Results 1 to 9 of 9
Thread: Bonding grid question
    May 2015
    Fullerton, CA
    636
    So, perhaps a bit after the fact, but I thought I would ask.
    So the pool structural rebar connected to the bonding grid around the pool with an approved clamping device and #8 copper wire and must extend 3ft out away from the edge of the pool. So, if there is rebar in the concrete pool deck, is it good enough to just have the deck rebar touching the bonding grid rebar and tied to it with regular rebar wire? See the underlined below. If that was not done is there an issue with potentially shocking somebody? I do recall the deck contractor telling the inspector that there was "no rebar" going to be used on the patio deck, when I asked about it the contactor told me it would have just caused delays if we told him we were putting rebar in the deck. Odd or I am just reading into this too much?
    The code states:
    Section 680.26. Equipotential Bonding.
    (C) Equipotential Bonding Grid. The parts specified in 680.26(B) shall be connected to an equipotential bonding grid with a solid copper conductor, insulated, covered, or bare, not smaller than 8 AWG or rigid metal conduit of brass or other identified corrosion-resistant metal conduit. Connection shall be made by exothermic welding or by listed pressure connectors or clamps that are labeled as being suitable for the purpose and are of stainless steel, brass, copper, or copper alloy. The equipotential bonding grid shall conform to the contours of the pool and shall extend within or under paved walking surfaces for 1 m (3 ft) horizontally beyond the inside walls of the pool and shall be permitted to be any of the following:
    (1) Structural Reinforcing Steel. The structural reinforcing steel of a concrete pool or deck where the reinforcing rods are bonded together by the usual steel tie wires or the equivalent. Where deck reinforcing steel is not an integral part of the pool, the deck reinforcing steel shall be bonded to other parts of the bonding grid using a minimum 8 AWG solid copper conductor. Connection shall be per 680.26(D).(2) Bolted or Welded Metal Pools. The wall of a bolted or welded metal pool.
    (3) Alternate Means. This system shall be permitted to be constructed as specified in (a) through (c):
    33x19, 3'4"-5'6", 7ft spa, baja reef, 14'x9', 18" deep, 10,668 Gal. Quartzite coping, Stonescape Tropics Blue mini-pebble, abalone & glass beads. Jandy Equip.(JXi heater, 2.7HPVS pump, PLC1400 SWG, CV580 filter, Aqualink, LEDs)
    TF-100, Doheny Discovery robot.
    Apr 2013
    Sacramento, CA
    2,769
    Re: Bonding grid question
    The deck rebar must connect to the pool rebar with #8 bare copper wire using listed clamps.
    This explains it better: http://www.mikeholt.com/download.php...as_2014NEC.pdf
    Look at page 19.
    Mod Squad JohnT's Avatar
    SW Indiana
    9,199
    Do it right. You can't go back and redo it after the concrete is poured and we often have members getting shocked when the touch their deck.
    Jan 2016
    Mesa, Az
    541
    Quote Originally Posted by JohnT View Post
    That's the problem. His concrete is already poured . . .
    May 2015
    Fullerton, CA
    636
    Well this is the funny part, the concrete is poured. I came across this question about bonding grids with a friend who is having a pool built also. It got me thinking as to why the deck contractor told the inspector there was no rebar going into the pool deck other than the bonding grid. I got some excuse from the contractor when I asked why he lied to the inspector. Now I am wondering if we are going to have an issue. The fun continues, suggestions?
    Jul 2015
    Central Valley CA
    1,109
    If the rebar in the deck is tied with rebar wire to the bonded rebar in the shell as you described above I think you are going to be fine what you have is basically a ufer ground. Would have been better to have the #8 wire clamped to the deck and cost would have been next to nothing but sounds as if that ship has sailed.
    12,300 Gallon, IG PebbleFina, 3 ft sheer, 2 Jandy nicheless LED lights, Jandy Pro 1.5HP VS pump (A.O. Smith Motor), PB4-60 Booster pump, Polaris 280, Jandy cv340 cartridge filter, Zodiac Z4 control panel W/iAquaLink, Stenner pumps for chlorine & MA connected to WiOn WiFi switches, TF-100. You can support TFP with AmazonSmile just click the link!
    borjis's Avatar
    Aug 2014
    Pacific NW
    2,329
    When your pool is built and filled/running:
    Wet the deck, then test with one multimeter probe in the water, the other on the wet deck.
    one guy last week reported .8 volts
    they felt a tingle when getting out after swimming.
    Dolphin E10 Cleaning Robot.
    May 2015
    Fullerton, CA
    636
    Well, here is another angle, we experienced excessive cracking in the cement from too wet of a mix. The contractor has agreed to take out the damaged sections all of which at the coping edge. 7 sections in total. This is when I asked how they are going to reconnect the bonding grid if they are cutting through it was a saw. So is there a "Correct" way to "re-connect" a bonding grid to adjacent sections of decking? This question and the discussion with my friend is what got me thinking about this situation. Sort of a mess.
    Apr 2013
    Sacramento, CA
    2,769
    Yes there is a correct way. Use listed clamps to clamp the bonding wire #8 copper solid bare and the wire to a clamp attached to the rebar. Something like this: