    I have been trying to figure out how to answer this question that someone asked me. im not sure if there is enough given information to solve this but any help at all would be greatly appreciated.
    A: Indoor hot tub.
    223 sq ft, 2' 1" deep, 2,600 gal.
    Design temperature: 104 F.
    GPM: 120 Gal. (Turnover rate under 30mins.)
    Hot water temperature from Boiler is140 F.
    What is the delta T between the waterout and back into the hot tub to maintain 104 F?
    What is the BTU amount to maintain thistemperature?
    Same questions for pool B.
    B: Outdoor pool.
    1,500 sq ft, 3' 6" deep, 39,000gal.
    Design temperature: 97 F
    GPM: 257 Gal. (Turnover rate app 3 hrs)
    Hot water temperature from Boiler is 140F.
    Thank you
    Patrick_B's Avatar
    Jun 2011
    Midland TX
    14,998
    Re: Help with Spa calculations
    Welcome to the forum!
    Sorry to begin this with a question back to you, but are you sure those circulation rates are correct?
    Essential Links:
    mas985's Avatar
    Pleasanton, CA
    11,742
    I think you are really asking how much heat is lost in the spa per min or hr. That is very difficult to figure out and requires a lot of details about the weather at the time you are using the spa.
    However, if you want to know how many BTU is required to take the spa water from say 50F to 104F (54F rise), that is easy.
    For spa A, that is BTU = 2600 * 8.34 * 54 = 1,170,936 BTU
    If you know the BTU output of a heater, you can then calculate the input to output water temperature delta at a given flow rate. So if you have a 400,000 BTU heater rated at 80% efficiency, then
    dT = 400,000 * 0.8 / 60 / (120 * 8.34) = 5.33F
    Is the boiler a hot water heater and not a pool heater?
    Mark
    Mar 2007
    San Rafael, CA USA
    12,082
    (typed this as Mark was posting so some duplicate information)
    (2600 gallons) * (8.34 pounds/gallon) = 21,684 pounds so that many BTUs to raise the water 1F
    (39000 gallons) * (8.34 pounds/gallon) = 325,260 pounds so that many BTUs to raise the water 1F
    As for how many BTU/hr it takes to maintain a temperature, that depends on the heat loss and that depends on many factors such as pool and air temperature, humidity (affects evaporation rates), and wind.
    It sounds like these are commercial spa and pool installations. This is primarily a residential pool and spa forum.