    Pool heater Fault

    Yesterday got this code from our pool heater. Fuse Link Fault/Field. It's a Jandy Legacy LRZ 399,000 BTU,. Did some googling and didn't find much. I found this in the troubleshooting guide FAULTFUSELINK/FIELD 1. Fusible link fault. 1. Identify and correct loose connections or replace Fusible Link... I believe the attached image points to the part needing replacement. Is there some diagnostic I can do before hand with a multimeter ? Is it just a fuse ? Any advice would be greatly appreciated !!!
    Attached Images Attached Images

  2. Back To Top    #2


    TFP Guide

    Join Date
    Apr 2016
    Location
    Quaker Hill, CT
    Posts
    1,247

    Re: Pool heater Fault

    The fusible link is there to protect you in the event the unit over heats. The link literally melts when it gets too hot shut off power to the gas valve/burner control system. If its a loose wire going to the link repair the loose wire. You can troubleshoot the link by testing it for continuity. If the fuse has melted carefully inspect the heater for signs of overheating / call a service tech. If you replace the link and it melts again stop using the heater and have the unit repaired.
    Chuck-
    15x30 Above ground, Pentair Superflo VS, 19" sand filter, TF-100 test kit
    Aqua Comfort ACT750 heat pump / 6x20 ground mount solar panel / DIY automation

    Photos of 2016 Build, Inside Your Breaker Panel, Free Copy of 2017 NEC code
    TFP is funded by member support click here to help

  3. Back To Top    #3

    Re: Pool heater Fault

    Thanks for the reply... Interesting .. When I opened the pool up I and ran the heater it had an issue with a varment that made a home inside. I cleaned it out best I could , but since the pool heater's control panel occasionally would go opaque from what I guess is excess heat. Do you think perhaps the varment ate or dug away at some insulation that could be causing this ?

  4. Back To Top    #4


    TFP Guide

    Join Date
    Apr 2016
    Location
    Quaker Hill, CT
    Posts
    1,247

    Re: Pool heater Fault

    Varments certainly do love to chew insulation it seems. They also seem to like using control boards as bathrooms. At least that's been my experience with them. Do your best to look for damage if you cant find any and continue to have issues a service tech may be your best bet.
    Chuck-
    15x30 Above ground, Pentair Superflo VS, 19" sand filter, TF-100 test kit
    Aqua Comfort ACT750 heat pump / 6x20 ground mount solar panel / DIY automation

    Photos of 2016 Build, Inside Your Breaker Panel, Free Copy of 2017 NEC code
    TFP is funded by member support click here to help

  5. Back To Top    #5

    Re: Pool heater Fault

    Is the insulation replaceable ? Didn't see any resources. Also didn't even see insulation on the exploded parts diagram. Unfortunately service in our area isn't great or specialized.

  6. Back To Top    #6

    In the Industry

    ps0303's Avatar
    Join Date
    Jul 2011
    Location
    FL
    Posts
    3,435

    Re: Pool heater Fault

    It's called a "rollout switch/fuseable link". It is used to sense if the flames kick out from under and into the front of the cabinet. If this item goes out, there is a reason and usually caused by the flames rolling out into the front of the heater. Make sure you don't have a blockage in the heat exchanger area and or anything on top of the burners. Most likely you have something blocking the heat exchanger from exhausting correctly.
    Paul
    http://www.gastekservices.com A word of caution: When working with gas and electrical you might want to consider a licensed contractor. Consider the value of your life and others around you. If you would like to provide a review of the help I provided, please use the following link to leave a review. gastek - Google Search,

  7. Back To Top    #7
    carlos31820's Avatar
    Join Date
    Nov 2010
    Location
    Midland, Georgia
    Posts
    345

    Pool heater Fault

    Do you have signs of soot near the exhaust? I had this happen a couple months back and it was caused by debris and soot blocking the heat exchanger fins. This blockage caused the inside of the cabinet to get hot enough to melt that fusible link because the heat could not go past the exchanger fins fast enough.

    You can take off the black metal covering the exhaust and make sure there's no debris or soot buildup. I used some wire brushes and compressed air to clean the fins on the top of the exchanger. You really can't get to the bottom of the exchanger but this is where the compressed air came in handy, I just blew compressed air from the top and then blew compressed air around the burner tubes to get all the soot out from around the burner tubes.

    To double check the fuse is indeed the problem and not the wiring, you can TEMPORARILY connect a wire between the spade connectors in the back of the fuse, if the heater comes on and stays on, you know the fuse is the issue as the temporary wire is basically bypassing the fuse. DO NOT be tempted to leave that temporary wire in place after your test. This is a safety item that shuts the heater off to keep it from getting too hot and damaging the electronics or just catching fire.

