    Convert 120v Light to 12v Low Voltage Using Existing Wiring?

    Topic says it all. My idea is to get an Intermatic transformer and use the existing wiring to the lams and use the same lamp housings with perhaps a screw adapter for the bulb. Is doing something like this considered safe and legal?

    The reason is that a tree root damaged the PVC conduit going to the spa light. After it rains, the GFCI will trip if the spa light is on for more than 5 minutes or so. The GCFI circuit has been replaced but the behavior is the same. There is likely a from water in the ground but barely (since it doesn't trip for after 5 min). My thinking is that reducing the voltage from 120 to 12 will not only drastically reduce the chances of a short (it would not overcome the resistance) but there would be piece of mind with low-voltage current going to the pool instead of 120v should a breaker fail.

  2. Back To Top    #2

    In the Industry

    bdavis466's Avatar
    Join Date
    Aug 2014
    Location
    Riverside, CA
    Posts
    3,286

    Re: Convert 120v Light to 12v Low Voltage Using Existing Wiring?

    What does the conduit have to do with the light? The light cord is watertight and the conduit is typically full of pool water anyway.

    The GFI is tripping for a reason and the issue needs to be fixed correctly.

    There have been a couple recent pool electrocutions that have resulted in death. I wouldn't take any chances.
    -Brian-
    33K Pool/Spa, Pentair Equipment
    POOL BUILD
    Davis Custom Construction - Home Page

  3. Back To Top    #3


    TFP Guide

    Join Date
    Jul 2015
    Location
    Central Valley CA
    Posts
    1,073

    Re: Convert 120v Light to 12v Low Voltage Using Existing Wiring?

    If you know about where the conduit damage is I would plug it at the pool so the hole you dig to repair it does not fill with water and cut and repair the conduit. Pvc is easy to cut and repair especially if you heat it up a bit. Then you can pul in a new safe line.
    12,300 Gallon, IG PebbleFina, 3 ft sheer, 2 Jandy nicheless LED lights, Jandy Pro 1.5HP VS pump (A.O. Smith Motor), PB4-60 Booster pump, Polaris 280, Jandy cv340 cartridge filter, Zodiac Z4 control panel W/iAquaLink, Stenner pumps for chlorine & MA connected to WiOn WiFi switches, TF-100. You can support TFP with AmazonSmile just click the link!

  4. Back To Top    #4

    Join Date
    Apr 2016
    Location
    Los Angeles, CA
    Posts
    10

    Re: Convert 120v Light to 12v Low Voltage Using Existing Wiring?

    Quote Originally Posted by atttech-2 View Post
    If you know about where the conduit damage is I would plug it at the pool so the hole you dig to repair it does not fill with water and cut and repair the conduit. Pvc is easy to cut and repair especially if you heat it up a bit. Then you can pul in a new safe line.
    It's underneath concrete. Can't get to it.

  5. Back To Top    #5

    Join Date
    Apr 2016
    Location
    Los Angeles, CA
    Posts
    10

    Re: Convert 120v Light to 12v Low Voltage Using Existing Wiring?

    What does the conduit have to do with the light?

    The conduit houses the electrical wire that feeds electrical power to the light.

    The light cord is watertight

    The electrical wire from the light cord (which is only like 3 feet or something right?) all the way to the nearest junction box is not watertight.

    Quote Originally Posted by bdavis466 View Post
    and the conduit is typically full of pool water anyway.
    It is? Because the copper wire in the junction box that leads to the spa light is definitely not meant to be submerged in water.

    There have been a couple recent pool electrocutions that have resulted in death
    Were they killed by 120v systems or 12v?

    I wouldn't take any chances.

    I'm not. That's why the spa light is disconnected at the junction box until i figure this out.

  6. Back To Top    #6

    In the Industry

    duraleigh's Avatar
    Join Date
    Apr 2007
    Location
    Sebring, Florida
    Posts
    30,084

    Re: Convert 120v Light to 12v Low Voltage Using Existing Wiring?

