    Replaced thermister, MInimax still reading 110 F

    My 10 year old minimax heater was reading 110F where pool sensor and thermometer floating in pool agreed it was 84. FIgured 10 year old thermister was failing and replaced it with correct part. Same reading after replacement. Guessing its the board, but anyone has input would be greatly appreciated.

  2. Back To Top    #2

    In the Industry

    ps0303's Avatar
    Join Date
    Jul 2011
    Location
    FL
    Posts
    3,436

    Re: Replaced thermister, MInimax still reading 110 F

    Is it reading 110 right when you turn it on?
    Paul
    http://www.gastekservices.com A word of caution: When working with gas and electrical you might want to consider a licensed contractor. Consider the value of your life and others around you. If you would like to provide a review of the help I provided, please use the following link to leave a review. gastek - Google Search,

  3. Back To Top    #3

    Join Date
    Jul 2015
    Location
    Los Angeles, ca
    Posts
    3

    Re: Replaced thermister, MInimax still reading 110 F

    Quote Originally Posted by ps0303 View Post
    Is it reading 110 right when you turn it on?
    Yes. usually tracks pool temperature, may read 108 if pool is 82 , 110 if 84. Consistent offset. Poll controller reads correct temperature as measured in pool. Cant think what it be other than board now that brand new thermister doingsame thing as old one.

  4. Back To Top    #4

    In the Industry

    ps0303's Avatar
    Join Date
    Jul 2011
    Location
    FL
    Posts
    3,436

    Re: Replaced thermister, MInimax still reading 110 F

    Yes if you already replaced the thermistor and it's still reading incorrectly, then it could be the board. This is a minimax NT correct?
    Paul
    http://www.gastekservices.com A word of caution: When working with gas and electrical you might want to consider a licensed contractor. Consider the value of your life and others around you. If you would like to provide a review of the help I provided, please use the following link to leave a review. gastek - Google Search,

  5. Back To Top    #5

    Join Date
    Jul 2015
    Location
    Los Angeles, ca
    Posts
    3

    Re: Replaced thermister, MInimax still reading 110 F

    Quote Originally Posted by ps0303 View Post
    Yes if you already replaced the thermistor and it's still reading incorrectly, then it could be the board. This is a minimax NT correct?
    yes . minmax nt Low NOx Series 6800 control board

  6. Back To Top    #6

    In the Industry

    ps0303's Avatar
    Join Date
    Jul 2011
    Location
    FL
    Posts
    3,436

    Re: Replaced thermister, MInimax still reading 110 F

    So then I guess its the board. I've seen where the display on the board is messed up and it shows weird stuff.
    Paul
    http://www.gastekservices.com A word of caution: When working with gas and electrical you might want to consider a licensed contractor. Consider the value of your life and others around you. If you would like to provide a review of the help I provided, please use the following link to leave a review. gastek - Google Search,