    Need conduit type recommendation for inside pool shed

    I have to make some wiring changes asap inside an existing covered pool shed and am looking for feedback on conduit choices.

    Application is between electrical panel or Intermatic timers and pumps, a gas heater and a GFCI outlet. No wiring is LEAVING the shed, I'm just reconnecting things inside.

    Approvable options seem to be emt, liquidtight and some form of PVC or CPVC. An insulated ground wire would be used along with the appropriate gage THWN wire inside.

    Connection between conduit and load would be with short length of liquidtite.

    A separate Bond wire will run amongst the various clientele.

    I'll check with my AHJ, but would appreciate thoughts on preferences where there is latitude.
    Thanks very much!
    ~29K gal, 20'x36' rectangular, outdoor IG plaster, built in '74. Intelliflo VF; Sta-rite system 3 w/300sq ft. Liquidator 8Gal-3/8ug; Polaris 380 sweep & PB4 booster. Equip. is in shed on ground level pad.

  2. Back To Top    #2

    Join Date
    May 2007
    Location
    South Central NJ
    Posts
    3,192

    Re: Need conduit type recommendation for inside pool shed

    Liquidtight Flex is fine for whip end connections here in NJ.

    Scott
    Owner of - PoolGuyNJ LLC
    Expert Pool and Spa Repairs, Renovations, and Augmentation. Helping people decide what is the right gear for meeting their needs. Expectations Set, Expectations Met, No Surprises.

  3. Back To Top    #3
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    22,331

    Re: Need conduit type recommendation for inside pool shed

    Liquidtight should pass inspection for anything shorter than 6'. I like to hard pipe everything except the pump, but it's usually not required.

    I'm sure you know it, but you'll need approved connectors on your bonding conductor and it'll also be ran outside your conduit.
    Dave J. TFP Moderator
    24' x 52" Round AGP. 2hp/¼hp SPL Power-Flo 2-speed pump. 200sqft Waterway Cartridge Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit

  4. Back To Top    #4

    Join Date
    Dec 2009
    Location
    Central Massachusetts
    Posts
    2,690

    Re: Need conduit type recommendation for inside pool shed

    Quote Originally Posted by Bama Rambler
    Liquidtight should pass inspection for anything shorter than 6'. .
    Another vote for liquid tight.

    As an FYI, the 6 feet or under requirement is for unstrapped "whips" that connect the equipment from a panel or J-box. Thats under section 680. These cant be over 6 feet. However, there's no place that says you cant run liquid tight as long a distance as you want as long as it's properly strapped to a structure. Thats covered by 351. Some inspectors actually get this wrong and flunk you for liquid tight over 6 feet. That is wrong and you can call them on it. In fact, you can bury liquid tight up to 1". Anything over 1" has to be strapped above ground since >1" isnt crush rated.
    Another one of those "ambiguous" parts of the NEC that needs to be cleaned up.
    14,000 gallon IG, Vinyl. Hayward 3/4 hp superpump, Penatair IC40 SWCG, Pentair automation, Hayward sand filter, Aqua Comfort heat pump, Hayward 400k Lo-Nox LP heater.

  5. Back To Top    #5
    Mod Squad Bama Rambler's Avatar
    Join Date
    Jun 2009
    Location
    SouthWest Alabama
    Posts
    22,331

    Re: Need conduit type recommendation for inside pool shed

    BK is right of course, but it's usually not worth it to call the inspector out. They'll just find something else to get you on. I just keep the flex to under 6' then there's no question.
    Dave J. TFP Moderator
    24' x 52" Round AGP. 2hp/¼hp SPL Power-Flo 2-speed pump. 200sqft Waterway Cartridge Filter. 45MHP2(3GPD) Stenner Peristaltic Pump
    Pool School ----- Pool Math ----- TF-Test Kit

  6. Back To Top    #6

    Join Date
    Mar 2010
    Location
    "Lamorinda" California
    Posts
    52

    Re: Need conduit type recommendation for inside pool shed

    Quote Originally Posted by Bama Rambler
    Liquidtight should pass inspection for anything shorter than 6'. I like to hard pipe everything except the pump, but it's usually not required.
    Swell.
    I was hoping to use Liquid tight non-metallic and the associated approved fittings. Max. length looks like ~16 feet.

    My understanding (subject to AHJ acceptance) from NEC 680.21 is that liquid tight LNFC-B, specifically, is approved at any length if properly supported IF in a dwelling or enclosed structure like a shed. I.E., it can then be any "chapter 3" approved conduit.

    Mike Holt's NEC site:
    http://www.mikeholt.com/newsletters....y&letterID=802 Has some great NEC section 680 references per this.

    Quote Originally Posted by Bama Rambler
    I'm sure you know it, but you'll need approved connectors on your bonding conductor and it'll also be ran outside your conduit.
    Yes, thanks, I appreciate the reminder. Of course what's "approved" depends on whether NEC 2005 or 2008 criteria are applied.

    Thanks very much guys!
    ~29K gal, 20'x36' rectangular, outdoor IG plaster, built in '74. Intelliflo VF; Sta-rite system 3 w/300sq ft. Liquidator 8Gal-3/8ug; Polaris 380 sweep & PB4 booster. Equip. is in shed on ground level pad.