    Welcome to the forum.

    bdavis466 is absolutely correct. The pvc conduit from the light niche to the surface is flooded. If you have wire going into (and out of) that pvc conduit that is not completely waterproof, that is a big problem and dangerous.
    Dave S.
    42k vinyl and concrete pool, 1.5hp pump, 140gpm filter
    TFTestkits , PoolMath , Pool School

  7. Back To Top    #7

    In the Industry

    bdavis466's Avatar
    Join Date
    Aug 2014
    Location
    Riverside, CA
    Posts
    3,286

    Re: Convert 120v Light to 12v Low Voltage Using Existing Wiring?

    The conduit is nothing more than a means to route the pool light to a listed pool junction box. The conduit needs to be water tight because it is completely flooded and equal to the water level in the pool. This is why the junction boxes must be 8" higher than the water level of the pool, regardless of how far away they are.

    Damaged conduit is not a good thing because you are likely losing pool water through that cracked portion. What makes you certain the conduit is cracked? Even if the conduit is broken or cracked, the pool light cord would also have to be damaged to cause the GFI to trip. Why it takes 5 minutes to trip is anyone's guess but you need to use that as a cue to take action. Switching to 12V isn't going to fix the damaged wire (if that is the case) and you lose GFI protection completely on low voltage lines.

    While 12V systems are generally considered safer, the situation you are describing is very unsafe.

    I don't understand this 3' cord you are talking about. The pool light cord runs continuously from the light to the junction box and IS watertight.

    The deaths were likely 120V systems but 12V can cause just as much trouble.

    The copper wire you are refering to may be the bond wire which should be an insulated stranded #8 copper wire. There should be no bare copper wires in the pool light niche or conduit.
    -Brian-
    33K Pool/Spa, Pentair Equipment
    POOL BUILD
    Davis Custom Construction - Home Page

  8. Back To Top    #8

    Join Date
    Apr 2016
    Location
    Los Angeles, CA
    Posts
    10

    Re: Convert 120v Light to 12v Low Voltage Using Existing Wiring?

    I don't understand this 3' cord you are talking about. The pool light cord runs continuously from the light to the junction box and IS watertight.

    Yeah I just watched a video and learned that. I misunderstood how it worked, my mistake sorry.

    Damaged conduit is not a good thing because you are likely losing pool water through that cracked portion. What makes you certain the conduit is cracked? Even if the conduit is broken or cracked, the pool light cord would also have to be damaged to cause the GFI to trip. Why it takes 5 minutes to trip is anyone's guess but you need to use that as a cue to take action. Switching to 12V isn't going to fix the damaged wire (if that is the case) and you lose GFI protection completely on low voltage lines
    The entire patio in the area where the conduit would be run has been lifted up from a tree root. It looks like earthquake damage it's so bad. I don't know if the cable is damaged but I'm pretty certain the conduit is. I just opened up the lamp housing and even though there was a tight vacuum seal around the gasket, there was a lot of moisture in there and the contacts are very badly corroded and caked in aluminum oxide residue. The short could be coming from that.

    I'm thinking I could clean the contacts and run the thing dry for a while to see if it trips?

    Replacing the housing is not an option. It can't be pulled through, believe me I've tried everything including wrapping it around a steel bar. The conduit makes a 180 degree turn somewhere between the niche and the j-box. The lamp literally faces the j-box. I need to figure out a way to repair this. There is no other option barring some battery powered unit controlled wirelessly--does that even exist? Hopefully it's simply just a short caused by corrosion inside the housing. I found an article on how to fix that and seal it up with epoxy, haven't read it yet.

    Assuming that can be done, back to the original question. Can the system be converted to 12V using the existing housing and cable? Couldn't I just use one of those j-box transformer adapters, and then pop in an Edison Screw to Bi-pin adapter in the housing and use a 12V LED bulb?



  9. Back To Top    #9

    In the Industry

    bdavis466's Avatar
    Join Date
    Aug 2014
    Location
    Riverside, CA
    Posts
    3,286

    Re: Convert 120v Light to 12v Low Voltage Using Existing Wiring?

