  1. Back To Top    #1

    Bonding wire between booster and main pump

    Hi - I think the answer is yes, but i just want to confirm. I have a bonding wire that can reach the main pump, but the wire is not longer enough to reach the booster pump. Can I just get a copper wire, attach it to the booster pump and then connect it to the lug on the main pump where the bonding wire is?

    Thanks!
    Inground pool; about 20,000 gallons (18' x 36'); pool liner (vinyl?) a few years old; Haywood pump SPX2607X10

  2. Back To Top    #2


    TFP Guide

    Join Date
    Apr 2016
    Location
    Quaker Hill, CT
    Posts
    1,256

    Re: Bonding wire between booster and main pump

    yes, it should be at a minimum 8awg bare copper wire. Where the wire is spliced you should use a split bolt connector like this one. http://www.homedepot.com/p/Blackburn...B2-5/100165861
    Chuck-
    15x30 Above ground, Pentair Superflo VS, 19" sand filter, TF-100 test kit
    Aqua Comfort ACT750 heat pump / 6x20 ground mount solar panel / DIY automation

    Photos of 2016 Build, Inside Your Breaker Panel, Free Copy of 2017 NEC code