Post subject: Pool bonding!???  Posted: December 28th, 2011, 9:56 pm |
Joined: December 16th, 2011, 3:10 pm Posts: 100
|
|
I'm about to build a 20x40..... I have a bit of knowledge on the electrical side of the pool build... As it all seems to be the same as regular wiring in wet areas (gcfi plugs, etc)... What I'm not sure of is the bonding... From what I've read on this site and google here is the plan
Ground wire connected to everything metal close to the pool... Including the metal pool walls, light housings, ladder, and diving board... A ground wire run all the way around the pool about 10 inches from the pool wall... All connected together and run back to the pool pump area.... Is this correct? Where does this wire connect to when it gets back to the pump?
Also... I don't plan on using rebar in my cement skirt as I will put fiber in the cement to take the place of it... So I won't have rebar to connect it to... Any thoughts are appreciated!!
_________________ 20x40 vinyl liner IG pool, 20x16 shallow end, deep end is 8ft....Metal walls... 1hp single speed Pentair Pump..... 24" sand filter... build in progress....
|
|
|
|
 |
|
JamesW
|
Post subject: Re: Pool bonding!???  Posted: December 28th, 2011, 10:09 pm |
Joined: March 2nd, 2011, 8:02 pm Posts: 1611
|
|
|
|
 |
|
WhoDat?
|
Post subject: Re: Pool bonding!???  Posted: December 29th, 2011, 12:05 am |
Joined: December 16th, 2011, 3:10 pm Posts: 100
|
Ok cool... That is some good reading... As I said... I didn't PLAN on using rebar... But plans change...  I was just gonna go without it because it would be easier... But after reading the guidelines it seems as though it's necessary!... So I can add the grid style rebar in the cement... Connect it to all metal components and the metal wall... Which, if I read if correctly... The metal wall structure can be used as the "grid"... So if I connect them all I do t see where I could have a problem.. You???
_________________ 20x40 vinyl liner IG pool, 20x16 shallow end, deep end is 8ft....Metal walls... 1hp single speed Pentair Pump..... 24" sand filter... build in progress....
|
|
|
|
 |
|
WhoDat?
|
Post subject: Re: Pool bonding!???  Posted: December 29th, 2011, 12:07 am |
Joined: December 16th, 2011, 3:10 pm Posts: 100
|
Ohm_Boy wrote: I believe that you will need to have either rebar in the concrete, or a bonding grid in or underneath the pour, as per NEC 680.26. I would recommend that you check with your local inspector, or AHJ, who will be happy to let you know what you need to have in your location to comply w/ code. How would I find this local inspector? Or AHJ??
_________________ 20x40 vinyl liner IG pool, 20x16 shallow end, deep end is 8ft....Metal walls... 1hp single speed Pentair Pump..... 24" sand filter... build in progress....
|
|
|
|
 |
|
WhoDat?
|
Post subject: Re: Pool bonding!???  Posted: December 29th, 2011, 3:10 am |
Joined: December 16th, 2011, 3:10 pm Posts: 100
|
Wasn't gonna.... I'm way out in the country.... I got one when I built my house... But that's it.... 
_________________ 20x40 vinyl liner IG pool, 20x16 shallow end, deep end is 8ft....Metal walls... 1hp single speed Pentair Pump..... 24" sand filter... build in progress....
|
|
|
|
 |
|
JamesW
|
Post subject: Re: Pool bonding!???  Posted: December 29th, 2011, 11:00 am |
Joined: March 2nd, 2011, 8:02 pm Posts: 1611
|
|
Even though a #8 awg copper conductor around the pool would satisfy code, I would still want a grid of mesh or rebar to reduce the risk of stray currents causing nuisance shocks to people in the water.
|
|
|
|
 |
|
PoolGuyNJ
|
Post subject: Re: Pool bonding!???  Posted: December 29th, 2011, 11:17 am |
| Special Contributor |
 |
Joined: May 20th, 2007, 4:29 pm Posts: 3053 Location: South Central NJ
|
|
IIRC, the mesh needs to be attached to the main bonding wire using underground rated connectors in several locations and the mats wire tied together.
Scott
_________________ Owner of - PoolGuyNJ LLC Expert Pool and Spa Repairs, Renovations, and Augmentation. Helping people decide what is the right gear for meeting their needs. Expectations Set, Expectations Met, No Surprises.
|
|
|
|
 |
|
WhoDat?
|
Post subject: Re: Pool bonding!???  Posted: December 29th, 2011, 12:25 pm |
Joined: December 16th, 2011, 3:10 pm Posts: 100
|
|
Thanks guys for all the comments!! I def don't want to have stray voltage!
_________________ 20x40 vinyl liner IG pool, 20x16 shallow end, deep end is 8ft....Metal walls... 1hp single speed Pentair Pump..... 24" sand filter... build in progress....
|
|
|
|
 |
|
PoolGuyNJ
|
Post subject: Re: Pool bonding!???  Posted: December 30th, 2011, 8:22 am |
| Special Contributor |
 |
Joined: May 20th, 2007, 4:29 pm Posts: 3053 Location: South Central NJ
|
|
Having it and dealing with it are two different things.
Strays can come from different sources. The may come from the power company, the earth itself, pool wiring anywhere, and so on.
You may also, as a last resort, need a sacrificial anode or two, thought this is not commonly needed as the earlier steps handle most situations.
Scott