Thread: #8 copper bonding wire in equipment pad: is stranded ok?

  1. Back To Top    #1
    MitchRyan912's Avatar
    Join Date
    Jul 2015
    Location
    Madison, WI
    Posts
    314

    Question #8 copper bonding wire in equipment pad: is stranded ok?

    I just realized I made an oversight and accidentally used stranded #8 copper wire instead of solid #8 to bond to the wire mesh in my concrete pad, a new pour last weekend. Is this a huge deal, or will it be OK so long as there is a #8 solid running to the pool frame, ladders, etc?
    2016 total pool rebuild thread: here. Pool: 26,000 gal IG vinyl liner (20'x40') in Madison, WI. Gear: ​Superflo VS, Triton TR-60 filter, 2" hi-flow MPV, & Raypak 266A heater. Testing: Taylor K-2006C. Manual chems: 12.5% NaClO liquid, granular CYA, baking soda, 31.25% muriatic acid.

  2. Back To Top    #2

    Re: #8 copper bonding wire in equipment pad: is stranded ok?

    Needs to be solid.

  3. Back To Top    #3
    MitchRyan912's Avatar
    Join Date
    Jul 2015
    Location
    Madison, WI
    Posts
    314

    Re: #8 copper bonding wire in equipment pad: is stranded ok?

    What happens if it's not? What's the likelihood an inspector would make an issue of that wire being stranded?
    2016 total pool rebuild thread: here. Pool: 26,000 gal IG vinyl liner (20'x40') in Madison, WI. Gear: ​Superflo VS, Triton TR-60 filter, 2" hi-flow MPV, & Raypak 266A heater. Testing: Taylor K-2006C. Manual chems: 12.5% NaClO liquid, granular CYA, baking soda, 31.25% muriatic acid.

  4. Back To Top    #4

    Join Date
    Apr 2013
    Location
    Sacramento, CA
    Posts
    2,769

    Re: #8 copper bonding wire in equipment pad: is stranded ok?

    Most Inspectors would fail you.

    The code requires solid wire for several reasons. First sold wire has greater current carrying capacity as compared to the same size of stranded wire. Another way of saying that is that sold wire has less resistance than stranded wire. Why is that important? Well in a bonding system you want the bonding system to have as little resistance as possible so voltage is equal throughout the system. The standard calls for a #8 sold copper wire. That will have less resistance than a #8 stranded copper wire.

    More importantly stranded copper wires, especially uninsulated wire, are susceptible to corrosion from the inside out. Uh?

    In other words instead of having the outside of one copper wire corrode, we have many corroding because stranded wire has multiple times the surface area of solid wire. Corrosion further reduces the cross section of the wire and its ability to act as a low resistance bond connection.
    22k gallon IG pebblefina, Jandy 1.5 HP VS, Jandy CV Cartridge filter, Fafco solar panels, Polaris 360 supply side cleaner, waterfall

  5. Back To Top    #5
    MitchRyan912's Avatar
    Join Date
    Jul 2015
    Location
    Madison, WI
    Posts
    314

    Re: #8 copper bonding wire in equipment pad: is stranded ok?

    Any chance I lucked out by using TWO #8 stranded wires? If it's about current carrying capacity, then a pair of #8 stranded wires will have more capacity than a single #8 solid.

    If not, how in the world can I fix this in 2 days without tearing up a brand new pad? PB will be here to set the gear on the pad on Monday!
    2016 total pool rebuild thread: here. Pool: 26,000 gal IG vinyl liner (20'x40') in Madison, WI. Gear: ​Superflo VS, Triton TR-60 filter, 2" hi-flow MPV, & Raypak 266A heater. Testing: Taylor K-2006C. Manual chems: 12.5% NaClO liquid, granular CYA, baking soda, 31.25% muriatic acid.

  6. Back To Top    #6
    Mod Squad tim5055's Avatar
    Join Date
    May 2014
    Location
    Columbia, SC
    Posts
    8,494

    Re: #8 copper bonding wire in equipment pad: is stranded ok?

