 Post subject: Electrical question
PostPosted: November 4th, 2011, 8:03 am 
New User

Joined: September 13th, 2011, 10:37 am
Posts: 18
My electrician is telling me that code requires me to put 3' of rebar in 1' squares all around my pool in the concrete..... for bonding purposes. I have a few in-ground pools around me and I don't think I have seen anyone using rebar all the way around. Does this seem right???


Offline
 Profile  
 
 Post subject: Re: Electrical question
PostPosted: November 4th, 2011, 8:22 am 
Mod Squad
Mod Squad
User avatar

Joined: June 22nd, 2009, 7:06 pm
Posts: 11258
Location: South Alabama
NEC 680.26 is the specific article that deals with equipotential bonding of pools. Section 680.26(B)(2) is the specific section. It states that you can either bond to the rebar OR have a copper bonding loop 18 to 24" from the inside wall all the way around the pool. However, your inspector has the last word. Don't win the battle and lose the war with him/her.



_________________
Dave J.
TFP Moderator
24' x 52" Round AGP. 1.5hp Dynamo pump. 24" Pentair Sand Dollar Filter. 45MHP2(3GPD) Peristaltic Pump
Pool School Pool Calculator TF-Test Kit
You have passed the OCLT when: 1)You lose 1ppm or less FC overnight, & 2)You have .5ppm CC's or less, & 3)your water is clear.
Online
 Profile  
 
 Post subject: Re: Electrical question
PostPosted: November 4th, 2011, 9:19 am 
Site Admin
Site Admin
User avatar

Joined: May 7th, 2007, 3:03 pm
Posts: 23723
Location: Silver Spring, MD
Rebar reaching out at least 3' from the water in a concrete deck around a pool is extremely common. There are some alternatives, such as replacing the rebar with #8 copper wire, or using certain kinds of steel mesh to form the grid, but they are almost always more expensive.



_________________
19K gal, vinyl, 1/2 HP WhisperFlo pump, 200 sqft cartridge filter, AutoPilot Digital SWG, Dolphin Dynamic cleaning robot
TFP Admin. Creator of The Pool Calculator. Other handy links: Support this site, TF Test Kits, Pool School
Online
 Profile  
 
 Post subject: Re: Electrical question
PostPosted: November 4th, 2011, 10:38 am 
Lifetime Supporter
Lifetime Supporter

Joined: July 9th, 2011, 12:42 pm
Posts: 58
Here is a document I found that is very helpful. But yes, a grid is necessary for proper bonding. http://www.mikeholt.com/files/PDF/Pooldownload.pdf



_________________
Under construction DIY 20x40 vinyl liner steel wall pool, Pentair 2hp wisperflo, Pentair tr100 sand filter, Pentair Minimax 400k heater, diving board, 8 foot sit n step, xtream waterslide, 1700 concrete deck, one amazing wife, 4 children and two German shepherds.
Offline
 Profile  
 
 Post subject: Re: Electrical question
PostPosted: November 4th, 2011, 9:25 pm 
New User

Joined: September 13th, 2011, 10:37 am
Posts: 18
The good thing is that I live in a village that doesn't have an inspector.. I want to make sure that I do it correctly so that I don't have any floating fish if you know what I mean... I guess I am going to go with the over 800 ft of rebar. **** more work.


Offline
 Profile  
 
Display posts from previous:  Sort by  
 Page 1 of 1 [ 5 posts ] 

All times are UTC - 6 hours [ DST ]


Who is online

Users browsing this forum: Google [Bot] and 0 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  


TroubleFreePool.com The Web