Page 1 of 2 12 LastLast
Results 1 to 20 of 23
Thread: Wire size for pool pump
    May 2009
    Columbus, MI
    22
    I am in the starting stage of installing a above ground pool, just starting to collect items before the install
    my question is what gauge wire should i be looking for
    pump will be located 200 ft from house fuse panel, and from what I have read that there will be some voltage drop over that length of a run,
    1 1/2 hp motor
    15 amp
    120 volts
    20amp breaker in panel
    I was thinking like 200ft 10-2 direct burial 18" deep
    20amp GFI on post 5ft away from pool wall with weather cover
    and bond the pump and pool
    do all you thinks 10-2 will be enough to allow for the drop in volts for that lenght of a run
    28ft round AG 52" high 18,500 gals, Hayward ASL cartridge filter, Hayward single speed 1 1/2 hp pump, 2-4 x 20 fafco solar bear heaters, TF100 test, BBB
    Mod Squad JohnT's Avatar
    SW Indiana
    9,171
    Re: Wire size for pool pump
    Two things that might make life easier: First, you shouldn't need a 1.5HP pump for an AG pool. 1HP should do the job on most any AG pool, and you might be able to get by with a 3/4HP. Second, a 220V pump will greatly reduce the wire size required and the voltage loss on the long run.
    May 2009
    Columbus, MI
    22
    forgot to add that this is a 28ft round pool 48" is only 2 years old the next door neighbor is moving out and the new owners did not want the pool so I received the pool free
    he had the pool next to his house but I am not so lucky, I have to install 200ft back from the house
    Round Rock, TX
    529
    The wire size determines your voltage drop. You need to know what kind of voltage drop you can afford on the pump.
    From what I'm seeing to keep your voltage drop to 5% on a 15A circuit at 200 feet you need #8 wire, which would actually cover you for a 20amp service also, thus giving you some head room after installation.
    There are some other rules to look into for continuous run motors and such that I'm not familiar with, but I'd say 10-2 is too small.
    dave
    15,500 gal, inground gunite pool with 7 ft spa, 2 speed pump 2hp/.33hp, 3/4 hp booster pump, Intermatic P1353 timer, AutoPilot SC-48, Sand filter with ZeoBest, Heater, that I never use . . .
    Aug 2008
    Conway SC
    102
    WOW #8 wire.. I like to see someone wrap that around the screws on the Receptacle..
    I myself also have approx 200 ft run.. Probably a tad more. I ran 10 gauge and my voltage didn't drop at all.
    I am also slightly confused and need to break out the Code book (need to find it).. Now regardless to a 240volt or a 120volt Pump, I still do believe that the circuit must be a 20 amp Circuit.. Somebody educate me on this while i try to locate my book..
    17000 Gallons (16x32) Vinyl In Ground Pool
    Sand Filter
    Install "Finish Date" July 30 2014"
    Propane heater installed.. Used for 1 day.
    City Water.
    Round Rock, TX
    529
    You can run a smaller wire for a 240V motor because the effective voltage drop is half that at 120V.
    I agree a #8 is huge, but 200 feet (I'm assuming one way) is a long way.
    May 2009
    Columbus, MI
    22
    Yes its 200ft one way.... I used this site to see how much voltage drop http://genuinedealz.com/voltage-drop.html
    for 10 AWG 120v at 200' run voltage was 6.162
    You need to run 4 conductor wire (10 gauge) from the main panel (240 volts off a 30 amp breaker in the main) to a subpanel located nearer the pool. Then you can wire up recepticles with 12-2 . You really should use conduit to run the 4 conductors, too.
    Honestly, wiring a pool is not a DYI job, IMO. Too much can go wrong. Everything needs to be bonded correctly, sub panel wired correctly (i.e. remove the jumper between the ground and common bus) , etc. the pump should be wired with flex conduit into a second sub box. Spend the extra money and hire an electrician that knows what he's doing. Electricity aorund water has to be done correctly. Lots of stuff you can DYI, but wiring a pool shouldnt be one of them, IMO.
    Not trying to discourage DYI; i'm a king DYI'er, but this i would hire out.
    Quote Originally Posted by Sparkmaster
    Yes, 20 amp. Doesnt matter if it's 240 or 120. 240 just has 2 hot legs, and a ground, instead of one hot leg and ground. You can run 240 on a 15 amp breaker if the equipment doesnt pull more than 12-13 amps.
    Sometimes you dont need a common on a 240 motor, depends on how its configured. Out by a pool, i would run #10, 4 conductor: 2 hots, 1 common, 1 ground. #10 needs a 30 amp breaker. Bond the pool to the pump, ladder fittings, heater if you have one. The bond wire should be 8 guage minimum and has nothing to do with the gound from the main.
    As i said previously, hire an electrician. You will be glad you did.