    No, pool lights are listed assemblies that are not designed to be tampered with. Even though your concrete has lifted, the conduit may not be broken. PVC is very flexible.

    You should try a good quality silicone lubricant. I'd amazing the difference the line makes.
    -Brian-
    33K Pool/Spa, Pentair Equipment
    POOL BUILD
    Davis Custom Construction - Home Page

  10. Back To Top    #10

    Join Date
    Apr 2013
    Location
    Sacramento, CA
    Posts
    2,769

    Re: Convert 120v Light to 12v Low Voltage Using Existing Wiring?

    I'm going to +1 Brian on everything above. I have my doubts that corded wires inside conduit are bad.

    I'd also like to strongly suggest that you replace the Jbox with a new one.

    Post some overall pictures of your pool, the inside of the niche, the jbox and the inside of the jbox as well as your pad and we can give you some ideas.

    Is the light the only thing on the GFCI?
    22k gallon IG pebblefina, Jandy 1.5 HP VS, Jandy CV Cartridge filter, Fafco solar panels, Polaris 360 supply side cleaner, waterfall

  11. Back To Top    #11
    wjr75's Avatar
    Join Date
    Jun 2013
    Location
    IL
    Posts
    816

    Re: Convert 120v Light to 12v Low Voltage Using Existing Wiring?

    We had water getting into the junction box for our lights which was tripping the GFCI. We had one light replaced with a LED and they replaced the rubber plugs that go around the power cable in the lights nook which prevents water getting into the conduit. They also sealed the junction box cover with silicon caulk. We have not had any problems since this was done over a year ago.
    Inground 22k gallon gunite 15x31 main pool, 15x7 wading pool/sunning deck, hot tub/with overflow (9' octagon with limestone top) & slide NSWG, Aqua Blue Pebble Sheen
    Filter dual cartridge Sta-rite 450sq/ft, TF-100 Test Kit
    Heater Raypak 2100 400k btu cupro-nickel exchanger
    Auto pool cover, Polaris 280 auto pool cleaner, Jandy AqualinkRS8 Remote Control System

  12. Back To Top    #12

    Join Date
    Apr 2016
    Location
    Los Angeles, CA
    Posts
    10

    Re: Convert 120v Light to 12v Low Voltage Using Existing Wiring?

    No, pool lights are listed assemblies that are not designed to be tampered with.

    What do you mean tampered with? The bulb is meant to be replaceable. I just realized that most 12v pool light bulbs use regular edison screws so I wouldn't even be modifying it in any way.

    I tried silicon lubricant last time I tried to get it out which was last summer. I guess I could give it another shot.

    Is the light the only thing on the GFCI?

    No there's a pool light which works fine. It only trips when the spa light is connected.


    - - - Updated - - -

    Thanks gwegan and wjr75 the j-box very well could be the culprit.

  13. Back To Top    #13

    In the Industry

    bdavis466's Avatar
    Join Date
    Aug 2014
    Location
    Riverside, CA
    Posts
    3,286

    Re: Convert 120v Light to 12v Low Voltage Using Existing Wiring?

    Call the manufacturer of the light and ask them if that's an acceptable practice. They would be the ideal point of contact.

    Then go to your building department and ask an inspector for his opinion.

    Finally ask your family and every person who may potentially enter your pool how they feel about it.

    You will not find anyone here that will tell you that a correct fix is not the best and only option. You seem to have your mind made up but if you are looking for support on not fixing the actual problem, you won't get it from me....
    -Brian-
    33K Pool/Spa, Pentair Equipment
    POOL BUILD
    Davis Custom Construction - Home Page

  14. Back To Top    #14

    Join Date
    Apr 2013
    Location
    Sacramento, CA
    Posts
    2,769

    Re: Convert 120v Light to 12v Low Voltage Using Existing Wiring?

    Here's the deal with lights. They are designed a certain way for a reason. The NEC is written that way for a reason. The principal reason is to reduce the risk of electric shock. Work arounds are not something that is ok.