    Quote Originally Posted by MitchRyan912 View Post
    Any chance I lucked out by using TWO #8 stranded wires? If it's about current carrying capacity, then a pair of #8 stranded wires will have more capacity than a single #8 solid.

    If not, how in the world can I fix this in 2 days without tearing up a brand new pad? PB will be here to set the gear on the pad on Monday!
    If you used stranded wire how did you attach it to the rebar? Plus, if you have already poured, how would add the second #8 stranded inside the concrete?

    I'm sorry to say (as Gordon pointed out) that most inspectors will fail the inspection. The code is specific to solid wire.
    TFP Moderator 39 X 18 23,000(ish) freeform gunite; built 2007ish; Pentair Triton II TR100 600lb Sand filter; 2 HP Pentair pump with 2.2 HP AO Smith single speed motor; 2 skimmers, 1 main drain, 4 returns w/waterfall, Stenner 45MHP2 3GPD running@ 60% - 15 gal Tank; heated by the sun CYA 200+ when I started - 50 now. Dolphin Supreme M5 Pool Cleaner. Hot Springs SX Spa, 285 gallon

  7. Back To Top    #7
    MitchRyan912's Avatar
    Join Date
    Jul 2015
    Location
    Madison, WI
    Posts
    314

    Re: #8 copper bonding wire in equipment pad: is stranded ok?

    I put two #8 wires in before I poured, attaching them in two spots to the wire mesh (no rebar) with a pair of split bolt connectors. I sanded down the mesh to remove all the rust, to give it a better connection to the wire.
    2016 total pool rebuild thread: here. Pool: 26,000 gal IG vinyl liner (20'x40') in Madison, WI. Gear: ​Superflo VS, Triton TR-60 filter, 2" hi-flow MPV, & Raypak 266A heater. Testing: Taylor K-2006C. Manual chems: 12.5% NaClO liquid, granular CYA, baking soda, 31.25% muriatic acid.

  8. Back To Top    #8

    Join Date
    Jul 2015
    Location
    Newton, NJ
    Posts
    89

    Re: #8 copper bonding wire in equipment pad: is stranded ok?

    Didn't you have to have the bonding inspection BEFORE the concrete was poured?
    20K gal, IG Fiberglass "Lifetime Pittsburgh", 1 1/2 HP TriStar pump, 525 sqft cartridge filter, AutoPlus T-15 SWG, Dolphin Oasis z5 Robot

  9. Back To Top    #9

    Join Date
    Apr 2013
    Location
    Sacramento, CA
    Posts
    2,769

    Re: #8 copper bonding wire in equipment pad: is stranded ok?

    So go invest in some more split bolts and where the two wires emerge from the slab connect solid #8.

    I'm not going to tell you that complies nor will I tell you that will pass an inspection. To comply you have to jack the slab.

    However I will say stranded encased in concrete will probably corrode less if exposed. You don't want bare stranded out exposed to the weather or buried in soil. Trippe no to buried in soil.
    22k gallon IG pebblefina, Jandy 1.5 HP VS, Jandy CV Cartridge filter, Fafco solar panels, Polaris 360 supply side cleaner, waterfall

  10. Back To Top    #10
    MitchRyan912's Avatar
    Join Date
    Jul 2015
    Location
    Madison, WI
    Posts
    314

    Re: #8 copper bonding wire in equipment pad: is stranded ok?

    Quote Originally Posted by avc8130 View Post
    Didn't you have to have the bonding inspection BEFORE the concrete was poured?
    I built the pad myself, and didn't know that an inspection was needed. This project is considered a repair of an existing IG pool (built 40+ years ago). I'm not sure how that affects things, but had we used the old pad instead of putting the gear in this new location, then there would have been no bonding of ANY kind done on that old pad, much less any other part of the pool. The ladders were previously grounded with the ground conductor in a 12/2 romex, connected to the water spigot nearest to the pool. The steel wall frame of the pool was never bonded.
    2016 total pool rebuild thread: here. Pool: 26,000 gal IG vinyl liner (20'x40') in Madison, WI. Gear: ​Superflo VS, Triton TR-60 filter, 2" hi-flow MPV, & Raypak 266A heater. Testing: Taylor K-2006C. Manual chems: 12.5% NaClO liquid, granular CYA, baking soda, 31.25% muriatic acid.

