Thread: Pump GFCI keeps tripping

  1. Back To Top    #1

    Join Date
    Apr 2016
    Location
    Cincinnati/OH
    Posts
    8

    Pump GFCI keeps tripping

    - Over the last 3 weeks, GFCI breaker has tripped 3 times (yesterday was during a dry/calm day while pump running at only 1400 rpm - a couple days after I siliconed around the junction box thinking maybe moisture was getting in box during rain...to rule that out).

    - 4 weeks ago installed a new Pentair variable speed pool pump #342001 (that auto senses voltage to run on 120 or 240).
    - Running on a new GFCI 120v/20amp breaker (pump has max 13.3A on 120 so not a max amperage thing).
    - Also on a new dedicated 70' 12/3 copper circuit (only using the 2 conductors now, but wanted to have option in future to easily go to 240v. I also ran electrical calculator for 70' run and 12/3 copper is in spec).
    - Also on a new well protected junction box with no signs of moisture.
    - Good new liquid tight conduit connections from box to pump.


    Looking for logical next step...
    Should I try a different brand breaker?
    Any idea if less likely if switching to a 240 circuit/GFCI breaker make it less likely to happen? (I assume breaker have same sensitivity and was hoping to avoid that with the added cost of 240 GFCI breaker).
    Any other ideas to troubleshoot/isolate?
    25K gallon in ground, 16'x32' oval hybrid pool (3' fiberglass wall with gunite floor - skimcoat refurb before 2002). Single 20' skimmer, 30' main drain, 1 return.
    Sand filter. (No other water features). 1.5. Pentair variable speed pump #3420011 on 120v, 2009 Re-gel coated walls with uglassit, 2015 New pool deck patio, 2016 Applied Pool Border around water line.

  2. Back To Top    #2

    TFP Guide

    Join Date
    Jun 2012
    Location
    western NY
    Posts
    1,557

    Re: Pump GFCI keeps tripping

    there is a breaker that works good with that pump. I don't recall the brand off the top of my head. maybe one of the other guys remembers it. That pump has issues on GFCI's that causes it to trip
    Unknown make 18' above ground (bought used in 1999) Sparco sand filter. Hayward 100,000 BTu heater. 2 speed pump

  3. Back To Top    #3

    Join Date
    Apr 2016
    Location
    Cincinnati/OH
    Posts
    8

    Re: Pump GFCI keeps tripping

    Here is what Pentair had to say....to then recommend their brand breaker which unfortunately only comes in Siemens type (and my panel is CH type):
    "Variable Speed pumps will commonly do this with standard GFCI breakers. You will need to switch the breaker out with one that has a minimum of a 6 milliamp GFCI rating, this will solve the issue."
    I am now leaning towards converting it to 240v GFCI to see if that changes the dynamics with lower amperage involved.
    25K gallon in ground, 16'x32' oval hybrid pool (3' fiberglass wall with gunite floor - skimcoat refurb before 2002). Single 20' skimmer, 30' main drain, 1 return.
    Sand filter. (No other water features). 1.5. Pentair variable speed pump #3420011 on 120v, 2009 Re-gel coated walls with uglassit, 2015 New pool deck patio, 2016 Applied Pool Border around water line.

  4. Back To Top    #4

    TFP Guide

    Join Date
    Jun 2012
    Location
    western NY
    Posts
    1,557

    Re: Pump GFCI keeps tripping

    Yep, Siemens is the one. I doubt changing to a 240 will solve the problem. This is a voltage issue not an amperage issue. The VFD in the pump is tricking the GFCI into thinking there is a voltage leak when it alters the frequency that the motor runs at.

    Dan
    Unknown make 18' above ground (bought used in 1999) Sparco sand filter. Hayward 100,000 BTu heater. 2 speed pump

  5. Back To Top    #5

    Join Date
    Apr 2013
    Location
    Sacramento, CA
    Posts
    2,769

    Re: Pump GFCI keeps tripping

    I'm going to agree with Dan here. This is the reason they like the Siemens breaker. It sounds like you are running this direct from you main house panel. Do you have a maintenance disconnect? Not a switch, a disconect within sight of the pump and not more than 50 feet away.

    I would see replace you 20 amp GFCI breaker with a regular breaker. Then get a Seamens sub panel and 20 amp GFCI breaker and set it up next to the pump as a disconnect.
    22k gallon IG pebblefina, Jandy 1.5 HP VS, Jandy CV Cartridge filter, Fafco solar panels, Polaris 360 supply side cleaner, waterfall

  6. Back To Top    #6


    TFP Guide

    Join Date
    Apr 2016
    Location
    Quaker Hill, CT
    Posts
    1,246

    Re: Pump GFCI keeps tripping

    I have the same pump and installed a Seimens GFCI breaker and haven't had an issue yet. Use the breaker for personal protection (class A) which is 5mA. That is what is required to protect you and your kids. DO NOT use the 20mA gfci breakers rated for equipment protection only. The breaker you are looking for is Siemens-QF120 (the 220v version is QF-220). I also prefer gwegan's suggestion of adding the subpanel and putting the breaker outside, but if you are using a twist lock plug on your pump that does count as a service disconnect.
    Chuck-
    15x30 Above ground, Pentair Superflo VS, 19" sand filter, TF-100 test kit
    Aqua Comfort ACT750 heat pump / 6x20 ground mount solar panel / DIY automation

    Photos of 2016 Build, Inside Your Breaker Panel, Free Copy of 2017 NEC code