    Basically, figure out what caused it to get so hot in the first place.

    I got my replacement fuse from Amazon.


    16x36 Vinyl Pool - 22.5K gallons.
    Jandy Stealth 1hp pump - Jandy CS-150 filter
    Jandy Legacy 250k heater - Jandy Ei SWCG
    Jandy Watercolors LED light
    Paramount Vanquish in-floor cleaner

  8. Back To Top    #8

    Re: Pool heater Fault

    Thanks all !!! I guess I need to take a closer look. I think the insulation has been compromised as when I cleaned out the mouse nest there in spring was some crumbly debris. Jandy sent me the part replacement # but it's the entire combustion chamber, not just an insulation panel. Hope I don't have to scrap the unit , it's only 2 years old.. Wish me luck !!!

  9. Back To Top    #9
    carlos31820's Avatar
    Join Date
    Nov 2010
    Location
    Midland, Georgia
    Posts
    345

    Pool heater Fault

    I doubt you need to replace all that. The crumbly debris may have been brought by the mouse from elsewhere.

    The design of these heaters is pretty low tech when you think about it. Flame source under fire box and most of the heat escapes thru the exhaust as it passes past the heat exchanger.

    I bet most of the insulation is probably to keep the outside of the heater panels from getting too hot that they could burn someone if they touch the heater's metal body.
    16x36 Vinyl Pool - 22.5K gallons.
    Jandy Stealth 1hp pump - Jandy CS-150 filter
    Jandy Legacy 250k heater - Jandy Ei SWCG
    Jandy Watercolors LED light
    Paramount Vanquish in-floor cleaner

  10. Back To Top    #10

    In the Industry

    ps0303's Avatar
    Join Date
    Jul 2011
    Location
    FL
    Posts
    3,435

    Re: Pool heater Fault

    Mice love the insulation inside many units. They will take and chew it up to make a nest. More so on the units that do not use the foam board type of insulator.

    Not sure if Jandy has a package where you can just get the refractory material. I can get them for the Raypak but I do not see any of the Jandy units to know if they carry it. If they do, it might just be for service techs since it's a very involved process to replace.
    Paul
    http://www.gastekservices.com A word of caution: When working with gas and electrical you might want to consider a licensed contractor. Consider the value of your life and others around you. If you would like to provide a review of the help I provided, please use the following link to leave a review. gastek - Google Search,

  11. Back To Top    #11

    Re: Pool heater Fault

    I think the panels also protect the electronics and keep the entering gas line from over heating .. Hopefully there's just an obstruction, otherwise it sounds like an expensive fix. Will know this weekend .. Again thanks all !! This is the best pool site bar none!!!

  12. Back To Top    #12

    Re: Pool heater Fault

    So today replaced the fusible link... No go.. Same error. Found this guide https://www.fwwebb.com/docs/gas/Jand...tingGuides.pdf ... Tested up to step 8 , no voltage. Step 7 had voltage but the diagram is oppositely wired with blue on bottom. Perhaps thats a LRZ vs LRZE issue. Guide says replace the PIB. Does that make sense ? Ps got contiuity accross the fusible link as well.

  13. Back To Top    #13

    In the Industry

    ps0303's Avatar
    Join Date
    Jul 2011
    Location
    FL
    Posts
    3,435

    Re: Pool heater Fault

    Don't you just love the error codes that really don't tell you the real problem. Yes I would suggest trying the PIB replacement. You could call and confirm with Jandy before you purchase and replace it.
    Paul
    http://www.gastekservices.com A word of caution: When working with gas and electrical you might want to consider a licensed contractor. Consider the value of your life and others around you. If you would like to provide a review of the help I provided, please use the following link to leave a review. gastek - Google Search,

  14. Back To Top    #14

    Re: Pool heater Fault

    Yea I was hoping it wouldn't come down to that.. PIB on the way..

  15. Back To Top    #15

    Re: Pool heater Fault

    Soo.. thought I'd write this so perhaps some other poor soul wont go threw the pain I did. As suggested here I opened up the vent again. Didn't expect to find anything since we run the heater almost daily since opening in spring when I cleaned out the vent then. To my surprise a new nest and 3 very well done mice where there. At that point I checked the vent limit switch for continuity and bingo that was the culprit. Not sure why Jandy didn't dedicate a different code/electrical path for that part so the fault would be more clear. Anyway no need to replace the PIB and now I know more about that heater than I should ...

  16. Back To Top    #16

    Join Date
    Jul 2015
    Location
    Knoxville
    Posts
    63

    Re: Pool heater Fault

    Pictures please or it didn't happen.... lol jk please keep the pics, but glad u got it figured out