Thread: Spa electricity issues

  1. Back To Top    #1
    Chatabox's Avatar
    Join Date
    Apr 2016
    Location
    Queensland, Australia
    Posts
    64

    Spa electricity issues

    I seem to be having issues with my spa. Our solar system wasn't putting anything back to the grid, and we were concerned as we suddenly have a very high consumption - 33+ kWh per day is being consumed. Our previous reading with the spa and prior to the solar being installed was about 18kwh. So it was a concern as it had jumped so much. We did a daily test with turning one large appliance off, and it's the spa that's draining all our power. I have no idea where to start even looking!

    We have the spa running on "standard mode" so the filter runs (1.5kw) and then the blowers turn on every 45ish minutes to an hour for a 15 minute cycle (3kw). We had a timer installed on the spa, so it runs from 9am - 5pm to keep the heat up, and to only use solar. We didn't have any issue in the beginning, and the solar production outweighed the spa consumption. But now it's blown right out! Where do I even begin?
    5900 litre or 1558 gal above ground swim spa. Approx 5 years old and heated to 37 degrees celsius year round. Cartridge filter, ozonator, Nature2 mineral sanitiser, Aqua Health non chlorine based shock, Lithium Hypochlorite dosed at each spa usage. Filled using mostly stored rainwater from tanks, and town water when the tanks are drained.

  2. Back To Top    #2

    Join Date
    Apr 2013
    Location
    Sacramento, CA
    Posts
    2,769

    Re: Spa electricity issues

    With the timer and the heating element. That's the only thing that is that large a drain on power. You may have a problem with your main board. You should have a service person out to look at it.
    22k gallon IG pebblefina, Jandy 1.5 HP VS, Jandy CV Cartridge filter, Fafco solar panels, Polaris 360 supply side cleaner, waterfall

  3. Back To Top    #3
    mas985's Avatar
    Join Date
    May 2007
    Location
    Pleasanton, CA
    Posts
    11,490

    Re: Spa electricity issues

    Spa heaters use a tremendous amount of energy.

    Do you have a cover on the spa?

    The previous measurement, was that with the heater actually on?

    Why do the blowers go on every 45 mins?
    Mark
    Hydraulics 101; Pump Ed 101; Pump/Pool Spreadsheets; Pump Run Time Study; DIY Acid Dosing; DIY Cover Roller
    18'x36' 20k plaster, MaxFlo SP2303VSP, Aqualogic PS8 SWCG, 420 sq-ft Cartridge, Solar, 6 jet spa, 1 HP jet pump, 400k BTU NG Heater

  4. Back To Top    #4
    Chatabox's Avatar
    Join Date
    Apr 2016
    Location
    Queensland, Australia
    Posts
    64

    Re: Spa electricity issues

    Yes, the comparison from the before and after is factored the exact same way. We have owned the spa for a year (new home owners where spa was already onsite) and it's only this past 3 months that have been having issues. Yes, we have insulated covers on it. I think the blowers go on to move around the water?
    5900 litre or 1558 gal above ground swim spa. Approx 5 years old and heated to 37 degrees celsius year round. Cartridge filter, ozonator, Nature2 mineral sanitiser, Aqua Health non chlorine based shock, Lithium Hypochlorite dosed at each spa usage. Filled using mostly stored rainwater from tanks, and town water when the tanks are drained.

  5. Back To Top    #5
    mas985's Avatar
    Join Date
    May 2007
    Location
    Pleasanton, CA
    Posts
    11,490

    Re: Spa electricity issues

    Blowers just inject air into the water stream. It is the pump that moves the water around.

    Are the pumps on all the time or by blowers are you really just referring to the spa jets? The spa may use venturis which pull in air only when the pump is on and that may be what you are seeing?

    Also, when you say you take power readings, exactly how are you doing that?
    Mark
    Hydraulics 101; Pump Ed 101; Pump/Pool Spreadsheets; Pump Run Time Study; DIY Acid Dosing; DIY Cover Roller
    18'x36' 20k plaster, MaxFlo SP2303VSP, Aqualogic PS8 SWCG, 420 sq-ft Cartridge, Solar, 6 jet spa, 1 HP jet pump, 400k BTU NG Heater

  6. Back To Top    #6
    Chatabox's Avatar
    Join Date
    Apr 2016
    Location
    Queensland, Australia
    Posts
    64

    Re: Spa electricity issues

    The pump is on whenever the spa timer is on. But the jets (we call them blowers here, the other ones that pump air through are the bubblers) come on occasionally. Maybe it's longer the. Every hour or so. But it feels like I hear it very regularly when I'm home.

    We had a monitoring system put in. It takes a reading of the solar generated, the solar exported to the grid, and the electricity pulled from the grid. We also check against the reading on the solar inverter, and the readings on the metre box to make sure they match.
    5900 litre or 1558 gal above ground swim spa. Approx 5 years old and heated to 37 degrees celsius year round. Cartridge filter, ozonator, Nature2 mineral sanitiser, Aqua Health non chlorine based shock, Lithium Hypochlorite dosed at each spa usage. Filled using mostly stored rainwater from tanks, and town water when the tanks are drained.

  7. Back To Top    #7
    mas985's Avatar
    Join Date
    May 2007
    Location
    Pleasanton, CA
    Posts
    11,490

    Re: Spa electricity issues

    I don't see why you would need the blowers to come on regularly. In fact, they are probably causing the spa to lose heat.

    Anyway, you have a 8 hour run time for the pump at 1.5kw which is 12 kwh plus 2 hours (8 hours * 25%) of run time for the blower at 3 kw or 6 kwh which is 18 kwh total. That is what you measured previously so I don't think it was with the heater on. Could not have been because the pump and blowers use that much.

