Unknown Part

JoMain

0
Mar 17, 2011
3
Can someone tell me what this piece is, I believe it is on the auto fill line, 3/4" PVC piping

countryinnunknown.jpg


Thanks!
 
Thank you very much! It looks slightly more complicated than some of the backflow valves i have seen in the past. What can I replace it with and do I need to involve the city if it is located at a hotel?
 
JoMain said:
it is leaking, i can find double backflow preventers but what is the piece that is pointing downward?

Watts call that a reduced pressure "zone assembly"

Many municipalities require them because they are more expensive than a standard double check valve

The piece on the bottom is calls an "air gap" which isnt needed if its just draining on the floor like it appears to be doing.
 