    (FYI: 15 amp is #14, 20 amp is #12, 30 amp is #10, 40 amp #8, etc
    Quote Originally Posted by Brad S
    Those are minimums. For longer distances you need to use thicker wire. There is no way that #12 is going to be acceptable for 20 amps over a 200 foot run. I agree with lovingHDTV, #8 is really the minimum you should be considering for this situation. To keep the voltage drop under 3%, which is a good rule of thumb, you would need to use #6.
    You cant put wire bigger than #12 around a recepticle screw, it's not practicle. And yes, #12 over 200 feet wont work either. 200 feet requires 4 wire conductucer, THHN wire to a sub panel. Besides, a pool pump requires an insulated ground wire, so NM or UF direct burial wont work anyway, at least not to code.
    IF I were going to DYI, i would:
    1) Put a 60 amp, dipole breaker in the main
    2) Run #4 THHN. Thats stranded wire. You need 4 conductors, 1 black, 1 red, for the hots, one green for ground, and one white for the common.
    3) Run the conductors in 1 1/2 inch conduit
    4) Mount an outdoor sub panel
    5) run the wires into the panel.
    6) wire the pump into the panel with flex conduit to an appropriate breaker size.
    7) You can add recepticles off the sub panel as needed for other devices you want to power. recepticles can be no closer than 5 feet from the pool.
    60 amps is plenty of power out there. Even accounting for the volatage drop. 60 amp really only requires #6 wire, but with the 200 feet, you should use #4.
    I should add item 8.
    8) If you are not EXTREMELY comfortable doing this, hire an electrican.
    May 2009
    Columbus, MI
    22
    I am comfortable doing this, I have wired my house and wired my garage, I use to work for a AC company and would wire AC units all day long....
    I just did not want to spent money and time on the wire for it to be undersized, for that long of a run as for the direct burial that is why I had asked, I was hoping someone would point me in the correct direction and I want to thank all that have responded
    Rocklin, Ca
    467
    I don't have my code book with me but I think I recall something about how close the conduit can be buried to the pool. 10 feet stick in my mind.
    Also don't forget that you can only have 360 degrees of bends between pull points.
    11000 Gals, Intelliflo, Sta-Rite Cartridge, Polaris 360
    Pool I built in my old house: my-new-pool-build-t4534.html
    Right on the 360. I believe the distance is 5 feet though. In-pool light condiut doent count since they are low voltage. But, you need a deck box since the conduit run from the light up to the deck gets full of water.
    May 2009
    Columbus, MI
    22
    this is what I have come up with after read the above post's
    going the 240v route
    50 amp main breaker
    30ft 6/3 with Gound NM-B cable [romex] inside basment to outside wall into LB type fitting
    Can I wire nut the nm-b cable to thwn in the lb fitting or is there a better way?
    165ft #6 thwn stand 2 black's one with red tape on both ends for hots (found new wire at my fathers house Hope he wasn't saving it )
    165ft #6 white common
    165ft #6 green ground (can I use a smaller green like #8 ) guess it will save a few dollars
    1" pvc conduit only need 2 90's min 18" deep
    outdoor sub panel (dont know it I will get a 2 or 6 breaker sub)
    gfi breaker to 120v pump ran in seal tight conduit
    i have been reading up on the bonding and will do as to code
    I think this sound much better just the few questions to figure out
    Rocklin, Ca
    467
    If your conduit is under concrete decking it does not need to be 18" deep. There are exceptions so you should consult the NEC.
    This sounds fine! 50 amp is great.
    1) Yes on the #8 ground
    2) 18 inches is ok,even if under concrete. Too hard to make a shallower trench and more work, why bother
    3) go with a 6 breaker panel, you wil be glad you did, you have plenty of power
    4) wire nuts from romex to THWN is fine
    Crazycalvin's Avatar
    Mar 2008
    Irmo, South Carolina
    56
    Interesting...
    15 x 26 Sharkline
    2.5 HP Dual Speed Pump
    200 Sq. Ft. cartridge filter
    Mar 2009
    NJ
    215
    Re #7 above, I think the "convenience receptacle" needs to be between 10 and 20ft away from the pool wall.
    Wow, this "free pool" will cost the OP some $$ in copper cable. It'll all be worth it. Good luck.
    18' x 54" Round AG 7500 gallon w/small prefab 2-piece fandeck
    Waterways 200sf Cartridge Filter, 1.5 hp 2-speed pump. 2" pvc piping
    Pool Pilot Total Control swg w/acid tank feeder
    Pool Rover Jr., BBB, TF 100 test kit
  20. Back To Top    #20
    Jun 2008
    Central MD
    149
    Convenience receptacles must be at least 5 but not more than 10 feet from pool and in my area- 1 is required.
    24' Round Doughboy AG.
    Usually filled with 3 kids, the wife, and occasionally the dog.