    My guess is the heater uses the rest of that (15 kwh). If something was stuck on, you would notice the water getting much hotter than the setting. If something was shorted, it would be getting hot as well or tripping a breaker. You can't use that much power without noticing.

    Can you take instantaneous power measurements with the heater on vs off?
    Mark
    Hydraulics 101; Pump Ed 101; Pump/Pool Spreadsheets; Pump Run Time Study; DIY Acid Dosing; DIY Cover Roller
    18'x36' 20k plaster, MaxFlo SP2303VSP, Aqualogic PS8 SWCG, 420 sq-ft Cartridge, Solar, 6 jet spa, 1 HP jet pump, 400k BTU NG Heater

  8. Back To Top    #8
    Chatabox's Avatar
    Join Date
    Apr 2016
    Location
    Queensland, Australia
    Posts
    64

    Re: Spa electricity issues

    It's always been with the heater on. We have it set to 37 (Celsius). 18kw was an approximation, as it was before the monitoring system was installed. So just basing it off meter readings and the bill. The monitoring system has just been installed because of this huge bill. The water is never hot. It always feels at about 37. Maybe I need to get a thermometer that's independent to the spa. I always based it on that. No breakers have been tripped.

    We honestly didn't know we were using that much. We only get our bills every 3 months here, and we had no reason to look in the meter box. We knew the solar was generating as we check that regularly. It was a very expensive lesson learnt!
    5900 litre or 1558 gal above ground swim spa. Approx 5 years old and heated to 37 degrees celsius year round. Cartridge filter, ozonator, Nature2 mineral sanitiser, Aqua Health non chlorine based shock, Lithium Hypochlorite dosed at each spa usage. Filled using mostly stored rainwater from tanks, and town water when the tanks are drained.

  9. Back To Top    #9
    Chatabox's Avatar
    Join Date
    Apr 2016
    Location
    Queensland, Australia
    Posts
    64

    Re: Spa electricity issues

    Could it be the motor at all?
    5900 litre or 1558 gal above ground swim spa. Approx 5 years old and heated to 37 degrees celsius year round. Cartridge filter, ozonator, Nature2 mineral sanitiser, Aqua Health non chlorine based shock, Lithium Hypochlorite dosed at each spa usage. Filled using mostly stored rainwater from tanks, and town water when the tanks are drained.

  10. Back To Top    #10
    mas985's Avatar
    Join Date
    May 2007
    Location
    Pleasanton, CA
    Posts
    11,490

    Re: Spa electricity issues

    Just because the heater is set to heat the water, it does not mean it is always "on". The thermostat will turn it on and off depending on heat demand. So at any point in time it can be either on or off. It never runs continuously.

    What is the make model of your spa?
    Mark
    Hydraulics 101; Pump Ed 101; Pump/Pool Spreadsheets; Pump Run Time Study; DIY Acid Dosing; DIY Cover Roller
    18'x36' 20k plaster, MaxFlo SP2303VSP, Aqualogic PS8 SWCG, 420 sq-ft Cartridge, Solar, 6 jet spa, 1 HP jet pump, 400k BTU NG Heater

  11. Back To Top    #11

    Join Date
    May 2016
    Location
    La Porte
    Posts
    25

    Re: Spa electricity issues

    Australia, hmmm aint it winter there?
    couple months back heater probably didnt need to be on to keep water warm enough.
    14.6k gal., AG, Pentair SD60 sand filter, Pentair DynII-N2-2 pump, 2 hp/2 speed motor, installed on 9/2015, taylor 2006 test kit, Hayward Diver Dive pool cleaner, well water

  12. Back To Top    #12
    Chatabox's Avatar
    Join Date
    Apr 2016
    Location
    Queensland, Australia
    Posts
    64

    Re: Spa electricity issues

    No, we don't really do winter here. Current daytime temps where I am are 26 degrees. (78F) so there should be no extra demand on the spa. The power bill before this one would be a truer "winter" bill. And that was a lot less. It's nearly consuming double what it has been for the past year.

    Mas - I was meaning that the heater is working. It's not overly hot (thermostat not turning off) or too cold (heater not working at all). It's just normal temp. I have sat beside it today and it has a whining noise that I've never noticed before. Maybe the pump?

    It's a 5900 litre signature brand swim spa. (1558 gal) It's about 5-6 years old, and was professionally installed.
    5900 litre or 1558 gal above ground swim spa. Approx 5 years old and heated to 37 degrees celsius year round. Cartridge filter, ozonator, Nature2 mineral sanitiser, Aqua Health non chlorine based shock, Lithium Hypochlorite dosed at each spa usage. Filled using mostly stored rainwater from tanks, and town water when the tanks are drained.

  13. Back To Top    #13
    mas985's Avatar
    Join Date
    May 2007
    Location
    Pleasanton, CA
    Posts
    11,490

    Re: Spa electricity issues

    The heater uses at least 3 KW (one model uses 6 kw) so depending on how much it runs, you can easily get to those usage levels. As I said before 18 kwh/day is just for the pumps and if the heater runs 50% of the time, that becomes 30 kwh/day. So I think what you are seeing is reality. You might want to consider changing the run schedule so it heats the spa right before you use it and only runs long enough for just heating. Also, there is no reason to run the blower unless you are actually in the spa and want it. Changing the run schedule could save a considerable amount of energy.
    Mark
    Hydraulics 101; Pump Ed 101; Pump/Pool Spreadsheets; Pump Run Time Study; DIY Acid Dosing; DIY Cover Roller
    18'x36' 20k plaster, MaxFlo SP2303VSP, Aqualogic PS8 SWCG, 420 sq-ft Cartridge, Solar, 6 jet spa, 1 HP jet pump, 400k BTU NG Heater