    Question Pump startup power surge

    Hello,
    I am a relatively new spa owner, and I could use some advice on how to troubleshoot or resolve a problem, or if I am dealing with normal behavior: When my spa pump turns on, it initially draws so much current that the voltage in the entire house fluctuates briefly (i.e. lights dim or brighten, depending on what phase they are on), until the pump stabilizes at the normal current. Here are more details:
    Supply voltage: 110V, dedicated 20A breaker
    Pump: 2-speed Cal Spas PL-353 with GE Motor 5KC38RN3818X, 110V, 12A (high speed), 4A (low speed)
    Pump startup current surge: 43A peak, less than 1 sec, happens for both high & low speed

    While the power surge is noticeable throughout the house from light dimming/brightening and a buzz at the breaker box, it doesn't last long enough to either trip the breaker or usually blow the 20A slow-blow fuse (although the fuse did blow a single time, but that hasn't happened again after replacing). I'm afraid the power fluctuation will damage other equipment in the house, so I've turned the spa off until the problem is resolved.

    I've opened up the pump and found a 161-193 uF capacitor. My multimeter only goes up to 100 uF, so I can't tell if the capacitance value is correct, but it doesn't appear to be leaking current, and it does have charging behavior according to resistance measurements. I removed the capacitor from the pump and turned it on to see if the behavior was consistent, but the motor would not turn and drew 43A while making a whining sound. Also, I was able to turn the pump shaft with a screwdriver, and there was a very small amount of high-pitch noise during rotation, which may be normal from the motor windings.

    I've had this spa for a few months now, and I don't recall having this problem initially, and it seems to be getting worse. However, maybe I was blinded by the enjoyment of the spa and didn't notice the problem until now. Is a 43A startup current surge on a 12/4A pump normal? I hope not, and so what are the next steps to troubleshoot and resolve the issue? Replace the capacitor? Use a larger capacitor? Add a local battery? Replace the motor? Rebuild the pump with new impeller? Replace the entire pump? Any help would be greatly appreciated!

    Shawn

  2. Back To Top    #2
    banditig's Avatar
    Join Date
    Sep 2015
    Location
    Ohio
    Posts
    464

    Re: Pump startup power surge

    I don't think it's the spa. What is your main supply At the meter?
    15x54 swim & play vinyl metal wall AG
    Hayward S210T sand filter 1.5 HP Pentair Superflo vs
    Rheem raypak 130,000 BTU mv ng
    Jacuzzi 345 whirlpool bath
    TF-100 test kit, HM digital com100 Wanda the Whale

  3. Back To Top    #3

    Join Date
    Jan 2016
    Location
    Camarillo, CA
    Posts
    3

    Re: Pump startup power surge

    Thanks for the reply, banditig. The voltage at the breaker box is 120V.

  4. Back To Top    #4
    banditig's Avatar
    Join Date
    Sep 2015
    Location
    Ohio
    Posts
    464

    Re: Pump startup power surge

    Ok if you're electric sevice to meter is less than 200 Amps and your house has other loads going on then a 110 V pump does have a huge startup.
    Last edited by banditig; 01-09-2016 at 06:53 PM. Reason: Typo
    15x54 swim & play vinyl metal wall AG
    Hayward S210T sand filter 1.5 HP Pentair Superflo vs
    Rheem raypak 130,000 BTU mv ng
    Jacuzzi 345 whirlpool bath
    TF-100 test kit, HM digital com100 Wanda the Whale

  5. Back To Top    #5

    Join Date
    Jan 2016
    Location
    Camarillo, CA
    Posts
    3

    Re: Pump startup power surge

    Thanks again banditig. I do have a 200 A service. So you think the 43A startup surge is normal?

  6. Back To Top    #6
    banditig's Avatar
    Join Date
    Sep 2015
    Location
    Ohio
    Posts
    464

    Re: Pump startup power surge

    That's a bit more complicated, I'll leave it to experts here. But I thought surge is about 1/5 x watts
    15x54 swim & play vinyl metal wall AG
    Hayward S210T sand filter 1.5 HP Pentair Superflo vs
    Rheem raypak 130,000 BTU mv ng
    Jacuzzi 345 whirlpool bath
    TF-100 test kit, HM digital com100 Wanda the Whale

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •