 Post subject: How should a Heater be added to a system with an existing HP
PostPosted: December 29th, 2010, 1:04 pm 
Registered User

Joined: December 14th, 2010, 4:45 pm
Posts: 72
Topic split from locked post located here for purposes of educational discussion and substantiation of potential Heat Pump damage claims, discussed further below. The continuation of discussion will only be allowed as long as the replys remain free of public personal dispute, which if necessary should be handled via PM - dmanb2b

PS - all members are reminded to read and adhere to our Site Rules & Forum Etiquette, here

galleymore wrote:
Hi
I have a large pool (80,000 gal) which is in a rental property, as a result the heaters (3 of them!) are off most of the time.
When we have a booking, say once a month, we fire up the heaters and it can take 3-4 days to get up to 85-88!!

If the air temp is low, or it rains we do not even achieve that!

Question: Could I add a LP heater to the row of heat pumps (should it go first or last??) to give that initial boost for heat then allow the HP to keep it there??
Perhaps let the gas heater kick in occasionally when needed??

Any thoughts!

Thanks!
Bama Rambler wrote:
I would pick the most convenient location for the heater. It doesn't make a big difference where in relation to the others it is in the plumbing circuit as far as efficiency goes.


This is totally incorrect. Any NG/LP heater has to go last in line after the filter. Never put a NG/LP heater before a Heat Pump, period.

Additional, are the multiple heat pumps in series or parallel? All heat pumps need to be in parallel, in other words, they all need to be drawing fresh cold filtered pool water and passing it back to the pool (not to any other heat pump) or on to a NG/LP heater.



_________________
Pool #1 IG 24k Diamond Brite plaster with spill-over spa. Jandy Aqua Link RS One Touch with built into pool floor cleaner. Jacuzzi Magnum pump/basket feeding Hayward top mount Zeosand filter. Jacuzzi Magnum pump/basket for Spa Jets. Heat Siphon pool heat pump. Dolphin Robotic pool cleaner.

Pool #2 IG 35K 20X40 Vinyl. Hayward top mount Zeosand filter with Pentair 3 HP IntelliFlo VS+SVRS. Chemical Free pool using Water Doctor Copper Ion Generator, PoolSkim, Polaris 9300 Sport robotic pool cleaner, Heat Siphon pool heat pump, solar blanket, Ameri-Dome 50X30 dome enclosure during Winter.
Offline
 Profile  
 
 Post subject: Re: Adding LP heater to existing Heat Pump???
PostPosted: December 29th, 2010, 1:46 pm 
Lifetime Supporter
Lifetime Supporter
User avatar

Joined: April 4th, 2009, 9:30 am
Posts: 3294
Location: NY
iPhone wrote:
Bama Rambler wrote:
I would pick the most convenient location for the heater. It doesn't make a big difference where in relation to the others it is in the plumbing circuit as far as efficiency goes.


This is totally incorrect. Any NG/LP heater has to go last in line after the filter. Never put a NG/LP heater before a Heat Pump, period.

Additional, are the multiple heat pumps in series or parallel? All heat pumps need to be in parallel, in other words, they all need to be drawing fresh cold filtered pool water and passing it back to the pool (not to any other heat pump) or on to a NG/LP heater.


Do you mind expanding on that "period" and explaining why, so that we may learn from your knowledge :goodjob:

Also, your statement about the heater having to go "last in line" has me confused vs. the statement about plumbing in parallel :scratch: .



_________________
24'x52" AGP (13,500 Gallons), Intex SWG, (2)Solar Bear 4x20 panels, Hayward S220T Filter, 1/2hp Pentair Superflo

Pool School, TFTestKits, Pool Calculator
Offline
 Profile  
 
 Post subject: Re: Adding LP heater to existing Heat Pump???
PostPosted: December 29th, 2010, 2:46 pm 
Mod Squad
Mod Squad
User avatar

Joined: June 22nd, 2009, 7:06 pm
Posts: 11276
Location: South Alabama
dmanb2b wrote:
Do you mind expanding on that "period"
I'd like to see the reason for that as well. We're talking pool heaters here, so you're only heating the water a few degrees per pass.



_________________
Dave J.
TFP Moderator
24' x 52" Round AGP. 1.5hp Dynamo pump. 24" Pentair Sand Dollar Filter. 45MHP2(3GPD) Peristaltic Pump
Pool School Pool Calculator TF-Test Kit
You have passed the OCLT when: 1)You lose 1ppm or less FC overnight, & 2)You have .5ppm CC's or less, & 3)your water is clear.
Offline
 Profile  
 
 Post subject: Re: Adding LP heater to existing Heat Pump???
PostPosted: December 29th, 2010, 3:54 pm 
Registered User

Joined: December 14th, 2010, 4:45 pm
Posts: 72
Bama Rambler wrote:
dmanb2b wrote:
Do you mind expanding on that "period"
I'd like to see the reason for that as well. We're talking pool heaters here, so you're only heating the water a few degrees per pass.



Yes what you said is true, but that is only true after the water mixes back into the thousands of gallons of pool water, not the current gallon in the 2 inch line direct from the NG/LP heater! The very hot water directly from an NG/LP Heater (remember its a 300 to 400K BTU heater) will ruin a heat pump if it is running and being feed water from the outlet of a running NG/LP Heater IE there is no where to "Exchange" the heat made by the Heat Pump.


Last edited by dmanb2b on December 31st, 2010, 9:14 am, edited 1 time in total.
Reason: personal comment deleted and all caps edited



_________________
Pool #1 IG 24k Diamond Brite plaster with spill-over spa. Jandy Aqua Link RS One Touch with built into pool floor cleaner. Jacuzzi Magnum pump/basket feeding Hayward top mount Zeosand filter. Jacuzzi Magnum pump/basket for Spa Jets. Heat Siphon pool heat pump. Dolphin Robotic pool cleaner.

Pool #2 IG 35K 20X40 Vinyl. Hayward top mount Zeosand filter with Pentair 3 HP IntelliFlo VS+SVRS. Chemical Free pool using Water Doctor Copper Ion Generator, PoolSkim, Polaris 9300 Sport robotic pool cleaner, Heat Siphon pool heat pump, solar blanket, Ameri-Dome 50X30 dome enclosure during Winter.
Offline
 Profile  
 
 Post subject: Re: Adding LP heater to existing Heat Pump???
PostPosted: December 29th, 2010, 4:03 pm 
Registered User

Joined: December 3rd, 2009, 11:28 am
Posts: 2419
Location: Central Massachusetts
Why would the heat pump even be running if you were using a gas heater? And if you hook it up as you say in parallel, its not an issue anyway.
If you run hot water thru the heat pump and it's not running, there is still no issue. I'm not even sure its an issue if it were running. I've heard this argument before, but not sure it has been substantiated.


Last edited by dmanb2b on December 31st, 2010, 9:22 am, edited 3 times in total.
Reason: deleted/edited personal comment, edited all caps



_________________
14,000 gallon IG, Vinyl. Hayward 3/4 hp superpump, Penatair IC40 SWCG, Pentair automation, Hayward sand filter, Aqua Comfort heat pump, Hayward 400k Lo-Nox LP heater.
Offline
 Profile  
 
 Post subject: Re: Adding LP heater to existing Heat Pump???
PostPosted: December 29th, 2010, 4:40 pm 
Special Contributor
Special Contributor

Joined: May 20th, 2007, 4:29 pm
Posts: 3053
Location: South Central NJ
I personally prefer to see gas fired units after heat pumps. The main reason has to do with the amount of heat the return side of each unit will inject. A gas fired unit's return flow is more likely to approach a heat pumps set point, shutting it off. There goes an extra 75 to 90 KBTUs that could be injected into the flow.

Bypasses can and should, but not must, be added in systems that push less than 110 GPM. Systems that push higher flows should be configured in an off-line configuration. That, though is usually how you would find a commercial pool like in an aquatic center (YMCA).

Scott



_________________
Owner of - PoolGuyNJ LLC
Expert Pool and Spa Repairs, Renovations, and Augmentation. Helping people decide what is the right gear for meeting their needs. Expectations Set, Expectations Met, No Surprises.
Offline
 Profile  
 
 Post subject: Re: Adding LP heater to existing Heat Pump???
PostPosted: December 29th, 2010, 4:46 pm 
Registered User

Joined: December 3rd, 2009, 11:28 am
Posts: 2419
Location: Central Massachusetts
PoolGuyNJ wrote:
The main reason has to do with the amount of heat the return side of each unit will inject. A gas fired unit's return flow is more likely to approach a heat pumps set point, shutting it off. There goes an extra 75 to 90 KBTUs that could be injected into the flow.


That one i'll buy.

The damage argument, eh, not so much :roll:



_________________
14,000 gallon IG, Vinyl. Hayward 3/4 hp superpump, Penatair IC40 SWCG, Pentair automation, Hayward sand filter, Aqua Comfort heat pump, Hayward 400k Lo-Nox LP heater.
Offline
 Profile  
 
 Post subject: Re: Adding LP heater to existing Heat Pump???
PostPosted: December 29th, 2010, 5:08 pm 
Special Contributor
Special Contributor

Joined: May 20th, 2007, 4:29 pm
Posts: 3053
Location: South Central NJ
20 years ago, the damage issue did hold some merit. With heat pumps, the use of titanium has eliminated issues there and Cu-Pro Nickel in gas fired units has reduced erosion and chem wear significantly when compared to straight copper exchangers.

While non-titanium and straight copper units are available, fewer dealers sell them.

Scott



_________________
Owner of - PoolGuyNJ LLC
Expert Pool and Spa Repairs, Renovations, and Augmentation. Helping people decide what is the right gear for meeting their needs. Expectations Set, Expectations Met, No Surprises.
Offline
 Profile  
 
 Post subject: Re: Adding LP heater to existing Heat Pump???
PostPosted: December 29th, 2010, 5:11 pm 
Lifetime Supporter
Lifetime Supporter
User avatar

Joined: May 19th, 2009, 5:02 pm
Posts: 717
Location: Dallas, TX
PoolGuyNJ wrote:
I personally prefer to see gas fired units after heat pumps. The main reason has to do with the amount of heat the return side of each unit will inject. A gas fired unit's return flow is more likely to approach a heat pumps set point, shutting it off. There goes an extra 75 to 90 KBTUs that could be injected into the flow.
Psst...bk gave that recommendation in his first post to this thread... :wink:



_________________
20K gal IG plaster pool, Manually chlorinated with 6% bleach, 1.5 HP Sta-Rite Dura-Glas II pump, Pentair FNS Plus 48 DE filter, Polaris 280
Offline
 Profile  
 
 Post subject: Re: Adding LP heater to existing Heat Pump???
PostPosted: December 29th, 2010, 8:38 pm 
Lifetime Supporter
Lifetime Supporter
User avatar

Joined: April 4th, 2009, 9:30 am
Posts: 3294
Location: NY
iPhone wrote:
Yes what you said is true, but that is only true after the water mixes back into the thousands of gallons of pool water, not the current gallon in the 2 inch line direct from the NG/LP heater! The very hot water directly from an NG/LP Heater (remember its a 300 to 400K BTU heater) will ruin a heat pump if it is running and being feed water from the outlet of a running NG/LP Heater IE there is no where to "Exchange" the heat made by the Heat Pump.


Can you define very hot? Assuming that 2 inch line you are referring to is made from PVC wouldn't that piping show damage before any inline heat pump's metal element was able to be damaged? Again, for full disclosure, I do not own either a HP or NG/LP heater, but wouldn't the output plumbing of an NG/LP Heater required to be metal if it is was really that hot?

I am not at all questioning the efficiency debate and I understand PoolguyNJ's point about tripping the HP set temp, I just question how even let's say 105 deg water can damage the HP element. I also agree with the suggestion about plumbing heaters in parallel, but quite frankly I do not think Bama was that far off in his statement as you are making it out to be. Heck, I would even consider adding a gas heater if the rise in temp is that significant. :goodjob:


Last edited by dmanb2b on December 31st, 2010, 9:21 am, edited 2 times in total.
Reason: deleted personal comment



_________________
24'x52" AGP (13,500 Gallons), Intex SWG, (2)Solar Bear 4x20 panels, Hayward S220T Filter, 1/2hp Pentair Superflo

Pool School, TFTestKits, Pool Calculator
Offline
 Profile  
 
 Post subject: Re: Adding LP heater to existing Heat Pump???
PostPosted: December 29th, 2010, 9:10 pm 
Special Contributor
Special Contributor

Joined: May 20th, 2007, 4:29 pm
Posts: 3053
Location: South Central NJ
When water passes through a heater, most is bypassed internally. The water coming out of the exchanger then mixes with the rest of the flow, cooling it.