    I would call a good industrial electrician. They have ways of getting things through conduit. Its worth the effort. But retrofiting a fixture is not something you can do.

    I would be figuring a way to replace the light fixture (and cable) and the junction box. Put up some pictures of the pool area maybe we can help.
    22k gallon IG pebblefina, Jandy 1.5 HP VS, Jandy CV Cartridge filter, Fafco solar panels, Polaris 360 supply side cleaner, waterfall

  15. Back To Top    #15

    Join Date
    Apr 2016
    Location
    Los Angeles, CA
    Posts
    10

    Re: Convert 120v Light to 12v Low Voltage Using Existing Wiring?

    Okay I must not have been clear. I am not "retrofitting" any fixtures beyond changing a bulb. I asked if using a bi-pin adapter was possible before but the question is now moot since I discovered 12V pool bulbs use edison screws. I am perfectly comfortable putting a 12v 9 watt LED bulb into a housing designed for replaceable 120V 500 watt incandescents and using a 75 watt isolation transformer to feed it low voltage power. Not only am I comfortable with it, but I am highly uncomfortable leaving my fully functioning 120V pool light as-is. Given what happened to my spa light, had the GFI failed someone could have died. I want the inherent safety not just for my family but for whoever lives here 30 years from now. That is why I am replacing my pool light (not my defective spa light--yet) bulb with a 12V bulb and sending 12V to the J-box via a transformer. None of my plans violate the NEC. And I expect to see them make 120V pool lights illegal in the coming decades. They are a needless danger and a relic. Thanks to very recent developments in LED lighting there people have no business sending a dangerous level of electrical power to a swimming pool.

    The lamp housings cannot be replaced without major excavation and destruction of the patio. This is a fact. I am not being lazy or cheap about it. It's simply not coming out. Last night I dumped 1/2 quart of wire lubricant into the conduit and it still won't budge in either direction. Because of this the spa lamp which is tripping the GFI will not be reconnected. I may hire an electrician to give it a try and I may redo the patio someday, but until then it is toast and I'm probably going to snip the housing off the cable and take it out for good. That is why I inquired about alternatives such as a battery powered remote control light.

    Here are some photos. Note that the watertight sheath part of the light cable does not extend to the J-box. I don't know why but see so for yourself.


    Attached Images Attached Images

  16. Back To Top    #16

    Re: Convert 120v Light to 12v Low Voltage Using Existing Wiring?

    You are absolutely wrong about low voltages being capable of killing people that are in water. It's the current that kills, not the voltage. It only takes about 100 milliamps to be fatal (or 0.1 Amps,) and in the water where your skin resistance is greatly reduced the voltage necessary to get that much current through your body is also greatly reduced. The GFCI protection on 120V pool lights and outlets in your bathroom and kitchen are designed to remove power when 5 milliamps of current are flowing somewhere they should not.

    https://www.physics.ohio-state.edu/~...l_current.html
    8.5k gallon IG pebble sheen play pool with Intellitouch control, Intellifo VF, IC 20, Rainbow tab feeder (not currently in use), Pentaire mystery cartridge filter with labels faded to the point I have no idea on the model, Intellibrite 5g LED light, Hayward Navigator. Adding IntelliPh and Crestron control next.

  17. Back To Top    #17

    Join Date
    Jan 2016
    Location
    TX
    Posts
    157

    Re: Convert 120v Light to 12v Low Voltage Using Existing Wiring?

    More than likely the reason you are tripping the GFI is due to damaged/worn out conductor insulation in your electrical circuit . Long and short, as temperature increases(current flowing through wire when lamp is on) resistance decreases. After a few minutes the old and worn out insulation becomes more susceptible to alow current to flow from the Ungrounded conductor(Hot wire) to anywhere with a path of minimal resistance to ground(conduit full of water etc..). It doesn't take much for a GFCI to trip, typically just a few milliamps.

    I'd just repull an entire new lamp assembly and not worry about trying to retrofit to a new technology. If you are having an electrician come out, make sure he brings a megger and knows how to use it properly.

