 24k plaster with overflow spa. Goldline PS-8 SWG. Tristar 0.75 HP filter pump, Polaris 280, large cartridge filter, 400k BTU NG Max-E-Therm HD, SR Smith Turbo Twister, Life Saver pool fence, ORP managed.

  14. Back To Top    #14
    JasonLion's Avatar
    Join Date
    May 2007
    Location
    Silver Spring, MD
    Posts
    37,879

    Re: running an electrical line for my SWG.

    I still think that it is extremely likely that the SWG can be reconfigured for 115 volts or the pump can be reconfigured for 230 volts and the pump and SWG can share a circuit, which would save a fair bit of the effort and expense that you all are proposing and be safer (since the SWG then could not come on unless the pump was also on).
    19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
    Creator of PoolMath and Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School