Sometimes, the heat is too much for schedule 40 pipes and a few feet of schedule 80 is needed.

Metal is never used anymore.

Scott



_________________
Owner of - PoolGuyNJ LLC
Expert Pool and Spa Repairs, Renovations, and Augmentation. Helping people decide what is the right gear for meeting their needs. Expectations Set, Expectations Met, No Surprises.
Offline
 Profile  
 
 Post subject: Re: Adding LP heater to existing Heat Pump???
PostPosted: December 30th, 2010, 7:26 am 
Mod Squad
Mod Squad
User avatar

Joined: June 22nd, 2009, 7:06 pm
Posts: 11276
Location: South Alabama
I still stand by my original statement. In the context of the OP's situation it won't make much difference.

Dman said it best. Before you can do any damage to an HP that PVC pipe between the two is gonna have serious problems.



_________________
Dave J.
TFP Moderator
24' x 52" Round AGP. 1.5hp Dynamo pump. 24" Pentair Sand Dollar Filter. 45MHP2(3GPD) Peristaltic Pump
Pool School Pool Calculator TF-Test Kit
You have passed the OCLT when: 1)You lose 1ppm or less FC overnight, & 2)You have .5ppm CC's or less, & 3)your water is clear.
Offline
 Profile  
 
 Post subject: Re: Adding LP heater to existing Heat Pump???
PostPosted: December 30th, 2010, 9:52 am 
Registered User

Joined: December 14th, 2010, 4:45 pm
Posts: 72
bk406 wrote:
Why would the heat pump even be running if you were using a gas heater? And if you hook it up as you say in parallel, its not an issue anyway.
If you run hot water thru the heat pump and it's not running, there is still no issue. I'm not even sure its an issue if it were running. I've heard your argument before. It's an old wives tale.


Nobody said the heat pump would be running, be it could be couldn't it? The question was were should a NG/LP heater be placed, common sense says always put the NG/LP heater last after all other heaters.

The Parallel only applies to multiple heat pumps on the same pool not necessarily multiple heater types. Multiple different heater types only need be placed in series in the proper heater type order as in Solar, Heat Pump, NG/LP Heater back to pool.

And yes if you run hot water through a heat pump that is not running there is no issue, but you can ruin a running heat pump if you run hot water directly from a NG/LP heater into a running heat pump so why chance it, just put the NG/LP Heater last. And its not a wife's tale, its true! What would happen to your car engine if after the water went through the radiator you reheated it hotter then it was before it entered the radiator and then sent that to the running engine? I will tell you, in time a ruined engine! A heat pump is designed to exchange heat it creates to water through the heat exchanger and that heat has to be removed. If the water the heat exchanger is in is hotter then the total exchange amount, heat will not be removed and the heat pump can be damaged.

Of course there is no law that says it has to be this way, more over, its a free country and people can still do what they want in their own back yards. But even having said all that, again common sense says that one wants to avoid any unnecessary problems/accidents and that means that a NG/LP Heater should always go last after the Filter and before the Chlorinator. Its just plain old good common sense and proper pool practices.


Last edited by dmanb2b on December 31st, 2010, 9:23 am, edited 3 times in total.
Reason: personal comment deleted



_________________
Pool #1 IG 24k Diamond Brite plaster with spill-over spa. Jandy Aqua Link RS One Touch with built into pool floor cleaner. Jacuzzi Magnum pump/basket feeding Hayward top mount Zeosand filter. Jacuzzi Magnum pump/basket for Spa Jets. Heat Siphon pool heat pump. Dolphin Robotic pool cleaner.

Pool #2 IG 35K 20X40 Vinyl. Hayward top mount Zeosand filter with Pentair 3 HP IntelliFlo VS+SVRS. Chemical Free pool using Water Doctor Copper Ion Generator, PoolSkim, Polaris 9300 Sport robotic pool cleaner, Heat Siphon pool heat pump, solar blanket, Ameri-Dome 50X30 dome enclosure during Winter.
Offline
 Profile  
 
 Post subject: Re: Adding LP heater to existing Heat Pump???
PostPosted: December 30th, 2010, 10:31 am 
Registered User

Joined: December 3rd, 2009, 11:28 am
Posts: 2419
Location: Central Massachusetts
Have any references for any of this"damage" u say that can happen if the HP is running and warm water is running thru it? We usually don't deal with undocumented claims on this site that are dubious at best.