    Regarding 12V and shock electrocution, you've made some assumptions that just aren't correct.
    Gunite Pool/Spa, CLI Caribbean blue crystal stone smooth, Pentair 3hp Intellifo VS, Pentair Quad DE Filter, Pentair 400k BTU Heater, KK Prowler 820, Pentair PSL4 controler with Screenlogic wifi, Inline Chlorinator, Pentair 1.5hp Spa Blower, TF-100 Test Kit w/ Speed Stir. My 2016 Pool Build

  18. Back To Top    #18

    Join Date
    Apr 2016
    Location
    Los Angeles, CA
    Posts
    10

    Re: Convert 120v Light to 12v Low Voltage Using Existing Wiring?

    Quote Originally Posted by dtlight View Post
    You are absolutely wrong about low voltages being capable of killing people that are in water. It's the current that kills, not the voltage. It only takes about 100 milliamps to be fatal (or 0.1 Amps,) and in the water where your skin resistance is greatly reduced the voltage necessary to get that much current through your body is also greatly reduced. The GFCI protection on 120V pool lights and outlets in your bathroom and kitchen are designed to remove power when 5 milliamps of current are flowing somewhere they should not.

    https://www.physics.ohio-state.edu/~...l_current.html
    Your link uses 42 volts as the minimum. I edited out my definitive claim though I shouldn't have said that. But maybe I'll take some photos of me swimming with a car battery some time.

    - - - Updated - - -

    Quote Originally Posted by bradj View Post
    More than likely the reason you are tripping the GFI is due to damaged/worn out conductor insulation in your electrical circuit . Long and short, as temperature increases(current flowing through wire when lamp is on) resistance decreases. After a few minutes the old and worn out insulation becomes more susceptible to alow current to flow from the Ungrounded conductor(Hot wire) to anywhere with a path of minimal resistance to ground(conduit full of water etc..). It doesn't take much for a GFCI to trip, typically just a few milliamps.

    I'd just repull an entire new lamp assembly and not worry about trying to retrofit to a new technology. If you are having an electrician come out, make sure he brings a megger and knows how to use it properly.

    Regarding 12V and shock electrocution, you've made some assumptions that just aren't correct.
    Thanks but the circuit works just fine with the pool light as well as a gazebo light on. It only trips when the spa light is connected at its nearby j-box. I'm unable to pull the cord.

  19. Back To Top    #19

    TFP Guide

    Join Date
    Jun 2012
    Location
    western NY
    Posts
    1,557

    Re: Convert 120v Light to 12v Low Voltage Using Existing Wiring?

    I have stayed out of this one untill now. Looking at the picture you posted kind of confirmed a suspicion I had about the problem you are having. Usually if a pool light is tripping a GFCI it is because the lamp housing has failed and water was getting inside. The other failure point can be in the wiring but it is rare as the cable assembly is rated for underwater use. If the cable gets damaged it can be the source of the problem. Your cable problem seems to be a splice somewhere in the conduit that has failed. Untill you dig it up and find the splice it is any guess as th where it is and how they did it. My best guess is there is a buried junction box that the wires are clamped to. This may be the reason why you can not pull the cable/wires out.


    I kind of chuckled when I read this comment... But maybe I'll take some photos of me swimming with a car battery some time. I have a pretty vivid imagination.

    Actually putting a 12 volt battery in the pool will do nothing as the potential difference will only be between the two posts of the battery.
    Unknown make 18' above ground (bought used in 1999) Sparco sand filter. Hayward 100,000 BTu heater. 2 speed pump

  20. Back To Top    #20

    In the Industry

    ps0303's Avatar
    Join Date
    Jul 2011
    Location
    FL
    Posts
    3,436

    Re: Convert 120v Light to 12v Low Voltage Using Existing Wiring?

    There are just some things that a qualified contractor should be performing.
    Paul
    http://www.gastekservices.com A word of caution: When working with gas and electrical you might want to consider a licensed contractor. Consider the value of your life and others around you. If you would like to provide a review of the help I provided, please use the following link to leave a review. gastek - Google Search,