  11. Back To Top    #11

    Join Date
    Mar 2015
    Location
    Texas
    Posts
    27

    Re: #8 copper bonding wire in equipment pad: is stranded ok?

    My equipment pad (built last year) has rebar in it but there was no bonding to the pool or the equipment located on it. The equipment is bonded using solid copper wire to the pool and decking around it though. It passed inspection. (Houston, Texas)
    Pool newbie - In ground 13.5k gallon gunite pool & spa. All Jandy equipment - 2.0HP VS pump, iAqualink touch controller, Jxi heater, & AquaPure salt cell system, CL 580 cartridge filter, & 1.0HP water feature pump. SAVI LED lights.

  12. Back To Top    #12
    MitchRyan912's Avatar
    Join Date
    Jul 2015
    Location
    Madison, WI
    Posts
    314

    Re: #8 copper bonding wire in equipment pad: is stranded ok?

    Quote Originally Posted by gwegan View Post
    So go invest in some more split bolts and where the two wires emerge from the slab connect solid #8.

    I'm not going to tell you that complies nor will I tell you that will pass an inspection. To comply you have to jack the slab.

    However I will say stranded encased in concrete will probably corrode less if exposed. You don't want bare stranded out exposed to the weather or buried in soil. Trippe no to buried in soil.
    You can see in this picture of the concrete after pouring, the 60' length of wire sticking out of the side (corner closest to the bottom of the pic). That wire also comes out through the top of the concrete, so it exits the form in two spots.
    IMG_4360.jpg
    Might I be able to attach a solid #8 to that long length of stranded #8, and bury that connection in a small form of concrete to prevent it from being exposed to the elements? At that point, I'd just attach everything together from this new connection and cut off the wire sticking out of the concrete. Thoughts? Might I be any closer to passing, assuming there even is a bonding inspection on a rebuild project? (I question that there even will be a bonding inspection, as bonding never came up in talks with either the PB nor the PB's preferred electrician.)
    2016 total pool rebuild thread: here. Pool: 26,000 gal IG vinyl liner (20'x40') in Madison, WI. Gear: ​Superflo VS, Triton TR-60 filter, 2" hi-flow MPV, & Raypak 266A heater. Testing: Taylor K-2006C. Manual chems: 12.5% NaClO liquid, granular CYA, baking soda, 31.25% muriatic acid.

  13. Back To Top    #13


    TFP Guide

    Join Date
    Apr 2016
    Location
    Quaker Hill, CT
    Posts
    1,246

    Re: #8 copper bonding wire in equipment pad: is stranded ok?

    So to make you life easier and because you technically didn't need to bond the pad because it is so far away from the pool. Get your solid lie and use a connector to that stranded wire in the slab. Then run the solid up onto the pad to go to your pump and heater. Then run it out to your pool and you will be fine.
    Chuck-
    15x30 Above ground, Pentair Superflo VS, 19" sand filter, TF-100 test kit
    Aqua Comfort ACT750 heat pump / 6x20 ground mount solar panel / DIY automation

    Photos of 2016 Build, Inside Your Breaker Panel, Free Copy of 2017 NEC code
    TFP is funded by member support click here to help

  14. Back To Top    #14
    MitchRyan912's Avatar
    Join Date
    Jul 2015
    Location
    Madison, WI
    Posts
    314

    Re: #8 copper bonding wire in equipment pad: is stranded ok?

    Pretty sure that's the best news I've heard all day! I went to bed in a bit of a panic last night, as my wife wasn't really thrilled with doing a concrete pad (she wanted 2'x2' pavers), so I never would have heard the end of it if I had messed up something... on the electrical end of the pad build!
    2016 total pool rebuild thread: here. Pool: 26,000 gal IG vinyl liner (20'x40') in Madison, WI. Gear: ​Superflo VS, Triton TR-60 filter, 2" hi-flow MPV, & Raypak 266A heater. Testing: Taylor K-2006C. Manual chems: 12.5% NaClO liquid, granular CYA, baking soda, 31.25% muriatic acid.