_________________
14,000 gallon IG, Vinyl. Hayward 3/4 hp superpump, Penatair IC40 SWCG, Pentair automation, Hayward sand filter, Aqua Comfort heat pump, Hayward 400k Lo-Nox LP heater.
Offline
 Profile  
 
 Post subject: Re: Adding LP heater to existing Heat Pump???
PostPosted: December 30th, 2010, 12:59 pm 
Mod Squad
Mod Squad
User avatar

Joined: April 4th, 2007, 10:08 am
Posts: 4933
Location: SW Indiana
This thread is locked until we make a determination on splitting some of it to The Deep End, deleting parts of it or both. The discussion, while not uninteresting, is not really helping the OP.

Everyone please try to stay more civil when/if it's reopened.



_________________
TFP Moderator
20K Gallon 20X36 Vinyl Inground
Hayward S244T Sand Filter with 1HP Whisperflo Pump. Liquidator C-201 and Solar Heat
Offline
 Profile  
 
 Post subject: Re: How should a Gas Heater be added to a system with an existin
PostPosted: December 31st, 2010, 9:12 am 
Lifetime Supporter
Lifetime Supporter
User avatar

Joined: April 4th, 2009, 9:30 am
Posts: 3294
Location: NY
Topic has been re-opened and edited to omit personal or interpreted to be personal comments. Thanks



_________________
24'x52" AGP (13,500 Gallons), Intex SWG, (2)Solar Bear 4x20 panels, Hayward S220T Filter, 1/2hp Pentair Superflo

Pool School, TFTestKits, Pool Calculator
Offline
 Profile  
 
 Post subject: Re: How should a Heater be added to a system with an existing HP
PostPosted: December 31st, 2010, 4:21 pm 
Site Admin
Site Admin
User avatar

Joined: May 7th, 2007, 3:03 pm
Posts: 23753
Location: Silver Spring, MD
When properly installed a gas heater should only raise the water temperature by a couple of degrees (ideally less than 10, but sometimes a bit more than that), which would not make much difference. There are going to be some exceptions, a large heater used in a fairly low flow rate system when the filter is very dirty could raise the water temperature by 20 to 40 degrees, but by and large the water temperature will never be hot enough to damage anything.

Of course, heaters are not always properly installed. It isn't too difficult to imagine a situation where an improperly designed plumbing system was allowing the heater to raise the water temperature by more than 40 degrees. In that range, a heat pump that skimped on protection circuitry could have problems.

Efficiency of the heat pump is a much clearer issue. Heat pump efficiency is fairly sensitive to the incoming water temperature. Higher water temperatures mean less efficient heating. This is the best reason to place a gas heater last. Gas heaters are much less sensitive to the incoming water temperature.

There will be a much higher peak temperatures right near the heater if the pump and heater turn off at the same time. Heat inside the heat exchanger continues to heat the water after the flow stops. This hot water won't migrate too far, because the pump is off, but it can cause problems very near the heater. Ideally, the heater should turn off before the pump to allow the heat exchanger to cool down. If it doesn't, the water in the pipe within a foot or two of the heater can get extremely hot. Typically, special high temperature pipe (generally either gray CPVC or metal pipe) is used for a foot or two after the heater because of this.

If a second heater, or a SWG, or any of several other things, is plumbed in directly after a gas heater, without a couple of feet of pipe between them, and the pump doesn't provide a cool down period, there can sometimes be real problems. Some heaters are designed to minimize this risk, using heat exchangers with lower thermal mass and/or putting in spring valves to stop the water flow when the pump goes off and keep the heat inside the heater.



_________________
19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
TFP Admin. Creator of The Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School
Offline
 Profile  
 
Display posts from previous:  Sort by  
 Page 1 of 1 [ 17 posts ] 

All times are UTC - 6 hours [ DST ]


Who is online

Users browsing this forum: No registered users and 0 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  


TroubleFreePool.com The Web